Default surface yellow gas flex piping?

I am assuming that running flex gas piping on the exterior of a finished wall, or inside a finished wall, is not code, but I cannot find the code justification for it - can someone please help me with this one? It is yellow flex piping as shown in the attached photo. It connects two ends of a rigid steel gas pipe which eventually feeds a gas range. Thanks in advance for any help on this
Attached Thumbnails
surface-yellow-gas-flex-piping-joannesutro-015.jpg  
Reply With Quote
  #2  
Old 11/28/06, 2:07 AM
jclark1's Avatar
jclark1 jclark1 is offline
Active Poster
 
Join Date: Nov 2005
Location: Vashon, Wa
Posts: 644
Please Note: jclark1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: surface yellow gas flex piping?

From what I've read, it depends on the local jurisdiction. All of the major codes allow it per manufacturers instructions. If it is adequately sized, the correct fittings are used, it's supported and it is not subject to physical damage it should be ok. I'm sure that someone here is more experienced with CSST than me and hopefully can look at your pic and see if there is a problem. Here is a link to a Design and Installation Guide of a major manufacturer of CSST. http://www.gastite.com/include/langu...IGuide2006.pdf
Reply With Quote
  #3  
Old 11/28/06, 2:26 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: surface yellow gas flex piping?

Current construction standards as a guide ("code" is a dirty word for an HI) usually require installation in accordance with manufacturer's instructions, which usually require protection if "subject to physical damage". That last part is usually a judgment call.

JMO



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #4  
Old 11/28/06, 7:45 AM
bsumpter bsumpter is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Martinez, CA
Posts: 232
Default Re: surface yellow gas flex piping?

Don't forget about the lawsuit regarding CSST piping.



Brian R. Sumpter
First Call Inspections
Proudly serving most Bay Area Counties

www.firstcallinspections.com
Reply With Quote
  #5  
Old 11/28/06, 9:11 AM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,846
Default Re: surface yellow gas flex piping?

I don't believe the flex gas lines and the CSST are the same animal. Flex has been around since Col Sanders was a corporal. CSST is a relatively newer product.
Reply With Quote
  #6  
Old 11/28/06, 11:16 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: surface yellow gas flex piping?

Quote:
Originally Posted by Coral
I am assuming that running flex gas piping on the exterior of a finished wall, or inside a finished wall, is not code...
If not on a wall or in a wall, then where would it be allowed??? If CSST, it has to be protected from potential damage as someone already stated. CSST can be run anywhere other types of gas lines are installed. If a gas appliance connector, it cannot be run through walls or floors.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 11/28/06, 11:17 AM
bsumpter bsumpter is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Martinez, CA
Posts: 232
Default Re: surface yellow gas flex piping?

Cant tell from the pic, but it depends on the brand stamped onto the line.

Just in case someone needs this:

CSST consists of a continuous, flexible, stainless steel pipe, and typically is covered with a yellow exterior plastic coating. In the case of one of the products manufactured by OmegaFlex, called "COUNTERSTRIKE," the product is covered with a black exterior coating with yellow lettering. CSST typically is routed beneath, through and alongside floor joists, inside interior wall cavities and on top of ceiling joists in attic space from a gas source to an appliance.

Titeflex's CSST product is known as "GASTITE,"
Ward's CSST product is known as "WARDFLEX,"
OmegaFlex’s CSST is known as "TRACPIPE" or "COUNTERSTRIKE,"
Parker Hannifin’s CSST product is known as "PARFLEX."

Typically, these products may be visible along floor joists, above basements, in attic spaces, or connected to exposed appliances such as water heaters. The piping should be stamped with a manufacturer’s mark.



Brian R. Sumpter
First Call Inspections
Proudly serving most Bay Area Counties

www.firstcallinspections.com
Reply With Quote
  #8  
Old 11/28/06, 2:36 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: surface yellow gas flex piping?

Quote:
Originally Posted by dedwards
I don't believe the flex gas lines and the CSST are the same animal.
In my mind CSST is a type of flexible gas piping. Flexible tubing and appliance connectors are also types of flexible gas piping. I just assumed it was CSST (has a plastic outer yellow jacket) from the photos, since it didn't look like flexible tubing (just painted yellow).

Here are some pics of the various basic flexible gas piping types (the first one is CSST, the second flexible tubing, and the last an appliance connector). But the bottom line is any flexible gas piping needs protection when "subject to damage" ... even appliance connectors.

[P.S. There is also a newer type of flex gas piping similar to CSST with an additional thick outer protective jacket which I understand is rated for direct burrial, but I didn't have a pic of that]

JMO
Attached Thumbnails
surface-yellow-gas-flex-piping-csst-gas-pipe.jpg   surface-yellow-gas-flex-piping-gas-flex-tubing.jpg   surface-yellow-gas-flex-piping-gasapplianceconnector.jpg  



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 11/28/06 at 2:44 PM..
Reply With Quote
  #9  
Old 11/28/06, 5:44 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: surface yellow gas flex piping?

P.S.S. Note the second pic with the painted yellow flex gas tubing is a good example of how flex gas piping should be connected to a furnace/boiler. Note that the flex pipe does not pass through the equipment knockout, but is instead connected to rigid pipe that projects out.

Running flex gas piping through an equipment knockout is a classic no-no that should get written up every time.

JMO



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #10  
Old 11/28/06, 7:29 PM
apolillo's Avatar
apolillo apolillo is offline
Active Poster
 
Join Date: Nov 2004
Location: Baltimore, Md
Posts: 191
Please Note: apolillo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: surface yellow gas flex piping?

that 90 degree bend is problamatic.
Reply With Quote
  #11  
Old 11/28/06, 7:39 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: surface yellow gas flex piping?

Anatol...I thought so too until I read Table 4-1 on pg 49 of the Gastite Installation Guide shown in post #2, now I'm not so sure.
Reply With Quote
  #12  
Old 11/28/06, 7:42 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: surface yellow gas flex piping?

Quote:
Originally Posted by roconnor
P.S.S. Note the second pic with the painted yellow flex gas tubing is a good example of how flex gas piping should be connected to a furnace/boiler. Note that the flex pipe does not pass through the equipment knockout, but is instead connected to rigid pipe that projects out.

Running flex gas piping through an equipment knockout is a classic no-no that should get written up every time.

JMO
I realize it's off topic but does the lack of a dust/drip leg in photo 2 bother anyone?
Reply With Quote
  #13  
Old 11/29/06, 12:23 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: surface yellow gas flex piping?

Quote:
Originally Posted by mlarson
I realize it's off topic but does the lack of a dust/drip leg in photo 2 bother anyone?
Not me.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #14  
Old 11/29/06, 4:41 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: surface yellow gas flex piping?

Quote:
Originally Posted by apolillo
that 90 degree bend is problamatic.
Although a larger radius sweep is desirable, with Pic #2 as a prime example, very tight bends for that type of flex piping are allowed (note it's not typical CSST, but painted flexible tubing).


Quote:
Originally Posted by mlarson
I realize it's off topic but does the lack of a dust/drip leg in photo 2 bother anyone?
That is a pic of a short run of flexible tubing between the main lines and the equipment connection at the top I believe. But if there was no dirt/drop leg at a low point I would agree that is a concern.

JMO



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #15  
Old 11/29/06, 5:16 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: surface yellow gas flex piping?

I think he was referring to the CSST bend in the original photo, I know I was.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you put polybutylene in the Summary? jfunderburk Plumbing Inspections 41 4/5/12 6:43 AM
Bonding both hot and hold supply pipes kshepard Plumbing Inspections 22 5/4/08 8:00 AM
Bonding Piping 101....Good To Know ! pabernathy Electrical Inspections 37 4/28/07 11:25 AM
Yellow Pages vs Internet vs Realtor jmckenna1 Miscellaneous Discussion for Inspectors 13 9/17/06 2:09 PM


All times are GMT -4. The time now is 7:14 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts