Default vent connector slope

What do you think about this vent connector slope for a natural gas fireplace/stove.
Attached Images
File Type: jpg DSC05001 (Medium).JPG (50.5 KB, 28 views)




Mark Nicholet
Apple Home Inspections
Reply With Quote
Find an InterNACHI certified Georgia Home Inspector (and anywhere else in North America)
  #2  
Old 9/19/08, 11:33 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 4,037
Larry D. Kage .
Default Re: vent connector slope

Quote:
Originally Posted by mnicholet View Post
What do you think about this vent connector slope for a natural gas fireplace/stove.
Could be fine...I'd have to see the manufacturer's install instructions to be sure.



"An Education, not just an Inspection"


Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525



Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #3  
Old 9/20/08, 1:28 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,124
Brian A. MacNeish is well trusted Brian A. MacNeish is well trusted Brian A. MacNeish is well trusted
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: vent connector slope

Quote:
Originally Posted by mnicholet View Post
What do you think about this vent connector slope for a natural gas fireplace/stove.
I'd be more concerned if that chimney was located on an outside wall where it will be cold upon unit start up. It will then have to push a column of cool/cold heavy air up out of the flue before it can warm the flue and get the recommended draft for efficient, safe operation. Those of us that have been in WETT for a number of years would like to see exterior chimneys (even the insulated steel metal types) banned. A chimney should always be installed through a warm area of the house so that's its warm with a column of light bouyant air creating draft without help or chance that it will draw.

In 1989, I worked on the local portion of a cross-country study on IAQ. It found that 39% of oil and gas installations had draft problems and were borderline for gas spillage upon startup!! Some corrected within seconds but some took almost a minute......too long to be spilling combustion gases into a living space! It would take very little to tip the scales to longer or constant spillage.

WETT #572
Master System Advisor

Last edited by Brian A. MacNeish; 9/20/08 at 3:56 PM.
Reply With Quote
  #4  
Old 9/20/08, 4:31 PM
Mark Nicholet's Avatar
Mark Nicholet Mark Nicholet is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Campbell River, BC
Posts: 216
Mark Nicholet is often very helpful Mark Nicholet is often very helpful Mark Nicholet is often very helpful
Default Re: vent connector slope

Thanks, great information. Very good reminder regarding the chimney location. This chimney was actually an external chimney installed several years after the home was built with a 2 inch gap between the masonry and the cladding and lateral supports every 10 feet. I sometimes find spillage on gas appliances with my carbon monoxide detector until it reaches its steady state.




Mark Nicholet
Apple Home Inspections
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Pellet stove help chellickson General Inspection Discussion 22 8/10/08 5:41 PM
Plumbing vent next to exhaust vent mpettitt Plumbing 4 10/12/07 6:38 PM
Air admittance valves everywhere apfaff Plumbing 13 4/16/07 10:17 AM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Misc. Discussion 8 1/25/07 6:22 PM


All times are GMT -4. The time now is 6:26 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics