Old 8/21/06, 11:52 PM
Emmanuel J. Scanlan Emmanuel J. Scanlan is offline
Unhappy Stumped and can use some assistance!
O.K., I've definitely hit a wall on this one and could use some input. The picture below is of a 4" flue for a gas fired heater. The heater is in a small, properly sealed mechanical closet in the middle of the home. The flue is being run directly above and out but through what is suppose to be the upper combustion air opening.
Yes, the opening should not be screened and yes the flue is improperly supported by the screen mesh. What I can not find is a restriction for routing the flue through the upper combustion air duct. Yes it is wrong but I need a reference for the client to take to the builder. Between the upper and lower CA openings there is more than adequate CA opening, even with the flue in the way.
I can think of possible consequences but can't find a good reference.
A second question is that the lower CA opening is screened with 1/2" opening mesh. We all know why it should not be screened but the IRC only specifies not screening the end of the duct that terminates in the attic:
M1703.3Attic combustion air
4. The end of ducts that terminate in an attic shall not be screened.
Any good references for that also?
Knowledge is power, but sharing knowledge brings peace!
http://www.psinspection.com
TREC License# 7593
Professional Real Estate Inspections for the counties of Collin, Rockwall, Hunt, Dallas, Tarrant, Kaufman and all surrounding areas. If you want the the best you will find it with PS Inspection & Property Services LLC!
Old 8/22/06, 1:07 AM
Jeffrey R. Pope's Avatar
Default Re: Stumped and can use some assistance!
I'd love to help you here Manny, but I can't find anything specifically prohibiting this installation method.
Perhaps this can be applied. . .
M1402.3 Combustion air. Combustion air shall be supplied in accordance with Chapter 17. Combustion air openings shall be unobstructed for a distance of not less than 6 inches (152 mm) in front of the openings.
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Old 8/22/06, 1:32 AM
Jeff,
Actually that was a great help! Thanks.
That reference was intended for the space in front of the combustion area. But reading the IRC Commentary for the section you referenced they made reference to the following which I totally missed:
G2407.2 (304.2) Appliance/equipment location.
Equipment
shall be located so as not to interfere with proper circulation of
combustion, ventilation and dilution air.
Commentary for this section:
The provisions of Sections G2407 rely on the natural
(gravity) movement of air; therefore, installations must
allow unimpeded flow of combustion air from the
source to the appliances being supplied. Other me-
chanical systems, appliances, or equipment in the
same room or building can adversely affect the com-
bustion air supply. For example,when placed too close
to the combustion air openings, gas-fired appliances
or equipment will restrict the free circulation of air.
TREC License# 7593
Old 8/22/06, 8:37 AM
gbeaumont's Avatar
Hi Manny,
I also am not aware of any regulation that would prohibit this installation, but like yourself think it "looks wrong".
My thought is that convection currents resulting from the heat of the flue in the vent would iinterfere with the flow within the vent.
One thing to bare in mind though is that the IRC is not the last word on this subject as the Fuel gas section of the IRC is just a condensed version of the full International Fuel Gas Code, which may have more to say on the subject.
Regards
Gerry
(Mark B Adams)
NACHI cell 484-429-5466
NACHI02121106
Old 8/22/06, 6:39 PM
Thanks guys! I appreciate the input.
TREC License# 7593
Old 8/22/06, 7:41 PM
Brian E. Kelly's Avatar
http://www.codecheck.com/pg21_22mech...7combustionair
It is an old version but I like the drawings.