Default To Sleeve or Not to Sleeve. That is the question

I recently had a situation and following discussion regarding chimneys and sleeving water heaters after a new furnace was installed. I have several pictures attached showing different problems all relating to homes with a direct vent furnace and no sleeve (or chimney liner) installed to the existing water heater.

Pictures 1-2-3 are from the same home. The lining looks to be in good shape for the 5% that is visible. No rain cap, no sleeve to the water heater, visible water at the bottom of the chimney. Looking at the 3rd photo, there was some evidence of back-drafting in the past shown with the melted pipe insulation.

Picture 4 shows a badly deteriorated flue liner (a chunk has fallen and is wedged in the chimney) with a direct vent furnace and an originally installed water heater. This home was built in the 1970's.

Picture 5 shows the top of the water heater where again evidence of back-drafting has occurred. Scorched top, melted insulators, etc. This water heater also vented to a chimney that was no longer used for the furnace.

If the chimney is no longer being used for any combustion appliance, I mention to my clients to consider removing the chimney at some point in the future to eliminate the maintenance that will be required at some point.

If the chimney is of original construction and designed for a water heater and furnace and the furnace is upgraded to a direct vent, the chimney size probably is no longer correct. This is the upper Midwest and we frequently see very cold temperatures (below freezing for months on end). Would this be a defect and the addition of a sleeve to the water heater be an option to be professionally evaluated and installed?
Attached Thumbnails
sleeve-not-sleeve-question-backdraft1.jpg   sleeve-not-sleeve-question-backdraft2.jpg   sleeve-not-sleeve-question-backdraft3.jpg   sleeve-not-sleeve-question-backdraft4.jpg   sleeve-not-sleeve-question-backdraft5.jpg  




Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
Find an InterNACHI certified Delaware Home Inspector (and anywhere else in North America)
  #2  
Old 4/6/09, 9:51 AM
John A. Sopher's Avatar
John A. Sopher John A. Sopher is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Oklahoma City, OK
Posts: 240
Default Re: To Sleeve or Not to Sleeve. That is the question

Hey thanks for posting these pics. We don't see this setup much here. Its nice to see some of the indicators before I see and miss them!



HLC Home Inspections



Okla. Lic. #776


I am licensed Realtor with Keller Williams. Office Phone # 405-691-2708
Reply With Quote
  #3  
Old 4/6/09, 7:01 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: To Sleeve or Not to Sleeve. That is the question

Here are a couple more pictures from the chimney clean-out. Both pictures are taken from the basement (dumb comment since I wouldn't expect a clean-out to be any other place on a single flue chimney ) of a two story home. Does anyone see a problem?

Both of these go along with the question stated earlier.
Attached Thumbnails
sleeve-not-sleeve-question-backdraft6.jpg   sleeve-not-sleeve-question-backdraft7.jpg  



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In

Last edited by gliebig; 4/6/09 at 7:10 PM..
Reply With Quote
  #4  
Old 4/6/09, 7:37 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: To Sleeve or Not to Sleeve. That is the question

Quote:
Originally Posted by gliebig View Post
Does anyone see a problem?
Yes, there are problems but you knew that.

The chimney is partially blocked and deteriorated and the connector pipe extends into the chimney too far and the water heater exhaust is condensing causing corrosive zinc oxide, etc. to bleed out from the pipe and it is backdrafting.

The cheapest fix may be to go electric with the water heater. A stainless steel liner may be the answer, too, but I would leave that up to the qualified professionals to decide.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 4/7/09, 10:59 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: To Sleeve or Not to Sleeve. That is the question

Quote:
Originally Posted by lkage View Post
Yes, there are problems but you knew that.
I wouldn't say I knew that, but I suspected a problem and referred it accordingly. When I asked my common question during the booking process "How did you hear about us?" He mentioned I was on a list from his Realtor but he did his research on the web and had decided to hire us even before he received the list. During the inspection I found out our client was the son-in-law of a local Realtor that I've worked with on occasion in the past. We've been hired by many Realtors and their family members to do their own inspections.

I had a great opportunity to help educate this Realtor during a follow-up call with the hopes of helping the importance and consistency of our industry. The feedback and comments from NACHI has been a tremendous help! Thank you!!



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #6  
Old 4/8/09, 1:04 PM
gkay gkay is offline
New User
 
Join Date: Jan 2009
Location: Olkanagan Valley British Columbiia Canada eh
Posts: 50
Please Note: gkay is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: To Sleeve or Not to Sleeve. That is the question

To answer your question I would definitely say that if you are using the clay chimney strictly for the gas water heater it would be oversized and should be lined with the appropriate size liner and as you stated be evaluated by a hvac contractor. For a water heater a 4 inch chimney liner is very typical.

About 1992 with the introduction of fan assisted venting of gas appliances the vent sizing tables for gas appliances have also changed to accommodate the changes in appliances and also addresses the type of construction of the home (air tightness)

Flue gas spillage can result from
1 most common blocked, damaged or deteriorating chimney or vent.
2 Spillage due to the vent of a natural gas appliance competing for air with other mechanical systems in the house or wood burning appliances. Pressure induced back drafting.
3 Spillage due to insufficient chimney draft because of poor chimney or vent design.
4 Poorly maintained equipment, cracked heat exchangers.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sump Pit/Pump Question Joey D'Adamo Plumbing Inspections 4 11/26/08 1:04 PM
Question for all... Bob Hopton-Jones General Inspection Discussion 9 4/6/07 7:43 AM
Basement Bathroom Venting Question Sean M. Jeric Plumbing Inspections 4 3/20/07 11:56 PM


All times are GMT -4. The time now is 7:10 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts