Does anyone know of any application where a Type BW vent is allowed for anything other than venting of a wall furnace?
Code reference or appliance manufacturer please. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#2
|
||||
|
||||
|
Okay, how about this?
Transition from Type BW to Type B is allowed with listed components, but is the opposite allowed (B-vent to BW-vent)? Anyone? IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net Last edited by jpope; 2/28/07 at 4:15 PM.. |
|
#3
|
||||
|
||||
|
Last edited by bkelly2; 2/27/06 at 6:56 PM.. |
|
#4
|
||||
|
||||
|
Not really, but I appreciate the effort.
Definition from IRC and UBC = Type BW vent. A vent listed and labeled for use with wall furnaces. I found these fireplaces vented with Type BW. This is new to me. Also, I can't find any information that supports the B to BW transition as in the picture. The dilemma? 400 + units completed, about a hundred to go (construction in progress) </IMG> IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
||||
|
||||
|
|
|
#6
|
||||
|
||||
|
Oval B is BW
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#7
|
||||
|
||||
|
http://www.mtlfab.com/newcom/media/l041.pdf
Hmmm, Than this should do it. Check out near the bottom "oval vent" #1 Last edited by bkelly2; 2/27/06 at 7:23 PM.. |
|
#8
|
||||
|
||||
|
That helps. Thanks Brian.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#9
|
||||
|
||||
|
Quote:
|
|
#10
|
||||
|
||||
|
Jeff what did you decide about this installation?
|
|
#11
|
||||
|
||||
|
I have sent a letter to the BW vent manufacturer and am waiting for a reply. . .
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#12
|
||||
|
||||
|
Please Note:
hspinnler is a non-member guest and is in no way affiliated with InterNACHI or its members.
How about clearance to combustibles?
|
|
#13
|
||||
|
||||
|
Quote:
|
|
#14
|
||||
|
||||
|
Conflicting information.
The BW vent manufacturer says "no problem." Anywhere a B-vent is used, a BW-vent can be used as well (generally speaking). The manufacturer of the fireplace says the vent system must be specifically listed for the fireplace, B or BW. The code books say that BW vents are listed for specific wall furnaces (not water heaters, not fireplaces - just wall furnaces). The code "enforcers" follow the BW manufacturers recommendations (allowed for all gas appliance vent systems). I will follow that lead. . . Anyone who wants the manufacturers info in a pdf file, send me an email. It's too large to attach to the message board. . . IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#15
|
||||
|
||||
|
Quote:
Clearances for type BW are the same as a standard B-vent - 1 inch minimum. In this case, there were several clearance issues that were addressed and corrected. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Air admittance valves everywhere | apfaff | Plumbing Inspections | 13 | 4/16/07 10:17 AM |
| Has anyone seen this type of vent material? | scosta | Inspecting HVAC Systems | 12 | 3/9/07 3:30 PM |
| Gas and oil hot water tank and Boiler Share Vents | hvanderbeek | Miscellaneous Discussion for Inspectors | 8 | 1/25/07 6:22 PM |
| Massachusetts Board of Registration of Home Inspectors | jtedesco1 | Legislation, Licensing & Legal Issues for Inspectors | 0 | 2/14/06 4:38 AM |