Default Single Wall Vent (Oil Furnace)

Single wall furnace vent piping (Direct Vent - Induced Draft Fan).

Piping runs approximately 50 feet to the front wall of the home.

(6) 45 degree bends.
(1) 90 degree elbow.

Vent pipe is run horizontally between the floor joists and suspended ceiling.

The last picture is classic. The Service records indicated that the HVAC tech had just evaluated and completed repair to the vent piping.



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member

Last edited by jhagarty; 2/18/08 at 5:34 PM..
Reply With Quote
  #2  
Old 12/30/06, 7:01 PM
jking2 jking2 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Troy, MI
Posts: 183
Default Re: Single Wall Vent (Oil Furnace)

That flue looks rather corroded and leaky. Being a 50' run, it would seem there must be some shorter route to the exterior. The furnace must have replaced some other original source of heat. Otherwise, there would be a chimney available.

Jim King
Reply With Quote
  #3  
Old 12/31/06, 11:58 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Single Wall Vent (Oil Furnace)

Hopefully their are other HVAC Contractors to call on to make repairs to this system.
The Service Tech. of note, should have to foot the bill and spend the time to make the repairs necessary to bring this system up to safe operating condition, if I'm enterpreting you pics accurately.

I can't believe any of this work was permitted and/or inspected/approved.
Reply With Quote
  #4  
Old 1/1/07, 12:42 AM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,091
Default Re: Single Wall Vent (Oil Furnace)

I do believe they have exceided the maximum allowable bends in a gas vent pipe.
They did have the right pitch though? lol

Man, can I spell or what? lol
Reply With Quote
  #5  
Old 1/4/07, 3:09 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Single Wall Vent (Oil Furnace)

Quote:
Originally Posted by jhagarty
Single wall furnace vent piping (Direct Vent - Induced Draft Fan).Piping runs approximately 50 feet to the front wall of the home.
(6) 45 degree bends.
(1) 90 degree elbow.
Depends on the size of the vent piping as compared to the equipment manufacturer specifications/recommendations. Longer runs and/or multiple bends generally need an increased direct vent piping size over the minimum (which will be the connection size at the equipment)

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Single wall furnace flue sspradling Inspecting HVAC Systems 8 6/29/07 8:23 PM
Single wall into B vent question sspradling Inspecting HVAC Systems 1 5/31/07 3:04 PM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 6:22 PM