Sorry no pictures for this but I walk into the garage there is a 24 inch updraft vent fan in the ceiling of the attached 2 car garage. The roof is gable with end vents and clay tile.
The fan is thermostatically controlled.

So the question is? any other faults besides the negation of the fire rating for the garage, drawing combustion fumes into the attic, and the negative pressure created in the garage when the door is closed?



Ken Dolin
Kenco Home Inspections
WWW.Kenco.org
State of Florida Licensed Home Inspector HI 59
Reply With Quote
Need a home inspection in Vermont? Check out InterNACHI's listing of Vermont certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/17/10, 2:42 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Thought on this vent system

Other than a possible breach in the fire wall, I would also be very concerned about CO finding it's way into the home.
Reply With Quote
  #3  
Old 8/17/10, 4:10 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Thought on this vent system

Needs to be vented out the sidewall or removed.(Period)!
Reply With Quote
  #4  
Old 8/17/10, 5:19 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Thought on this vent system

Quote:
Originally Posted by belliott View Post
Needs to be vented out the sidewall or removed.(Period)!
Not necessarily true Bob.
Reply With Quote
  #5  
Old 8/17/10, 5:26 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Thought on this vent system

Firewall issue.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #6  
Old 8/17/10, 5:49 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is online now
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Thought on this vent system

Was there a damper on the opening? Sometimes they have normally open contacts that are hooked up to the smokes. When the smokes go into trouble, the damper automatically closes.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #7  
Old 8/17/10, 5:56 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Thought on this vent system

Currently as described I would agree it is a Firewall issue....

Call out the defect and move on...

There may be many ways to correct the situation, and it is up to the Client as to how this work is done.

For a HI to tell anyone that there is one way to correct this is not very clever.

Of course some of the 4 hours inspectors just do not know when to keep quiet..... Hence the long draaaaaaaaaaaawn out inspections......
Reply With Quote
  #8  
Old 8/17/10, 8:02 PM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: Thought on this vent system

Was the area above the fan able to be viewed? If so, does the vertical portion of the vertical/wall firewall extend up to the roof? I mention this to rule out whether the d/wall on the ceiling was added after original construction.

All things equal... there may be 2 issues here. But simply put, if you can't see the firewall extend and properly divide the living space and the garage you should call it out, whether it's that the fan violates the integrity of the firewall OR that you can't see/confirm the firewall, this is up to you as you were there. Basic firewall construction and protection is just that .... basic.

The fan/pressurization issue is another one entirely.. fuel burning appliances and so on.

Speaking of Dry-Walled garage ceilings

I see a fair amount of Dry-walled garages that originally were just a firewall that extended up into the trusses or roof framing and unfinished studs and walls, kinda like an unseedy club. Well, many times the drywall is put on after the fact by a less than knowledgeable contractor or a Home Owner and creates an area with NO ventilation, just Damp Framing Then a few years later, Saggy Framing. If you haven't seen the movie Soggy Framing Boys by the COHN Brothers... it's a goodie BTW.



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #9  
Old 8/18/10, 10:55 AM
Kenneth Dolin's Avatar
Kenneth Dolin Kenneth Dolin is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Palm Beach County, Florida
Posts: 502
Default Re: Thought on this vent system

There was no attempt here to comply with ANY codes or safety issues. There was no fusible link automatic closing fire damper, it vents directly into the attic that has a straight shot through the entire attic. no vents in the garage walls or door. The register on the face of the fan was not even like the old whole house fans that opened upon operation.
I think this was installed by the AC guy to prevent condensate buildup on the air handler located in the attic, by reducing the attic temp.



Ken Dolin
Kenco Home Inspections
WWW.Kenco.org
State of Florida Licensed Home Inspector HI 59
Reply With Quote
  #10  
Old 8/18/10, 11:05 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Thought on this vent system

Quote:
Originally Posted by bkelly2 View Post
Not necessarily true Bob.


......and your alternatives ?.or are you just spouting till someone else answers for you.
Reply With Quote
  #11  
Old 8/19/10, 1:16 AM
dproulx dproulx is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: edmonton alberta canada
Posts: 8
Send a message via MSN to dproulx
Default Re: Thought on this vent system

Quote:
Originally Posted by kdolin View Post
Sorry no pictures for this but I walk into the garage there is a 24 inch updraft vent fan in the ceiling of the attached 2 car garage. The roof is gable with end vents and clay tile.
The fan is thermostatically controlled.

So the question is? any other faults besides the negation of the fire rating for the garage, drawing combustion fumes into the attic, and the negative pressure created in the garage when the door is closed?
drawing fumes into the attic should be a concern on the account if there is no fireproofing in the attic if attached to the house. if the two attics are not sperated then yes major concern. if detached other than neg pressure the venting should be able to disharge the fumes created by stored chemicals/gasoline etc. my question is why the vent. is this client a painter and using the garage as a spray booth? look around for clues that might help to understand why it is there. and then make your notes into the report you create. this is my opinion but take it for whats its worth for i'm new into home inspecting but have a variety of construction background

Last edited by dproulx; 8/19/10 at 1:19 AM.. Reason: spell check
Reply With Quote
  #12  
Old 8/19/10, 1:39 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Thought on this vent system

Quote:
Originally Posted by belliott View Post
......and your alternatives ?.or are you just spouting till someone else answers for you.
Bob, I can think of a number of ways to correct the defect.

But telling a Client that "The only way" to fix something is "This" is asking for trouble, IMO.

You will get someone who comes along after you that will say something else, and in this case they will be right.
Reply With Quote
  #13  
Old 8/19/10, 2:26 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Thought on this vent system

Quote:
Originally Posted by bkelly2 View Post
Bob, I can think of a number of ways to correct the defect.

But telling a Client that "The only way" to fix something is "This" is asking for trouble, IMO.

You will get someone who comes along after you that will say something else, and in this case they will be right.
OK name one.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pellet stove help chellickson General Inspection Discussion 23 8/19/10 1:23 AM
A little on the Commercial side of things. mcyr General Inspection Discussion 457 8/1/09 10:50 AM
Air Vent Inc. "FREE" Seminar in Toronto mkyriacou Canadian Inspectors 10 2/13/09 10:30 AM


All times are GMT -4. The time now is 12:23 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts