Default Termination of furnace vent

Power vented furnace terminated underneath a deck. The termination was 5ft away from opening slider panel on glass sliding door and 5 ft away from an opening window. If I remember correctly that was an acceptable distance. Is that correct?
Reply With Quote
Find an InterNACHI certified Colorado Home Inspector (and anywhere else in North America)
  #2  
Old 10/27/09, 10:08 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: Termination of furnace vent

Part V- Mechanical
Chapter 18 Chimneys and Vents
Section M 1804 Vents

M1804.2.5 Direct vent terminations.
Vent terminals for direct-vent appliances shall be installed in accordance with the manufacturer’s installation instructions.

M1804.2.6 Mechanical draft systems.
Mechanical draft systems shall be installed in accordance with their listing, the manufacturer’s installation instructions and, except for direct vent appliances, the following requirements:

1. The vent terminal shall be located not less than 3 feet (914 mm) above a forced air inlet located within 10 feet (3048 mm).

2. The vent terminal shall be located not less than 4 feet (1219 mm) below, 4 feet (1219 mm) horizontally from, or 1 foot (305 mm) above any door, window or gravity air inlet into a dwelling.

3. The vent termination point shall not be located closer than 3 feet (914 mm) to an interior corner formed by two walls perpendicular to each other.

4. The bottom of the vent terminal shall be located at least 12 inches (305 mm) above finished ground level.

5. The vent termination shall not be mounted directly above or within 3 feet (914 mm) horizontally of an oil tank vent or gas meter.

6. Power exhauster terminations shall be located not less than 10 feet (3048 mm) from lot lines and adjacent buildings.

7. The discharge shall be directed away from the building.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #3  
Old 10/27/09, 10:23 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 243
Default Re: Termination of furnace vent

Thanks Larry, I was thinking it was 3 ft. The fall colors are probably well over by now I suppose.....I lived in Alpena, MI for about 14 years, you know the wrong side of I-75. Used to work for a fellow that owned Great Lakes Pipe and Supply. We had supply house's in Petoskey, Gaylord, Alpena etc.
Reply With Quote
  #4  
Old 10/27/09, 10:26 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: Termination of furnace vent

You're welcome.

We had the first sunny day in a while today and the colors were nice...but winter, she is a comin'.

Hope you and yours are well.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Direct vent oil furnace question Bart Connors HVAC 6 7/29/08 8:55 AM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 2:26 AM
Vent for Electric Furnace?? mlong HVAC 5 11/7/07 10:16 AM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Misc. Discussion 8 1/25/07 6:22 PM


All times are GMT -4. The time now is 8:51 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts