Are you asking about the equipment, or are you asking about the code reference?
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#19
|
||||
|
||||
|
Both.
|
|
#20
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
They don't want smoke, CO or other vapours re-circulated through the central system. |
|
#21
|
||||
|
||||
|
Quote:
I'll get you the reference later Bob. I'm headed out this evening for a little R&R. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#22
|
||||
|
||||
|
|
|
#23
|
||||
|
||||
|
Is that the best technical answer you have?
|
|
#24
|
||||
|
||||
|
For someone not familiar with basic Garage Wall Fire Safety requirements, Yes.
|
|
#25
|
||||
|
||||
|
Quote:
|
|
#26
|
||||
|
||||
|
CA Code and Uniform Code
406.1.4 Separation. Separations shall comply with the following: 2. Ducts in a private garage and ducts penetrating the walls or ceilings separating the dwelling unit from the garage shall be constructed of a minimum 0.019-inch (0.48 mm) sheet steel and shall have no openings into the garage. 716.5 Where required. Fire dampers, smoke dampers, combination fire/smoke dampers and ceiling radiation dampers shall be provided at the locations prescribed in Sections 716.5.1 through 716.5.5 and Section 716.6. Where an assembly is required to have both fire dampers and smoke dampers, combination fire/smoke dampers or a fire damper and a smoke damper shall be required.
716.5.1 Fire walls. Ducts and air transfer openings permitted in fire walls in accordance with Section 705.11 shall be protected with listed fire dampers installed in accordance with their listing. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#27
|
||||
|
||||
|
Quote:
|
|
#28
|
||||
|
||||
|
Smoke and fire dampers have sensors for smoke and fire. The dampers posted in this thread are controlled by thermostats.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
![]() |