Default Type BW Vent

Does anyone know of any application where a Type BW vent is allowed for anything other than venting of a wall furnace?

Code reference or appliance manufacturer please.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #2  
Old 2/27/06, 5:51 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Type BW Vent

Okay, how about this?

Transition from Type BW to Type B is allowed with listed components, but is the opposite allowed (B-vent to BW-vent)?

Anyone?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 2/28/07 at 4:15 PM..
Reply With Quote
  #3  
Old 2/27/06, 6:33 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Type BW Vent

http://web1.sanbruno.ca.gov/city_ser...nical_Code.pdf

Does this help Jeff? Pg 36

Good question

Last edited by bkelly2; 2/27/06 at 6:56 PM..
Reply With Quote
  #4  
Old 2/27/06, 7:04 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Type BW Vent

Not really, but I appreciate the effort.

Definition from IRC and UBC = Type BW vent. A vent listed and labeled for use with wall
furnaces.


I found these fireplaces vented with Type BW. This is new to me. Also, I can't find any information that supports the B to BW transition as in the picture.

The dilemma? 400 + units completed, about a hundred to go (construction in progress) I don't want to "unnecessarily" open up a hornets nest, but I want my client(s) to be aware if the installation is improper.





</IMG>



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 2/27/06, 7:16 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Type BW Vent

http://www.mtlfab.com/media/l041r.pdf

Still looking, sure it is not oval B vent?
Reply With Quote
  #6  
Old 2/27/06, 7:17 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Type BW Vent

Oval B is BW



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 2/27/06, 7:18 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Type BW Vent

http://www.mtlfab.com/newcom/media/l041.pdf

Hmmm, Than this should do it.

Check out near the bottom "oval vent" #1

Last edited by bkelly2; 2/27/06 at 7:23 PM..
Reply With Quote
  #8  
Old 2/27/06, 8:13 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Type BW Vent

That helps. Thanks Brian.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 2/27/06, 9:03 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Type BW Vent

Quote:
Originally Posted by jpope
That helps. Thanks Brian.
My pleasure Jeff, learned something new.
Reply With Quote
  #10  
Old 3/22/06, 5:34 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Type BW Vent

Jeff what did you decide about this installation?
Reply With Quote
  #11  
Old 3/23/06, 12:53 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Type BW Vent

I have sent a letter to the BW vent manufacturer and am waiting for a reply. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 3/24/06, 8:01 PM
hspinnler's Avatar
hspinnler hspinnler is offline
Active Poster
 
Join Date: Apr 2005
Location: Hoschton, GA
Posts: 149
Please Note: hspinnler is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Type BW Vent

How about clearance to combustibles?
Reply With Quote
  #13  
Old 5/8/06, 9:20 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Type BW Vent

Quote:
Originally Posted by bkelly2
Jeff what did you decide about this installation?
Anything yet?
Reply With Quote
  #14  
Old 5/8/06, 11:39 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Type BW Vent

Conflicting information.

The BW vent manufacturer says "no problem."

Anywhere a B-vent is used, a BW-vent can be used as well (generally speaking). The manufacturer of the fireplace says the vent system must be specifically listed for the fireplace, B or BW.

The code books say that BW vents are listed for specific wall furnaces (not water heaters, not fireplaces - just wall furnaces).

The code "enforcers" follow the BW manufacturers recommendations (allowed for all gas appliance vent systems). I will follow that lead. . .

Anyone who wants the manufacturers info in a pdf file, send me an email. It's too large to attach to the message board. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #15  
Old 5/9/06, 12:38 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Type BW Vent

Quote:
Originally Posted by hspinnler
How about clearance to combustibles?
Sorry, I missed that post Hank.

Clearances for type BW are the same as a standard B-vent - 1 inch minimum. In this case, there were several clearance issues that were addressed and corrected.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Air admittance valves everywhere apfaff Plumbing Inspections 13 4/16/07 10:17 AM
Has anyone seen this type of vent material? scosta Inspecting HVAC Systems 12 3/9/07 3:30 PM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 6:22 PM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues for Inspectors 0 2/14/06 4:38 AM


All times are GMT -4. The time now is 3:49 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts