Question Uhm, new furnace will be cooking my A-coil ???

Hello all, first post here and need a little help. I had an old Interdyne(?) 55/45 furnace that has the recalled gas valve burn up on me. I was lucky to have it not burn down my home, so, now that I still have my home, I need to fix it. I looked for a gas valve and they are around $200, give or take. When I opened my big oval portal door to the furnace, I could see the heat chamber/exchanger cracking in the corners leading to the inner portion of the back wall. There was one on each side about 4” long. I knew this back a year ago, but, being a double walled unit, I figured it was good for a little while. I decided to trash that unit completely and got me a Bryant 312AAV03070 (I believe it is). I am using this as a downflow and the unit sits on top of my old evaporator almost perfect, but, I am concerned as to how far the bottom of the furnace needs to be from the AC coil. It looks as if it is the same distance as the old unit (about 5-8” give or take) but the old unit was put in 1972 and this is a new 70k unit, MUCH hotter I am sure.

I have looked everywhere but can not find a “heat exchanger to AC coil distance” notes. I have looked EVERYWHERE and its getting real cold outside. Will this be enough distance or do I need some kind of transition duct work to raise the furnace?

Thanks.

Last edited by Hvac Man123; 10/20/08 at 6:16 PM..
Reply With Quote
  #2  
Old 10/21/08, 12:41 AM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Uhm, new furnace will be cooking my A-coil ???

Quote:
Originally Posted by Hvac Man123 View Post
Hello all, first post here and need a little help. I had an old Interdyne(?) 55/45 furnace that has the recalled gas valve burn up on me. I was lucky to have it not burn down my home, so, now that I still have my home, I need to fix it. I looked for a gas valve and they are around $200, give or take. When I opened my big oval portal door to the furnace, I could see the heat chamber/exchanger cracking in the corners leading to the inner portion of the back wall. There was one on each side about 4” long. I knew this back a year ago, but, being a double walled unit, I figured it was good for a little while. I decided to trash that unit completely and got me a Bryant 312AAV03070 (I believe it is). I am using this as a downflow and the unit sits on top of my old evaporator almost perfect, but, I am concerned as to how far the bottom of the furnace needs to be from the AC coil. It looks as if it is the same distance as the old unit (about 5-8” give or take) but the old unit was put in 1972 and this is a new 70k unit, MUCH hotter I am sure.

I have looked everywhere but can not find a “heat exchanger to AC coil distance” notes. I have looked EVERYWHERE and its getting real cold outside. Will this be enough distance or do I need some kind of transition duct work to raise the furnace?

Thanks.
I much prefer to chat with folks with real names so I am going to give a real short answer NO



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #3  
Old 10/21/08, 9:21 AM
Hvac Man123 Hvac Man123 is offline
New User
 
Join Date: Oct 2008
Posts: 5
Please Note: Hvac Man123 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Uhm, new furnace will be cooking my A-coil ???

Does that make me less of a real person?

Chris
Reply With Quote
  #4  
Old 10/22/08, 12:22 AM
Vince Santos's Avatar
Vince Santos Vince Santos is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Canton, MI - Serving Souteast Michigan
Posts: 1,040
Default Re: Uhm, new furnace will be cooking my A-coil ???

I believe you may receive a low airflow due to the heat exchanger being too close to the evaporator coil. You should perhaps call the furnace manufacture for specifications.






Vince Santos
Owner / Certified Home Inspector
StepByStep Home Services LC
(734) 748-9584
http://www.stepbystepinspections.com
Providing Home Inspection Services to Southeast Michigan

Active Rain blog
http://activerain.com/sbsinspections

ITA Trained and Certified
Reg104669Cc

Reply With Quote
  #5  
Old 10/22/08, 7:10 AM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,607
Default Re: Uhm, new furnace will be cooking my A-coil ???

What Charley is saying is that it is an accepted practice that real names are used on this site, something about protecting the inocent or some such stuff, unless of course you have been sucking CO fumes, http://cgi.ebay.com/KIDDE-9CO5-02-Ca...3286.m20.l1116 for the past year, then there might be room for an exception

General speaking matching factory compontents have their clearances builtin.



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #6  
Old 10/22/08, 9:30 AM
Hvac Man123 Hvac Man123 is offline
New User
 
Join Date: Oct 2008
Posts: 5
Please Note: Hvac Man123 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Uhm, new furnace will be cooking my A-coil ???

I am just a simple guy, didnt think not using my real name was a big deal. Not so big someone would take such offense to it, seems a little petty to me. He could have just given a nice answer and then said "You should use your real name just for the people in the forum" or something, not act like someone beat his dog.

Actually, this is a new unit going on top of a 1972 unit. I know some are going to say replace the whole unit, but, I am strapped, REALLY strapped for cash, just cant do it and the unit I have still works fine.

Anyways, thanks for the answers so far, which that link makes me ask another question.

When carbonmonoxide detectors first came out, am I correct that they used to have a cartridge that needed changing once every month/3months/6months or something like that? Do they still have that or is there a new detector in which that is no longer needed?

Chris Marini
Reply With Quote
  #7  
Old 10/22/08, 10:18 AM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,607
Default Re: Uhm, new furnace will be cooking my A-coil ???

most here will list a 1972 unit as "at the end of it's useful life" and I do understand about cash flow.



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #8  
Old 10/22/08, 10:59 AM
Hvac Man123 Hvac Man123 is offline
New User
 
Join Date: Oct 2008
Posts: 5
Please Note: Hvac Man123 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Uhm, new furnace will be cooking my A-coil ???

Living by myself, paying the rent, groceries, insurance...etc. Only have an extra $200 a month most, and that is if I am lucky if nothing else comes up, which it useually does. I cant afford a complete system, AKA matching factory units, so, I need to make sure this new furnace is sitting high enough above my old coil that it will not cook my AC coil.
Reply With Quote
  #9  
Old 10/24/08, 7:35 AM
Charles Jones Charles Jones is offline
New User
 
Join Date: Jul 2007
Location: new jersey
Posts: 22
Please Note: Charles Jones is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Uhm, new furnace will be cooking my A-coil ???

To not replace the evap coil along with the furnace on a down flow system is plain old dum. So in a year or two it will be time to upgrade the condenser and evap coil and Im gonna have to remove the furnace just to replace the coil $$$$ pay day for me. an up flow coil not a problem but down flow a waist of money not to do it with the furnace change out.
The evap coils drain pan is built to hold up to high temps. upflow set up the coils drain pan is even closer to the heat exchanger then on the down flow set up.
Reply With Quote
  #10  
Old 10/24/08, 9:51 AM
Hvac Man123 Hvac Man123 is offline
New User
 
Join Date: Oct 2008
Posts: 5
Please Note: Hvac Man123 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Uhm, new furnace will be cooking my A-coil ???

Well, you WOULD have gotten me for more $$$ for that, but, I dont mind removing the furnace myself. Heck, if I had accsess to the freon, I would do it all myself, but....

Yes, if I had all the money in the world, logically, it would be one of the dumbest things to do.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 2:26 AM
Furnace Problem Comments Welcome rfrost HVAC 24 10/21/07 7:26 PM
Armstrong Ultra 80 Oil Forced air furnace Stephen Frazer HVAC 19 4/9/07 9:00 PM
Condemned Furnaces Spark Safety Issues Gary Reecher HVAC 7 3/8/07 9:17 PM
Explaining MultiWire Circuits- For Fun :) pabernathy Electrical 38 11/8/06 7:04 PM


All times are GMT -4. The time now is 12:34 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts