The tpr extension on the home I just inspected went through the floor and terminated in the crawlspace. If it starts discharging, the homeowner will never know because it is discharging into the crawlspace. Do I write this up?
|
|
#2
|
||||
|
||||
|
504.6 Requirements for discharge piping. The discharge piping serving a pressure relief valve, temperature relief valve or combination thereof shall: 1. Not be directly connected to the drainage system. 2. Discharge through an air gap located in the same room as the water heater. 3. Not be smaller than the diameter of the outlet of the valve served and shall discharge full size to the air gap. 4. Serve a single relief device and shall not connect to piping serving any other relief device or equipment. 5. Discharge to the floor, to an indirect waste receptor or to the outdoors. Where discharging to the outdoors in areas subject to freezing, discharge piping shall be first piped to an indirect waste receptor through an air gap located in a conditioned area. 6. Discharge in a manner that does not cause personal injury or structural damage. 7. Discharge to a termination point that is readily observable by the building occupants. 8. Not be trapped. 9. Be installed so as to flow by gravity. 10. Not terminate more than 6 inches (152 mm) above the floor or waste receptor. 11. Not have a threaded connection at the end of such piping. |
|
#3
|
||||
|
||||
|
Please Note:
cbrands is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
#7 says it all. |
|
#4
|
||||
|
||||
|
Please Note:
cfuoco is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thank you!
|
|
#5
|
||||
|
||||
|
Here's what I say:
"The discharge pipe from the pressure relief valve discharges into the crawl space, where any leaks would not be noticed. It should be plumbed to a conspicuous exterior location and terminate no more than twenty-four inches above grade and no closer than six inches to it, or it should discharge to a concrete floor in a conspicuous area where no damage would result." “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Garage door opener extension cord | cfolsom | Electrical Inspections | 4 | 11/22/07 12:49 PM |
| Extension Cords in Crawl Spaces | Skip Erwin | Electrical Inspections | 10 | 6/25/06 3:39 PM |
| Extension Cord Wiring | psmothers | Electrical Inspections | 1 | 6/4/06 9:11 PM |
| Joe F, update? | jtedesco1 | Electrical Inspections | 54 | 4/10/06 10:35 AM |