First time I have seen power vents for the HVAC and DHW made of PVC vented through the roof as opposed to out a side wall. I am assuming they must follow the same rules as draft vents for 3'/2'/10'. Am I wrong?
|
| Need a home inspection in Wyoming? Check out InterNACHI's listing of Wyoming certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
I don't know the answer per code or installation instructions, but by inference I wouldn't think they would need to follow the same rules...
1) the vent gas is cool so there is no concern about fire or damage to the roof. 2) there is no need for "proper drafting" of the vents since they are power driven. Like I said though, I could easily be wrong. That's just my thought on it without knowing the installation instructions. Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#3
|
||||
|
||||
|
Greg,
I have not seen them through the roof as in your pic either. Normally they are located in the chimney, or out a side wall. Seems to me you will have issues whenever you have snow accumulation Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#4
|
||||
|
||||
|
Yes, the same rules follow as if they go through the roof. I have installed several of them like that without any problems. Some local codes may require it to be above the peak of the roof though.
|
|
#5
|
|||
|
|||
|
The three flashing boots on top of the shingles is a poor (leak prone) installation, also.
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#6
|
||||
|
||||
|
I guess my main concern was with snow - these vents don't stick up more than 12 inches and we get larger accumulations than that every winter - and you are right, the boots aren't caulked at all - thanks guys -
|
|
#7
|
||||
|
||||
|
Greg, I see those roof-installed here in CO fairly often, but I've never seen them terminated that close to the roof. I don't believe that they need to comply with the 2-10 rule, which is mainly for adequate draft, but I'm pretty sure that the AHJ defers to the manufacturer's recommendations. I have never seen them comply with the 2-10 rule when installed on a roof. I generally see them terminate around 18-24" above the roof.
I'd be concerned about snow cover too and I'd call it out as needing confirmation of proper installation by a qualified contractor. The exhaust might blow itself free, but the intake might be a problem. As Mark said, they're power-driven, but you don't want the furnace sucking in moisture from snow. Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
Last edited by kshepard; 9/12/10 at 1:50 AM.. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Pellet stove help | chellickson | General Inspection Discussion | 23 | 8/19/10 1:23 AM |
| Oil Vent Height | bsmith | Inspecting HVAC Systems | 2 | 4/30/09 11:14 AM |
| Air admittance valves everywhere | apfaff | Plumbing Inspections | 13 | 4/16/07 9:17 AM |
| Gas and oil hot water tank and Boiler Share Vents | hvanderbeek | Miscellaneous Discussion for Inspectors | 8 | 1/25/07 5:22 PM |