Default Tee Vent connection & dirt leg.

I am suspect of the tee connection above the tank as I believe CO can spill out. I have never seen one installed like this. Am I correct or is this OK.

The dirt leg is missing, because if it was installed correctly you wouldnt be able to open the filter door.

Thanks for any input on the vent.

Dave
Attached Thumbnails
tee-vent-connection-and-dirt-leg-72106-parma-041-small-.jpg.jpg
Views:	64
Size:	55.8 KB
ID:	4004   tee-vent-connection-and-dirt-leg-72106-parma-042-small-.jpg.jpg
Views:	64
Size:	43.9 KB
ID:	4005  
Reply With Quote
  #2  
Old 6/12/06, 11:38 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,753
Default Re: Tee Vent connection & dirt leg.

I believe you are correct David. The exhaust vent should slope up.
Where does the tee go to?



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #3  
Old 6/13/06, 12:09 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,703
Default Re: Tee Vent connection & dirt leg.

Sizing is incorrect also.

The main flue must be the size of the largest plus half of the second.

P/T valve pipe not w/in 6" of floor.
Reply With Quote
  #4  
Old 6/13/06, 7:20 AM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,466
Default Re: Tee Vent connection & dirt leg.

Brian

The Tee or wye is from the furnace. I did document the PT extension.

I just didnt look right and I recommended that it would be corrected so it wouldnt backdraft.

Dave
Reply With Quote
  #5  
Old 6/13/06, 12:12 PM
jmcmahan jmcmahan is offline
InterNACHI Member
 
Join Date: May 2006
Location: Jamestown, Oh
Posts: 9
Default Re: Tee Vent connection & dirt leg.

in ohio the furnace flue has to vent below the water heater flue. i have installed heating and air for 17 years.the way this is flued will cause water heater to back draft. needs fixed
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Plumbing vent next to exhaust vent mpettitt Plumbing 4 10/12/07 6:38 PM
Air admittance valves everywhere apfaff Plumbing 13 4/16/07 10:17 AM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Misc. Discussion 8 1/25/07 6:22 PM
Flue vent connection for water heater hspinnler Plumbing 11 5/11/06 10:56 PM


All times are GMT -4. The time now is 1:33 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts