Default Trane Heat Pump

A Trane split system heat pump, only hvac system installed in a 2100 square foot home. Model # is TWR730A100A1 , manufactured 09/91. I determine this unit to be 2.5 tons, that would be under sized for 2100 square feet. Does anyone have info on this model # to confirm this is a 2.5 ton unit ?
Thanks in advance.
Reply With Quote
  #2  
Old 12/3/07, 7:56 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 2,736
Send a message via MSN to bwiley
Default Re: Trane Heat Pump

That would be a two and a half ton unit. To determine whether it is the proper size or not would require a load calculation.



If the opposite of pro is con, the opposite of progress must be...

www.qualityhomeinspectionsfl.com
Reply With Quote
  #3  
Old 12/3/07, 8:39 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,729
Default Re: Trane Heat Pump

Model # is TWR730A100A1

30/12 = 2.5



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #4  
Old 12/3/07, 9:00 PM
William Sutton's Avatar
William Sutton William Sutton is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Nashville, Tn
Posts: 33
Default Re: Trane Heat Pump

This inspection is tomorrow, I went by to look at the HVAC this afternoon, the reason I wanted confirmation on the size is because I have never seen a 2.5 ton unit serving a two story 2100 square foot home, if the heat operates my job is done. I will recommend when the unit is replaced, it is 15 years old, the HVAC contractor do a load calculation for proper size of new unit.

Last edited by wsutton; 12/3/07 at 9:06 PM..
Reply With Quote
  #5  
Old 12/4/07, 9:52 AM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Trane Heat Pump

Quote:
Originally Posted by wsutton
This inspection is tomorrow, I went by to look at the HVAC this afternoon, the reason I wanted confirmation on the size is because I have never seen a 2.5 ton unit serving a two story 2100 square foot home, if the heat operates my job is done. I will recommend when the unit is replaced, it is 15 years old, the HVAC contractor do a load calculation for proper size of new unit.
Very unlikely that a 2-1/2 ton unit has the proper CFM to properly supply the needs of a two story home regardless of heat load calculations. I would think TN has approximately the same average high and low ambient temp as Okla and I would never have considered installing that size unit on a two story.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #6  
Old 12/4/07, 7:49 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,219
Default Re: Trane Heat Pump

Charley, what if the air handler is the variable speed type? Don't these typically have CFM jumpers to choose the airflow?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #7  
Old 12/4/07, 8:15 PM
Gary T. Heller's Avatar
Gary T. Heller Gary T. Heller is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Peoria, AZ
Posts: 256
Default Re: Trane Heat Pump

A 2.5 ton unit is too small to cool that size house in any climate.
Reply With Quote
  #8  
Old 12/4/07, 9:29 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Trane Heat Pump

Quote:
Originally Posted by bking
Charley, what if the air handler is the variable speed type? Don't these typically have CFM jumpers to choose the airflow?
Its like trying to power a Peterbuilt with a Volkswagen engine.

The overall blower size is smaller in a 2.5 ton system. It was stated the unit was 15 years in age so it may or may not have multi-speed motor and even if it does just not enough push for a two story. As a Hi I don't get into efficiency very often but on occasion I have when I absolutely knew I was right based on my experience.

But I will inform my client even if the unit is performing as intended but has to run non-stop because of being under sized or poor duct/return problem. I do not want my client to be surprised and start calling me. I want everything on the table. I consider myself as being on the clients informational TEAM for making purchase decisions



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #9  
Old 12/4/07, 10:44 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,729
Default Re: Trane Heat Pump

Quote:
Originally Posted by cbottger
I do not want my client to be surprised and start calling me. I want everything on the table. I consider myself as being on the clients informational TEAM for making purchase decisions
Good advice...



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #10  
Old 12/5/07, 11:50 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,694
Default Re: Trane Heat Pump

Quote:
I went by to look at the HVAC this afternoon, the reason I wanted confirmation on the size is because I have never seen a 2.5 ton unit serving a two story 2100 square foot home,
You will see it all the time in homes built about 15 years ago (ooh, just noticed the unit is 15 yrs old!). Also newer, but not as much.

In accordance with the Laws of Thermodynamics and general physics, you can not effectively cool two stories with one unit unless it has a balanced zoning system and a return duct to both levels of the house.

If the second floor area is above the garage, this problem becomes 400% worse. You will see a lot of this.
Reply With Quote
  #11  
Old 12/5/07, 7:09 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 499
Default Re: Trane Heat Pump

I just can't believe whoever has been living there, hasn't already corrected the probable undersize problem.
I'd look further, determine what size Furnace/AHU, and what size Evap.Coil is existing. I'd for sure recommend that the your Client have a Prof. HVAC Contractor inspect and advise.
I am sometimes cynical, but the older, larger unit may have crapped out and the owner/seller may have purchased what ever he could, on the cheap.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Heat pump in a 80+ year old masonry house jskrypka HVAC 9 11/25/06 11:47 PM
Installing new heat pump with existing furnace wlmoss HVAC 6 5/14/06 12:23 PM
Question on my heat pump dbush HVAC 7 3/12/06 1:15 AM
Armstrong heat pump -- good or bad? skipswift HVAC 3 2/13/06 10:17 PM
Heat Pump Check list for inspecting dmacy HVAC 21 2/1/06 1:56 PM


All times are GMT -4. The time now is 7:57 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts