  #1  
Old 12/3/07, 7:12 PM
wsutton's Avatar
wsutton wsutton is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Nashville, Tn
Posts: 33
Default Trane Heat Pump

A Trane split system heat pump, only hvac system installed in a 2100 square foot home. Model # is TWR730A100A1 , manufactured 09/91. I determine this unit to be 2.5 tons, that would be under sized for 2100 square feet. Does anyone have info on this model # to confirm this is a 2.5 ton unit ?
Thanks in advance.
Reply With Quote
  #2  
Old 12/3/07, 7:56 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,161
Send a message via MSN to bwiley
Default Re: Trane Heat Pump

That would be a two and a half ton unit. To determine whether it is the proper size or not would require a load calculation.



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #3  
Old 12/3/07, 8:39 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,466
Default Re: Trane Heat Pump

Model # is TWR730A100A1

30/12 = 2.5



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #4  
Old 12/3/07, 9:00 PM
wsutton's Avatar
wsutton wsutton is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Nashville, Tn
Posts: 33
Default Re: Trane Heat Pump

This inspection is tomorrow, I went by to look at the HVAC this afternoon, the reason I wanted confirmation on the size is because I have never seen a 2.5 ton unit serving a two story 2100 square foot home, if the heat operates my job is done. I will recommend when the unit is replaced, it is 15 years old, the HVAC contractor do a load calculation for proper size of new unit.

Last edited by wsutton; 12/3/07 at 9:06 PM..
Reply With Quote
  #5  
Old 12/4/07, 9:52 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,873
Default Re: Trane Heat Pump

Quote:
Originally Posted by wsutton
This inspection is tomorrow, I went by to look at the HVAC this afternoon, the reason I wanted confirmation on the size is because I have never seen a 2.5 ton unit serving a two story 2100 square foot home, if the heat operates my job is done. I will recommend when the unit is replaced, it is 15 years old, the HVAC contractor do a load calculation for proper size of new unit.
Very unlikely that a 2-1/2 ton unit has the proper CFM to properly supply the needs of a two story home regardless of heat load calculations. I would think TN has approximately the same average high and low ambient temp as Okla and I would never have considered installing that size unit on a two story.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #6  
Old 12/4/07, 7:49 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Trane Heat Pump

Charley, what if the air handler is the variable speed type? Don't these typically have CFM jumpers to choose the airflow?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #7  
Old 12/4/07, 8:15 PM
Gary T. Heller's Avatar
Gary T. Heller Gary T. Heller is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Peoria, AZ
Posts: 454
Default Re: Trane Heat Pump

A 2.5 ton unit is too small to cool that size house in any climate.
Reply With Quote
  #8  
Old 12/4/07, 9:29 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,873
Default Re: Trane Heat Pump

Quote:
Originally Posted by bking
Charley, what if the air handler is the variable speed type? Don't these typically have CFM jumpers to choose the airflow?
Its like trying to power a Peterbuilt with a Volkswagen engine.

The overall blower size is smaller in a 2.5 ton system. It was stated the unit was 15 years in age so it may or may not have multi-speed motor and even if it does just not enough push for a two story. As a Hi I don't get into efficiency very often but on occasion I have when I absolutely knew I was right based on my experience.

But I will inform my client even if the unit is performing as intended but has to run non-stop because of being under sized or poor duct/return problem. I do not want my client to be surprised and start calling me. I want everything on the table. I consider myself as being on the clients informational TEAM for making purchase decisions



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #9  
Old 12/4/07, 10:44 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,466
Default Re: Trane Heat Pump

Quote:
Originally Posted by cbottger
I do not want my client to be surprised and start calling me. I want everything on the table. I consider myself as being on the clients informational TEAM for making purchase decisions
Good advice...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #10  
Old 12/5/07, 11:50 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Trane Heat Pump

Quote:
I went by to look at the HVAC this afternoon, the reason I wanted confirmation on the size is because I have never seen a 2.5 ton unit serving a two story 2100 square foot home,
You will see it all the time in homes built about 15 years ago (ooh, just noticed the unit is 15 yrs old!). Also newer, but not as much.

In accordance with the Laws of Thermodynamics and general physics, you can not effectively cool two stories with one unit unless it has a balanced zoning system and a return duct to both levels of the house.

If the second floor area is above the garage, this problem becomes 400% worse. You will see a lot of this.
Reply With Quote
  #11  
Old 12/5/07, 7:09 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Trane Heat Pump

I just can't believe whoever has been living there, hasn't already corrected the probable undersize problem.
I'd look further, determine what size Furnace/AHU, and what size Evap.Coil is existing. I'd for sure recommend that the your Client have a Prof. HVAC Contractor inspect and advise.
I am sometimes cynical, but the older, larger unit may have crapped out and the owner/seller may have purchased what ever he could, on the cheap.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Heat pump in a 80+ year old masonry house jskrypka Inspecting HVAC Systems 9 11/25/06 11:47 PM
Installing new heat pump with existing furnace wlmoss Inspecting HVAC Systems 6 5/14/06 12:23 PM
Question on my heat pump dbush Inspecting HVAC Systems 7 3/12/06 1:15 AM
Armstrong heat pump -- good or bad? skipswift Inspecting HVAC Systems 3 2/13/06 10:17 PM
Heat Pump Check list for inspecting dmacy Inspecting HVAC Systems 21 2/1/06 1:56 PM


All times are GMT -4. The time now is 4:43 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts