On December 1, my neighbourhood experienced a flash flood that brought 50+ inches of water, destroying my car, flooding the basement and completely submerging my new A/C condenser unit for approx 2 hours. After the (muddy) water receded, the temperature dropped to well below freezing for a couple of days.
I've talked to my HVAC guy, who thinks that the unit should survive relatively unscathed. I'm sure that some of the members have had experience with submerged units.... any comments / suggestions? Should I be doing something special when I start it up this season? Thanks in advance. Joe Skrypka MBA RHI CMI The Home Inspection Guy Inc. Hamilton, Ontario Canada Membership No. NACHI050062193 |
|
#2
|
|||
|
|||
|
Please Note:
Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
As a guess I would rinse the fins gently with water (and a garden hose?) and start it up before the season starts to see if it runs OK (assuming the temperature is not too cold). (1/23rd of an inch) 0.042 inches of dirt on an air conditioning coil can reduce it's efficiency by 21%. But be gentle. I'm sure the HVAC guy would have stung you with a bill if there was the smallest chance of a problem.
What about the unit on the inside of the house (I assume in the basement). Was this OK? I hate to think what a flood would do to my little condensate pump that sits just above the basement floor. The poor little thing would probably try to act like a sump pump, at 76 gallons per hour! If your condensate line discharges outside, you may want to flush this through with water to make sure it is not muddied up from the flood. Last edited by Ian Gills; 3/30/07 at 2:51 PM.. |
|
#3
|
|||
|
|||
|
Please Note:
briddle is a non-member guest and is in no way affiliated with InterNACHI or its members.
I would flush the fins and motor, (and any electronics) with water, to clean any muck from the entire unit. Since this is a sealed unit, it should not cause a major issue, in my opinion. Of course, you might want to shut off the breakers first.
|
|
#4
|
||||
|
||||
|
Quote:
</IMG> Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#5
|
|||
|
|||
|
Please Note:
bbenjamin is a non-member guest and is in no way affiliated with InterNACHI or its members.
I ditto what Charlie said,
Now is the time to use that parts warranty that came with your equipment. Be wary I have noticed a trend of insurance companies going belly up after natural disaters. I have had one of the properties I own in Charleston, SC drop by an insurance company simply because the wind zone changed. |
|
#6
|
||||
|
||||
|
Most people in these parts (myself included) don't carry flood insurance..... because it just doesn't happen that often, and it's very expensive...... so..... any repairs are on my nickel.
I'll try the garden hose flush (electricity disabled) and hope for the best. I'm assuming that the manufacturers warranty will still apply for any parts that I need replaced. Hopefully I'll only be paying for the labor to replace the effected parts. One more question. The flood water undermined the 24" x 24" paving stone that the unit sits on, and as a result it tilts down about 10 degrees on one side. What is the maximum tolerance for "off level"? Thanks again. Joe Skrypka MBA RHI CMI The Home Inspection Guy Inc. Hamilton, Ontario Canada Membership No. NACHI050062193 |
|
#7
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#8
|
|||
|
|||
|
Please Note:
Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#9
|
||||
|
||||
|
The major problem I see (and I go along with Charlie) is that most new equipment have single poll magnetic contactor's that only break one leg of electrical power to the unit. So, in light of this all of your electronics which was below water may have been damaged through short circuit to the water.
If your HVAC guy thinks there's nothing wrong with it being underwater, I would have him do the startup. |
|
#10
|
||||
|
||||
|
Quote:
They must be completely dried after the flood before any power is restored . . If this has to be done at home wash softly and well . I would put on a couple of heat lamps and make sure the equipment gets very warm for a few days. I have no idea on the electronics but what have you got to lose by doing the same thing Good luck and please keep us posted . Remember the left hand rule for all disconects. Roy Cooke Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#11
|
||||
|
||||
|
Thanks to all for their advice and suggestions...... great information.
Charley - My plan is to level the unit again, but I'm concerned about damaging the refrigerant lines - just how flexible are they? I've attached a picture for your reference - you can see how it tilts towards the house now. Joe Skrypka MBA RHI CMI The Home Inspection Guy Inc. Hamilton, Ontario Canada Membership No. NACHI050062193 |
|
#12
|
||||
|
||||
|
Yes, all is not lost.
Most of this equipment can be washed off as long as you don't turn it back on until is completely dry. However, some damage could occur from having 120 V passing through the components while underwater, so stand back when you turn it on! |
|
#13
|
||||
|
||||
|
Sorry - can't get the picture to upload.
Joe Skrypka MBA RHI CMI The Home Inspection Guy Inc. Hamilton, Ontario Canada Membership No. NACHI050062193 |
|
#14
|
||||
|
||||
|
Most residential refrigerant piping is soft drawn copper and can be bent easily as long as you don't allow it to crimp.
|
|
#15
|
||||
|
||||
|
Quote:
Roy Cooke Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| What is a 'condenser' dryer ?? | rcooke | Canadian Inspectors | 9 | 9/9/07 7:02 PM |
| Age of Goodman A/C condenser unit | pbarker | Inspecting HVAC Systems | 3 | 9/26/06 9:51 PM |
| Water heater combution near condenser unit | jlybolt | Inspecting HVAC Systems | 2 | 8/27/06 4:19 PM |
| Need Assistance on A/C Unit | pcarter-old-04 | Inspecting HVAC Systems | 9 | 6/21/06 7:23 AM |
| Condenser unit not level | loconnor | Inspecting HVAC Systems | 5 | 6/5/06 1:36 PM |