My question is on RLA's, (Run Load Amps) Does anyone know what the range of the measured RLA's should be compared to the data plate? Thanks! Dave |
|
#2
|
||||
|
||||
|
Generally guidelines, 60-90%, FLA too
************************************** Shawn Rowe, CMI HomeFirst Inspection Services, LLC - InfraRed Specialist (Level 1 & Building Science certified) - Code Certified Residential Building Inspector - Certified Master Inspector -- Serving NE Florida, St. Johns, Duval, Flagler, Putnam counties -- |
|
#3
|
||||
|
||||
|
Quote:
Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#4
|
||||
|
||||
|
Quote:
|
|
#5
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
It can show you if a compressor may be going bad. If it is pulling too many amps, there is a reason. Better to report it than get a phone call a few weeks later that the unit does not work. Its just one more little thing we can do that could save us a lot of money with little effort.
|
|
#6
|
||||
|
||||
|
Quote:
|
|
#7
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
A lot of times I will check it at the disconect. As you stated: "There are numerous reasons that can and do create excessive amp draw on a compressor such as a dirty condenser, Condenser fan motor rotating backwards, Condenser fan motor not running at MFG design speed or a wrong RPM fan motor installed". I do not diagnose why the amperage draw is high, I just state that it needs to be repaired by a licensed air conditioning company. We are stating a condition, not the remedy.
|
|
#8
|
||||
|
||||
|
Quote:
We could check water pressure and water flow . We could check the voltage and see if it too high or too low. Incidentally these things also change at different times of the Day. I am so glad to see all the Home Inspectors before us ( This I think is in all Associations) set a sensible SOP. When we start exceeding the SOP our liability goes up not down. I like the system we have now and do not like the idea of 6 hour inspections . I have enough trouble with those who charge too little . Roy Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#9
|
||||
|
||||
|
Quote:
|
|
#10
|
||||
|
||||
|
Quote:
|
|
#11
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Roy,
SOP is a minimum standard. It takes me an extra minute to take a reading. I have had too many instances where the system was charged for the inspection and it dies a couple of days later. If the unit is easily accessible, I will pull off the cover panel and inspect the wires. I cannot tell you how many times the wires are burned or corroded. I guess i got tired of hearing the AC guy say the inspector should have seen this. A little extra work goes a long way in warding off those phone calls. Charley, I never state that the compressor is bad, just that the reading is high, which could mean a possible problem. This way it gets deferred to a licensed air conditioning company for repair. As we both know, there are many issues which could cause a high reading. I am not diagnosing, just reporting what I see or can test easily. |
|
#12
|
||||
|
||||
|
Quote:
When does an air-conditioning guy know anything about what a home inspector is supposed to do? It appears to me that the HVAC contractor is operating outside of his license and is violating the home inspection laws in many states when he provides information to your client concerning home inspection. In my opinion this performing home inspection services without a license. I'm going to test the waters on this one. Does anyone have any opinion on this? A large majority of lawsuits against home inspectors or outside of court settlement is generated because of what a home inspector was supposed to do in accordance with an HVAC contractor. An HVAC contractor will be the first to say that a home inspector knows nothing about HVAC but they are also the first to tell the client what you the home inspector was supposed to do. I think I will carry this thread over to the legal section and get Joe Ferry's opinion on this, if you wish to join us. |
|
#13
|
||||
|
||||
|
Quote:
When I find a motor that is leaking oil, that may not spin freely, is heavily rusted etc. I sometimes test the RLA just to see if it exceeds the manufacturers specifications. This is just further backup for noting deterioration of the component. Just because a motor seal is leaking does not mean it is "not functional". However the motor does become "not functional" when oil leakage is apparent, overheated motor casing is detected, and/or RLA exceeds manufacturers specifications. |
|
#14
|
||||
|
||||
|
[quote=dandersen]One word of caution about using RLA/FLA (which by the way is the same thing) to evaluate operating conditions of HVAC equipment.
Wow David that was some One Word. Do you like RLA as determining factor for further evaluation or not. I personally do not to many variables. |
|
#15
|
||||
|
||||
|
Negative, I sometimes take the RLA for my own reference so I know how much emphasis to put on the repair/evaluation.
Yeah, my one-word often gets carried on. Like RRay, I use voice dictation and it's easy to get carried away! |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Moisture in slabs | mcyr | Structural Inspections | 7 | 8/20/07 7:33 PM |
| bbbb | mcyr | Structural Inspections | 1 | 8/19/07 10:26 PM |
| Soil Testing | Mike Jewett | Ancillary Inspection Services & Additional Topics | 2 | 7/20/07 7:43 AM |
| Arizona, one day mold cert | dbucknavich | General Inspection Discussion | 4 | 6/26/06 9:32 PM |