Default Vent sizing?

The boiler is 5" the water heater is 3" and the gas stove is 4". The gas stove is only used if the electric power goes out, so it doesn't run if the boiler is on. My understanding is that if the boiler was 5" and you add a water heater you must increase the size of the vent 1". Here it's 5" through to termination. Is this allowed? Owner stated that a local HVAC company did the install....
Attached Thumbnails
vent-sizing-4791-hwy-3-south-098-small-.jpg.jpg
Views:	57
Size:	30.6 KB
ID:	37629   vent-sizing-4791-hwy-3-south-099-small-.jpg.jpg
Views:	52
Size:	22.3 KB
ID:	37630  
Reply With Quote
Need a home inspection in Hawaii? Check out InterNACHI's listing of Hawaii certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/22/10, 9:33 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: Vent sizing?

Bump
Reply With Quote
  #3  
Old 6/22/10, 9:42 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Vent sizing?

How many BTU's was the boiler and how many was the water heater?




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #4  
Old 6/22/10, 10:07 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: Vent sizing?

Hi Stephen,
The boiler was 105,000 input 88,000 BTU per hr, the water heater was 36,000 btu.
Reply With Quote
  #5  
Old 6/23/10, 11:34 AM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Vent sizing?

Gerald,

Typically you are correct. The connector should increase in size where more than one appliance is manifolded into the flue. The flue must equal the largest connector plus 50% of the others. The smallest appliance connector must enter at the highest level consistent with available headroom or clearance to combustibles.

Of course your area AHJ may vary. Ultimately you should contact the local AHJ and ask them about this installation, especially if no permits or inspection tags are visible.




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #6  
Old 6/23/10, 6:19 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: Vent sizing?

Thanks for the info William. I did see that the AGA had charts that did show that a common ( 2 or more appliances ) 5" diameter gravity vent with draft diverter's within 2ft verticle height, with the horizontal run no higher than 5ft with a total vertical height of 15ft could handle 140,000 btu. But that was alot of work.........the AHJ would be the best choice.
Thanks
Reply With Quote
  #7  
Old 6/23/10, 6:48 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Vent sizing?

Was there any evidence that the existing setup was not functioning or signs of implications resulting from incorrect sizing and connections? i.e. visible staining or corrosion from condensation, back drafting, scorching at the combustion chamber, etc...




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #8  
Old 6/23/10, 9:03 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: Vent sizing?

Both the boiler and water heater drafted well. With no backdrafting. Normal scale / rust from lack of recent service. No visible issues with condensation, roll out or sooting. It seemed functional, I just question the vent sizing as you said it should be 6 or 7" based upon " The flue must equal the largest connector plus 50% of the others."
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pellet stove help chellickson General Inspection Discussion 23 8/19/10 1:23 AM
Plumbing vent next to exhaust vent mpettitt Plumbing Inspections 5 10/12/07 5:38 PM
Air admittance valves everywhere apfaff Plumbing Inspections 13 4/16/07 9:17 AM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 5:22 PM


All times are GMT -4. The time now is 12:28 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts