Default Is this type of gas line ok, for gas log fireplace..






An Ounce of prevention is better
than a pound of cure :}
Reply With Quote
Need a home inspection in Delaware? Check out InterNACHI's listing of Delaware certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/19/12, 7:12 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Is this type of gas line ok, for gas log fireplace..

Where is the isolation valve?



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #3  
Old 1/19/12, 7:20 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Is this type of gas line ok, for gas log fireplace..

Line is fine
Reply With Quote
  #4  
Old 1/20/12, 10:55 PM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: Is this type of gas line ok, for gas log fireplace..

Quote:
Originally Posted by belliott View Post
Line is fine

Thanks...



An Ounce of prevention is better
than a pound of cure :}
Reply With Quote
  #5  
Old 1/20/12, 11:31 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Is this type of gas line ok, for gas log fireplace..

Quote:
Originally Posted by belliott View Post
Line is fine
In Chicago. What about California?
Reply With Quote
  #6  
Old 1/21/12, 12:00 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Is this type of gas line ok, for gas log fireplace..

Quote:
Originally Posted by jjonas View Post
In Chicago. What about California?
Do the laws of physics apply there?

Or do we have a code Inspector hat on.
Reply With Quote
  #7  
Old 1/21/12, 7:47 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Is this type of gas line ok, for gas log fireplace..

Quote:
Originally Posted by belliott View Post
Do the laws of physics apply there?

Or do we have a code Inspector hat on.
California is more restrictive than Chicago in many of their regulations, such as Chicago is to others.

You claim the CSST is (blanket statement) OKAY.

It may not be allowed in California.

The California inspector needs to verify with a qualified CA source, just as you would if someone in CA gave you an opinion for use in Chicago.

Get it?
Reply With Quote
  #8  
Old 1/21/12, 8:21 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Is this type of gas line ok, for gas log fireplace..

Quote:
Originally Posted by jjonas View Post
California is more restrictive than Chicago in many of their regulations, such as Chicago is to others.

You claim the CSST is (blanket statement) OKAY.

It may not be allowed in California.

The California inspector needs to verify with a qualified CA source, just as you would if someone in CA gave you an opinion for use in Chicago.

Get it?
Sorry dude but I recommend by safety rather than political code.
Do you understand what I am saying ?

Now tell me how what you see in the picture is an issue and why in your own words.
Reply With Quote
  #9  
Old 1/21/12, 8:34 AM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,187
Default Re: Is this type of gas line ok, for gas log fireplace..

Looks like it might be an issue ........................in California. Wait for Jeff Pope to chime in.
Reply With Quote
  #10  
Old 1/21/12, 8:50 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Is this type of gas line ok, for gas log fireplace..

Quote:
Originally Posted by belliott View Post
Sorry dude but I recommend by safety rather than political code.
Do you understand what I am saying ?

Now tell me how what you see in the picture is an issue and why in your own words.
So you are saying that CSST if SAFER than rigid black pipe???

Appearantly you don't understand what I'm saying.

Never said it was an issue, just that it could be in a state 2,000 miles away!
Reply With Quote
  #11  
Old 1/21/12, 8:51 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Is this type of gas line ok, for gas log fireplace..

Quote:
Originally Posted by ldapkus1 View Post
Looks like it might be an issue ........................in California. Wait for Jeff Pope to chime in.
Exactly.

Hopefully his report isn't already sent off with potentially bad information listed!
Reply With Quote
  #12  
Old 1/21/12, 9:06 AM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,187
Default Re: Is this type of gas line ok, for gas log fireplace..

Quote:
Originally Posted by jjonas View Post
Exactly.

Hopefully his report isn't already sent off with potentially bad information listed!
It will be OK if they're confused with 200 unrelated photos in the report.
Reply With Quote
  #13  
Old 1/21/12, 9:11 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Is this type of gas line ok, for gas log fireplace..

Quote:
Originally Posted by ldapkus1 View Post
It will be OK if they're confused with 200 unrelated photos in the report.
In all fairness, if you're referring to the OP, at least he has the balls to ask questions.

If you're referring to Bob, I defer all comments to yourself!
Reply With Quote
Need a home inspection in Delaware? Check out InterNACHI's listing of Delaware certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/21/12, 11:50 AM
clambert2 clambert2 is offline
Active Poster
 
Join Date: Jan 2011
Location: Southern California
Posts: 343
Please Note: clambert2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this type of gas line ok, for gas log fireplace..

Quote:
Originally Posted by dnasser View Post


Yes, per the UMC. Decorative logs can have flexible gas line connector. Gas log lighters must have solid pipe.
Hope this helps

Last edited by clambert2; 1/21/12 at 1:37 PM..
Reply With Quote
  #15  
Old 1/21/12, 12:40 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Is this type of gas line ok, for gas log fireplace..

Quote:
Originally Posted by jjonas View Post
California is more restrictive than Chicago in many of their regulations, such as Chicago is to others.

You claim the CSST is (blanket statement) OKAY.

It may not be allowed in California.

The California inspector needs to verify with a qualified CA source, just as you would if someone in CA gave you an opinion for use in Chicago.

Get it?
This appliance connector is perfectly acceptable.

FWIW - CSST is gas piping. Appliance connectors (although made of the same material) do not qualify as CSST. They are pre-assembled, listed "connectors." Rules for installation of CSST are different than rules for use of appliance connectors.

CSST is also allowed in CA.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gas Line to fireplace jharrison Plumbing Inspections 8 12/28/10 10:00 PM
Fireplace clean and scan dmacy Interior Inspections 4 11/21/10 8:16 PM
Coming soon. Free, online, fireplace and chimney inspection course. gromicko General Inspection Discussion 15 12/14/09 4:19 PM
Hearth size??? jcampbell Inspecting HVAC Systems 32 6/1/08 1:56 PM
TPRV line and condensate line marriage ccarrington Plumbing Inspections 3 4/29/06 7:59 AM


All times are GMT -4. The time now is 12:26 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts