Default venting

venting-dscf0012-small-.jpg.JPG
Views:	94
Size:	59.1 KB
ID:	8638
Reply With Quote
  #2  
Old 1/23/07, 4:39 PM
brepanshek brepanshek is offline
Active Poster
 
Join Date: May 2006
Location: York, PA
Posts: 235
Please Note: brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: venting

Sorry what you are looking at is a hot water heater vent that is 3" and runs 15' to the chimney flue. Doesn't this seem to long? No back drafting was evident at time of operation.
Reply With Quote
  #3  
Old 1/23/07, 4:44 PM
brepanshek brepanshek is offline
Active Poster
 
Join Date: May 2006
Location: York, PA
Posts: 235
Please Note: brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: venting

also saw this. this is a 5" single wall smoke pipe to chimney flue, do you see the the screen on the tee portion of the pipe? This is a naturaql gas furnace and this seems to be acting like a damper to prevent negitive draft for combustion gases. I don't know what this is and if is proper?????
venting-dscf0014-small-.jpg.JPG
Views:	88
Size:	56.7 KB
ID:	8639
Reply With Quote
  #4  
Old 1/23/07, 4:51 PM
John W. Springstead's Avatar
John W. Springstead John W. Springstead is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Central Lake, MI
Posts: 143
Default Re: venting

All looks questionable to me and would require further evaluation and necessary repairs/upgrades by quailified HVAC tech.



John Springstead
Home Inspections of USA
1752 N.E. Torch Lake Dr.
Central Lake, MI 49622
1-231-544-8016 office
1-231-544-6001 fax
www.homeinspectionsusa.us
Reply With Quote
  #5  
Old 1/24/07, 2:39 AM
jclark1's Avatar
jclark1 jclark1 is offline
Active Poster
 
Join Date: Nov 2005
Location: Vashon, Wa
Posts: 644
Please Note: jclark1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: venting

If it is 15' long, it needs about 4" total horizontal rise, and the top of the chimney would have to be 20' above where the connector enters the chimney. Per NFPA 211. http://www.nfpa.org/freecodes/free_access_document.asp
Reply With Quote
  #6  
Old 1/24/07, 6:46 AM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: venting

Quote:
Originally Posted by brepanshek
also saw this. this is a 5" single wall smoke pipe to chimney flue, do you see the the screen on the tee portion of the pipe? This is a naturaql gas furnace and this seems to be acting like a damper to prevent negitive draft for combustion gases. I don't know what this is and if is proper?????
Attachment 8639
Is the natural gas draft induced or natural draft? Is their a draft diverter on the furnace? Yes then this tee needs to be removed. If no then screen needs to be removed as that is the draft diverter. Screening the diverter will cause the flames to lift off the burners and pilot assembly during high draft conditions.
Reply With Quote
  #7  
Old 1/24/07, 11:39 AM
brepanshek brepanshek is offline
Active Poster
 
Join Date: May 2006
Location: York, PA
Posts: 235
Please Note: brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: venting

It is natural draft, and this pic shows it has a heatilator on the smoke pipe. What this is doing is taking the exshaust flue gas heat through a exchanger and a mini blower fan blows the warm air into the basement for additional heat. So way is that screen tee in last pic required if so??????
venting-dscf0013-small-.jpg.JPG
Views:	41
Size:	48.7 KB
ID:	8660
Reply With Quote
  #8  
Old 1/24/07, 10:41 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: venting

That's a draft hood that the heatilator is attached to. No the draft hood tee is not needed and is actually double drafting the furnace and is most likely causing spillage at the furnace's draft hood at times. Write it up for an HVAC Compnay evaluation.
Reply With Quote
  #9  
Old 1/25/07, 1:50 PM
brepanshek brepanshek is offline
Active Poster
 
Join Date: May 2006
Location: York, PA
Posts: 235
Please Note: brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: venting

Thanks
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Venting an oil-fired water heater mh718 Inspecting HVAC Systems 3 11/16/06 9:36 AM
Venting a bathroom in a highrise condo Mark Ellison Inspecting HVAC Systems 1 10/8/06 11:00 PM
mixed fuel venting? sfalvey Inspecting HVAC Systems 7 4/17/06 9:23 AM
Bad Dryer and Bath Fan Venting Jkrt00 Inspecting HVAC Systems 3 3/13/06 11:07 PM
For anyone who needs info on venting! pbolliger Inspecting HVAC Systems 8 2/18/06 8:58 PM


All times are GMT -4. The time now is 7:20 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts