Default secondary drain on a vertical unit

an inspector gave me a hit on not installing a secondary drain on a vertical hvac unit. I used a condensate pump with the primary draining into it and the float on the pump wired to shut unit down. Honestly i have never seen a secondary piped up on vertical unit. On a horizonal unit i know you have to have the primary ran out and the emergency pan either run out or a float switch wired in. Just never seen it on vertical...is that national code or is that a local code he is enforcing?
Reply With Quote
Need a home inspection in Nevada? Check out InterNACHI's listing of Nevada certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/22/11, 12:20 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: secondary drain on a vertical unit

Quote:
Originally Posted by Ralph Hickox View Post
an inspector gave me a hit on not installing a secondary drain on a vertical hvac unit. I used a condensate pump with the primary draining into it and the float on the pump wired to shut unit down. Honestly i have never seen a secondary piped up on vertical unit. On a horizonal unit i know you have to have the primary ran out and the emergency pan either run out or a float switch wired in. Just never seen it on vertical...is that national code or is that a local code he is enforcing?
What kind of a inspector are we talking about Home inspectors do not inspect for code and have no means or authority to enforce anything are you referring to the AHJ (Authority having jurisdiction)



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #3  
Old 8/23/11, 9:07 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: secondary drain on a vertical unit

What would happen if the drain line from the equipment to the condensate pump gets clogged?

If your above finished space or in a finished basement you should have a pan below the equipment with a secondary drain or float switch, or you can install a separate secondary drain line from the equipment condensate tray to a visible location. Model codes like the IRC have another option for installing a water detection device to shut down the equipment if the condensate rises above the primary, but before the level reaches the top of the equipment condensate tray ... but I haven't seen that yet. See IRC M1411.3.1 for the model code provisions.

Your local code mileage may vary, but it's sounds like an issue from a home inspectors point of view.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Condensate Drainage jevans Inspecting HVAC Systems 28 11/27/10 2:55 PM
No secondary (pan) drain in Attic Okay per builder mgault Inspecting HVAC Systems 14 1/30/09 8:38 AM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM


All times are GMT -4. The time now is 10:38 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts