Default Is this venting necessary?

Todays inspection was on a 23 year old condo.

Both the gas hot water heater and boiler are in separate closets on the 2nd floor. Both closets have a short metal vent in the ceiling (assuming to let warm air out (to the attic)) and combustion air in from the attic.

Are these necessary? What are the draw backs and general comments.

It doesn't sit right with me, but I can't put my finger on it.

Also check out the flue pipe job.
Attached Thumbnails
venting-necessary-img_5594.jpg   venting-necessary-img_5597.jpg   venting-necessary-img_5604.jpg   venting-necessary-img_5615.jpg   venting-necessary-img_5622.jpg  




Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #2  
Old 8/13/08, 9:46 PM
Colin Cutler Colin Cutler is offline
New User
 
Join Date: Aug 2008
Posts: 7
Please Note: Colin Cutler is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this venting necessary?

Scott, my take on the vent pipes in the attic is, there's more free air available in the attic than in perhaps a closed closet. but the horizontal flue looks kinda long.
Reply With Quote
  #3  
Old 8/13/08, 10:21 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Is this venting necessary?

That is the way we draw combustion air from attic here in this state all the time almost on every one The short pipe is suppose to be into the closet at least 12 inches and the longer pipe is suppose to be 12 inches from the floor creates a natural circulation.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 8/14/08, 8:41 PM
lfoster's Avatar
lfoster lfoster is offline
Active Poster
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 489
Please Note: lfoster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this venting necessary?

On pic 5, what about the piping that doesn't reach the ceiling vent opening?
Reply With Quote
  #5  
Old 8/14/08, 9:08 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this venting necessary?

Linda, that looks like an opitcal conclusion. I think there are two holes there with the one pipe (against the wall) extending toward the floor.
Reply With Quote
  #6  
Old 8/14/08, 9:14 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Is this venting necessary?

Quote:
Originally Posted by cbottger
That is the way we draw combustion air from attic here in this state all the time almost on every one The short pipe is suppose to be into the closet at least 12 inches and the longer pipe is suppose to be 12 inches from the floor creates a natural circulation.
Combustion air cannot be drawn from the attic. The attic is ventilated to allow air outflow. The attic is under negative pressure, therefore. Stack effect.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #7  
Old 8/14/08, 9:16 PM
sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Is this venting necessary?

Quote:
Originally Posted by Mark Thorman
Linda, that looks like an opitcal conclusion. I think there are two holes there with the one pipe (against the wall) extending toward the floor.
That is correct.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #8  
Old 8/14/08, 9:43 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Is this venting necessary?

Quote:
Originally Posted by wdecker
Combustion air cannot be drawn from the attic. The attic is ventilated to allow air outflow. The attic is under negative pressure, therefore. Stack effect.
03 IRC allows attic combustion air. 1703.2
Reply With Quote
  #9  
Old 8/15/08, 1:30 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: Is this venting necessary?

Attic air here too.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #10  
Old 8/15/08, 8:20 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Is this venting necessary?

Quote:
Originally Posted by wdecker
Combustion air cannot be drawn from the attic. The attic is ventilated to allow air outflow. The attic is under negative pressure, therefore. Stack effect.
It is allowed around here, too, Will.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #11  
Old 8/15/08, 9:05 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Is this venting necessary?

Quote:
Originally Posted by wdecker
Combustion air cannot be drawn from the attic. The attic is ventilated to allow air outflow. The attic is under negative pressure, therefore. Stack effect.
What, Two million homes in Ok improperly vented for combustion air



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #12  
Old 8/15/08, 10:09 AM
msylvester's Avatar
msylvester msylvester is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Batavia, IL
Posts: 672
Send a message via AIM to msylvester
Default Re: Is this venting necessary?

It's OK here in Illinois as well.



Mark Sylvester
P.I. Home Inspection Services
www.pihomeinspection.com
mark@pihomeinspection.com
Reply With Quote
  #13  
Old 8/15/08, 3:14 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Is this venting necessary?

Quote:
Originally Posted by msylvester
It's OK here in Illinois as well.
Mark Chicago is not in Illinois right
</IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #14  
Old 8/15/08, 3:27 PM
msylvester's Avatar
msylvester msylvester is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Batavia, IL
Posts: 672
Send a message via AIM to msylvester
Default Re: Is this venting necessary?

nowhere near Illinois.



Mark Sylvester
P.I. Home Inspection Services
www.pihomeinspection.com
mark@pihomeinspection.com
Reply With Quote
  #15  
Old 8/15/08, 6:23 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Is this venting necessary?

I stand corrected by my peers.

I was always taught that getting combustion air from the attic was wrong, mainly because of the stack effect and that the attic tends to craw air out.

Must have been wrong.

Sorry.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pellet stove help chellickson General Inspection Discussion 23 8/19/10 1:23 AM
Water Heater Venting dedwards Plumbing Inspections 1 8/19/06 12:46 PM
mixed fuel venting? sfalvey Inspecting HVAC Systems 7 4/17/06 9:23 AM
For anyone who needs info on venting! pbolliger Inspecting HVAC Systems 8 2/18/06 8:58 PM


All times are GMT -4. The time now is 12:29 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts