I am looking for some enlightment regarding what I found, or at least think I found, on an inspection yesterday. I am relatively new in the business (two + years) and I haven't run in to this before. House had split AC system with evaporator coil, horizontal-flow furnace & air handler unit in the attic. What has me perplexed is that there are two air conditioner condensing units (ACCU's) outside for this single system. One ACCU is 1½ ton and the other is a 2½ ton. Is it possible to have two working ACCU's for a single evap coil? How does this work? I have never seen anything in literature about this arrangement. If anyone out there knows what this is all about, I would appreciate a shout.

Thanks much,
Gary Loughman
Assured Home Inspections, Pllc
Reply With Quote
  #2  
Old 4/29/07, 12:50 PM
jking2 jking2 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Troy, MI
Posts: 183
Default Re: Two for One???

Did you see 2 sets of refrigerant lines in the attic? I doubt that a single evap coil would have 2 condensing units in a residential setup. There might be 2 coils in parallel, providing 2 stages of cooling, though. If you didn't see both sets of refrigerant piping, then there may be a coil at another location for a separate zone.

Jim King
Reply With Quote
  #3  
Old 4/29/07, 3:39 PM
gloughman gloughman is offline
New User
 
Join Date: Apr 2006
Location: Houston, TX
Posts: 18
Please Note: gloughman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two for One???

Looking at my digital picture, I am only seeing one set of refrigerant lines at the coil location. This is a small one story place and there is only one zone. Outside , each ACCU has there own refrigerant lines that enter the house going to the attic. I am sorry that I haven't figured out how to send the picture along with my message.

Gary
Reply With Quote
  #4  
Old 4/29/07, 5:58 PM
jking2 jking2 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Troy, MI
Posts: 183
Default Re: Two for One???

Gary,
If two sets of lines are entering the house, and you only saw one set in the attic, then the other set must be going somewhere else. Perhaps to a wall mounted unit in the master bedroom?

Jim
Reply With Quote
  #5  
Old 4/29/07, 6:20 PM
gloughman gloughman is offline
New User
 
Join Date: Apr 2006
Location: Houston, TX
Posts: 18
Please Note: gloughman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two for One???

Jim,

No wall units anywhere. I may try to go back and look this over a little better than I did the first time. Because I hadn't seen anything like this before I should have been more of a detective to find out more about what I was looking at.

Thanks for your help.

Gary
Reply With Quote
  #6  
Old 4/29/07, 6:49 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Two for One???

If you've got two Condensers, you got to have two air handlers. The attic unit usually conditions the upper floor. There's got to be another air handler in the lower crawlspace/basement area somewhere.

Are these two Condensers the same age?
Reply With Quote
  #7  
Old 4/29/07, 8:09 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Two for One???

Quote:
Originally Posted by dvalley
If you've got two Condensers, you got to have two air handlers. The attic unit usually conditions the upper floor. There's got to be another air handler in the lower crawlspace/basement area somewhere.

Are these two Condensers the same age?
Not necessarily. Many years age FEDDERS developed a dual coil that fit into a single furnace/air handler, but was operated by two condensing units. It was controlled by a thermostat with two mercury bulbs that would make connection 2 degrees apart. If the first system could not cool the house, the temperature would rise 2 more degrees and activate the second condenser.

Frequently the two line sets were joined in a common conduit and appeared to be a singe installation inside the house.

There was also an occasional attempt to use two small condensers in place of a larger unit (sometimes the cost difference was enough to do this) by joining the two lines into one larger line set. There were about 200 reasons why this didn't work, but you never know until you try.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #8  
Old 4/29/07, 10:03 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: Two for One???

Was that the side by side evap unit?
Reply With Quote
  #9  
Old 4/29/07, 10:56 PM
gloughman gloughman is offline
New User
 
Join Date: Apr 2006
Location: Houston, TX
Posts: 18
Please Note: gloughman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two for One???

To David Valley,
Thanks, but there is only one floor, 1,144 sq.ft., on pier & beam.
ACCU's are same age.

To Jae Williams,
Thanks, I thought I was going nuts or something.

Gary Loughman
Reply With Quote
  #10  
Old 4/30/07, 6:13 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Two for One???

Quote:
Originally Posted by jwilliams4
Not necessarily. Many years age FEDDERS developed a dual coil that fit into a single furnace/air handler, but was operated by two condensing units. It was controlled by a thermostat with two mercury bulbs that would make connection 2 degrees apart. If the first system could not cool the house, the temperature would rise 2 more degrees and activate the second condenser.

Frequently the two line sets were joined in a common conduit and appeared to be a singe installation inside the house.

There was also an occasional attempt to use two small condensers in place of a larger unit (sometimes the cost difference was enough to do this) by joining the two lines into one larger line set. There were about 200 reasons why this didn't work, but you never know until you try.

Hmmm...Never seen such an animal in my area.
Reply With Quote
  #11  
Old 4/30/07, 6:16 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Two for One???

Quote:
Originally Posted by gloughman
To Jae Williams,
Thanks, I thought I was going nuts or something.

Gary Loughman
You're not off the hook yet. You definitely have an additional air handler somewhere.

You stated....
Quote:
I am only seeing one set of refrigerant lines at the coil location.
So the other set of pressure lines are going somewhere!!!
Reply With Quote
  #12  
Old 4/30/07, 6:45 AM
jking2 jking2 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Troy, MI
Posts: 183
Default Re: Two for One???

Four tons of cooling is way too much for 1,144 SF, even in hot, humid Houston. I suspect one of those condensers was abandoned when replaced by the other.

Jim King
Reply With Quote
  #13  
Old 4/30/07, 11:12 AM
Matt Berman, CMI Matt Berman, CMI is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Mt. Clemens, MI
Posts: 107
Default Re: Two for One???

James is correct, thats way too much cooling for that size home even in Texas. Did you run the ac units to see if they both ran at all.Without seeing the set up,I would go with possible abandoned unit also.Matt
Reply With Quote
  #14  
Old 4/30/07, 12:40 PM
dchew dchew is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: San Ramon, CA
Posts: 317
Default Re: Two for One???

My 1st question is did you try to operate the AC system with automatic controls? If you did, did both condensers operate?

If there is no 2nd air handler in the house, then consider the possibility that the AC had been swapped out at one time or another and whoever did the changeout didn't remove the old condenser. Just a thought.
Reply With Quote
  #15  
Old 4/30/07, 1:19 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Two for One???

Quote:
Originally Posted by dvalley
Hmmm...Never seen such an animal in my area.
My "go to guy" in HVAC, considered one of the very best in the business, lived in the Cinci area, and was the FEDDERS trouble-shooter nationally. I think the pilot program for those units was centered around him. I know he didn't think much of the concept, but made a concerted effort to make them work.

I don't know if the system got too far away from the mid-west.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin

Last edited by jwilliams4; 4/30/07 at 1:22 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 7:17 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts