Measuring and reporting the RLA is not the same as calling for an evaluation.

In our area, A/C is a huge issue. If we report the condition and document the facts, then the A/C contractor can't tell the new owner " your home inspector should have told you xyz was bad."

If you measure all the A/C's you encounter during the day, you will soon learn what is "normal" and what is not "normal" for each size range and type of unit. In Florida, every house has central A/C, so you get proficient quickly.

Measure the draw, report it, (good or bad, it's just data), and if it's too high (exceeds the mfr. data plate for example) call it out for repairs.

It is a liability control for A/C inspections.

Dom.
Reply With Quote
  #17  
Old 12/11/06, 3:21 PM
Justin Watts Justin Watts is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Rancho Santa Margarita, CA
Posts: 771
Default Re: Testing RLA's

RLA..... way to specialized for me....
Reply With Quote
  #18  
Old 12/11/06, 5:02 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Testing RLA's

Quote:
Originally Posted by Dom D'Agostino
.



Measure the draw, report it, (good or bad, it's just data), and if it's too high (exceeds the mfr. data plate for example) call it out for repairs.

It is a liability control for A/C inspections.

Dom.
Just curious have you ever found a unit that exceeded its name data for amperage draw.
Reply With Quote
  #19  
Old 12/11/06, 5:27 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Testing RLA's

Quote:
Originally Posted by jwatts1
RLA..... way to specialized for me....
Me too Justin. Next we will be measuring furnace BTU's in actual operating conditions.
Reply With Quote
  #20  
Old 12/11/06, 6:06 PM
Dom D'Agostino Dom D'Agostino is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Jan 2006
Location: Central Florida
Posts: 45
Please Note: Dom D'Agostino is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Testing RLA's

Quote:
Just curious have you ever found a unit that exceeded its name data for amperage draw.
Yes, many have had high readings. Typically older, or otherwise "challanged" units. Feedback from clients has been that the system needed expensive repairs or, sometimes, replacement.

Dom.
Reply With Quote
  #21  
Old 5/22/11, 8:07 AM
Richard Luciano Richard Luciano is offline
New User
 
Join Date: May 2011
Posts: 1
Please Note: Richard Luciano is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Testing RLA's

RLA is Rated Load Amps not Running Load Amps. RLA is not used to determine if the compressor is running correctly.RLA is a rating point that manufactures use to help guide you in selecting a contactor for a compressor.The running amps of a compressor are determined by the evaporator temperature, condensing temperature and the line voltage."Running Amps" vary depending on conditons or load, never confuse with "RLA", for the various amp ratings view a compressor curve sheet"
Reply With Quote
  #22  
Old 5/22/11, 12:53 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: Testing RLA's

I completely agree with Anderson.
Think of the air conditioning as being a car without oil. Will it use more fuel or seize right up.
The fact of checking the oil is the job of all gas station attendants when asked. Is this in their standards of practice? No!
To test the RLA without being a HVAC tech is no different.
You will only receive a call from your local AHJ.
If you are an HVAC tech do this as a side option to your business. This way you will not confuse the public as to what should be done on a home inspection.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Moisture in slabs mcyr Structural Inspections 7 8/20/07 7:33 PM
bbbb mcyr Structural Inspections 1 8/19/07 10:26 PM
Soil Testing Mike Jewett Ancillary Inspection Services & Additional Topics 2 7/20/07 7:43 AM
Arizona, one day mold cert dbucknavich General Inspection Discussion 4 6/26/06 9:32 PM