  #1  
Old 12/17/07, 4:16 PM
Kevin R. Weiss Kevin R. Weiss is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Rowlett, TX
Posts: 842
Default Temperature differential in a home

I have had a number of clients complain about HVAC control in their homes. Generally, there is a room that they say is too hot of cold (depending on the season.) Several have thrown out different numbers as "official" allowable temperature differences within the home - 4 degrees, 6 degrees etc.

I have not been able to find a specific differential number like this. Is there such a number/rule? If so, where are the reading supposed to taken at?
Reply With Quote
  #2  
Old 12/17/07, 4:47 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Temperature differential in a home

Quote:
Originally Posted by kweiss
I have had a number of clients complain about HVAC control in their homes. Generally, there is a room that they say is too hot of cold (depending on the season.) Several have thrown out different numbers as "official" allowable temperature differences within the home - 4 degrees, 6 degrees etc.

I have not been able to find a specific differential number like this. Is there such a number/rule? If so, where are the reading supposed to taken at?
If you are asking is there a code specific regulation the answer would be no.

The national association generally excepts 2 to 3 degree duct loss as acceptable for residential duct work. In my experience most hot pockets are self inflected poor installation, poor duct design inadequate ventilation for attic installs. old or missing insulation on the attic duct, Return air drawing in non-conditioned air, improper air balancing at the registers. The list is just endless.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #3  
Old 12/17/07, 5:57 PM
Kevin R. Weiss Kevin R. Weiss is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Rowlett, TX
Posts: 842
Default Re: Temperature differential in a home

Thanks Charley, that is exactly what I was asking.

I spend much time on these type clients explaining all of the different things which can negatively affect the performance and that, to my knowledge, there were no "code" type guidelines on this, just accepted guidelines or rules of thumb. But occasionally someone is just sure, such exists and presses me.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 10:46 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts