Default Supply Plenum Mounted High in Attic

I was measuring the difference in temperature between the return air vent and the supply vents in the second floor of this house today. The difference was around nine degrees. I know that's not the best place to take the measurements, but I'm not a HVAC guy. It was 80 degrees outside. I go in the attic and it jumps out at me that the supply plenum is mounted 7 feet off the bottom of the attic floor. It’s in the top of the attic space where it's hottest. Is that a really bad choice as to where to run the supply plenum? It just struck me as odd that the temperature differential was so low and then I see the plenum mounted in the hottest part of the attic space?
Attached Thumbnails
supply-plenum-mounted-high-attic-hvac.jpg  
Reply With Quote
  #2  
Old 4/3/07, 7:21 PM
bbenjamin bbenjamin is offline
New User
 
Join Date: Feb 2007
Location: Round O, SC
Posts: 45
Please Note: bbenjamin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Supply Plenum Mounted High in Attic

Skip,

More pictures are need to evaluate this system correctly.
Reply With Quote
  #3  
Old 4/4/07, 1:56 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Supply Plenum Mounted High in Attic

If you want to say something about where the plenum is mounted, why not say something about the lack of ventilation in the attic?

It doesn't matter how high it is located in the attic, if it's properly ventilated for HVAC purposes.

Ventilation requirements for an attic do not pertain when you install an HVAC system there.

An efficiency loss will occur because heat transfer is the area of the exposed duct , times the resistance factor (inverse of R-) of the insulation around the duct, times the temperature difference of the attic space and the supply air. For every degree Fahrenheit of increased heat in the attic equals one multiplier to the equation. So if you drop the temperature 100° (which is feasible) you can reduce the multiplier by 100! Quite substantial.
Reply With Quote
  #4  
Old 4/4/07, 3:00 PM
rmccullough rmccullough is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Arvada, CO
Posts: 272
Default Re: Supply Plenum Mounted High in Attic

I would recommend insulating the ducting in the attice areas. Heat loss in the winter, cooling loss in the summer.
Reply With Quote
  #5  
Old 4/4/07, 9:41 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Supply Plenum Mounted High in Attic

Skip

Here in Georgia, I see HVAC systems installed in the attic space all the time. I agree, it's not the best/optimum location to locate a system, but if designed and installed properly, they work fine and efficiently.
Your description tells me it is likely an Upflow Furnace setup, and although your PIC is limited, it does look like the plenum is sheetmetal and uninsulated. I recommend you check to see if the Plenums (S/A & R/A) are insulated on the inside. I'll assume the branch ductwork is insulated or flexduct.
Not sure what part of the country you're in, but the system should work fine.
Reply With Quote
  #6  
Old 4/6/07, 3:34 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Supply Plenum Mounted High in Attic

The amount if insulation makes no differance in the efficency loss!

I often see insulation on water pipes in unheated spaces that appear to be installed to keep water pipe from freezing. If you don't have a heat source, in this case water is never used on an outside faucet in the wintertime, it will freeze. Insulation does not keep the heat loss from occurring, it simply slows it down.

If the attic space is 190° and you're trying to make 50° air, the temperature differential is a multiplier of 140! If you have adequate ventilation and lower the attic temperatures to 95° (outdoor air temperature), there is a multiplier of only 45. That is a 68% reduction in heat gain in the supply air!

HVAC attic ventilation is the cheapest and most efficient means of reducing power consumption and increasing efficiency. The business of HVAC means heating/ventilation/air-conditioning. No one ever discusses the ventilation part of it! Actually I see trucks running around that don't have the "V" in there! It's H/AC!
Reply With Quote
  #7  
Old 4/7/07, 11:07 AM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,025
Default Re: Supply Plenum Mounted High in Attic

Not to mention the reduced heat gain to the interior of the home.



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Is inadequate roof or attic ventilation a defect? gliebig Exterior Inspections 85 1/16/08 7:56 PM
Spray Foam to the Rescue ? mcyr Structural Inspections 3 3/27/07 8:29 PM
Furnace in attic (High Efficient) jcordell Inspecting HVAC Systems 14 2/10/07 7:02 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 6:58 PM
Vertical furnaces mounted directed in drip pan in the attic knorton Inspecting HVAC Systems 1 8/28/06 9:06 AM


All times are GMT -4. The time now is 6:11 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts