Default Is this venting necessary?

Todays inspection was on a 23 year old condo.

Both the gas hot water heater and boiler are in separate closets on the 2nd floor. Both closets have a short metal vent in the ceiling (assuming to let warm air out (to the attic)) and combustion air in from the attic.

Are these necessary? What are the draw backs and general comments.

It doesn't sit right with me, but I can't put my finger on it.

Also check out the flue pipe job.
Attached Images
File Type: jpg IMG_5594.JPG (118.6 KB, 47 views)
File Type: jpg IMG_5597.JPG (103.4 KB, 49 views)
File Type: jpg IMG_5604.JPG (86.3 KB, 51 views)
File Type: jpg IMG_5615.JPG (54.6 KB, 46 views)
File Type: jpg IMG_5622.JPG (63.8 KB, 65 views)



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
Find an InterNACHI certified Minnesota Home Inspector (and anywhere else in North America)
  #2  
Old 8/13/08, 10:46 PM
Colin Cutler Colin Cutler is offline
New User
 
Join Date: Aug 2008
Posts: 7
Colin Cutler hasn't had much positive or negative feedback
Please Note: Colin Cutler is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this venting necessary?

Scott, my take on the vent pipes in the attic is, there's more free air available in the attic than in perhaps a closed closet. but the horizontal flue looks kinda long.
Reply With Quote
  #3  
Old 8/13/08, 11:21 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,281
Charley L. Bottger .
Default Re: Is this venting necessary?

That is the way we draw combustion air from attic here in this state all the time almost on every one The short pipe is suppose to be into the closet at least 12 inches and the longer pipe is suppose to be 12 inches from the floor creates a natural circulation.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #4  
Old 8/14/08, 9:41 PM
Linda J. Foster's Avatar
Linda J. Foster Linda J. Foster is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 328
Linda J. Foster is generally well trusted
Default Re: Is this venting necessary?

On pic 5, what about the piping that doesn't reach the ceiling vent opening?



Linda Foster
www.HomeInspectionsByFoster.com
HomeInspectionsByFoster@yahoo.com

TREC #7654
InterNACHI #06032691

Reply With Quote
  #5  
Old 8/14/08, 10:08 PM
Mark Thorman Mark Thorman is offline
New User
 
Join Date: Mar 2008
Posts: 78
Mark Thorman is generally well trusted
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this venting necessary?

Linda, that looks like an opitcal conclusion. I think there are two holes there with the one pipe (against the wall) extending toward the floor.
Reply With Quote
  #6  
Old 8/14/08, 10:14 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 5,250
William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information
Default Re: Is this venting necessary?

Quote:
Originally Posted by cbottger
That is the way we draw combustion air from attic here in this state all the time almost on every one The short pipe is suppose to be into the closet at least 12 inches and the longer pipe is suppose to be 12 inches from the floor creates a natural circulation.
Combustion air cannot be drawn from the attic. The attic is ventilated to allow air outflow. The attic is under negative pressure, therefore. Stack effect.



Will Decker
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #7  
Old 8/14/08, 10:16 PM
Scott Falvey Scott Falvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 390
Scott Falvey is generally well trusted
Default Re: Is this venting necessary?

Quote:
Originally Posted by Mark Thorman
Linda, that looks like an opitcal conclusion. I think there are two holes there with the one pipe (against the wall) extending toward the floor.
That is correct.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #8  
Old 8/14/08, 10:43 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 8,061
Brian E. Kelly has a reputation beyond repute Brian E. Kelly has a reputation beyond repute Brian E. Kelly has a reputation beyond repute Brian E. Kelly has a reputation beyond repute Brian E. Kelly has a reputation beyond repute Brian E. Kelly has a reputation beyond repute Brian E. Kelly has a reputation beyond repute Brian E. Kelly has a reputation beyond repute Brian E. Kelly has a reputation beyond repute Brian E. Kelly has a reputation beyond repute Brian E. Kelly has a reputation beyond repute
Default Re: Is this venting necessary?

Quote:
Originally Posted by wdecker
Combustion air cannot be drawn from the attic. The attic is ventilated to allow air outflow. The attic is under negative pressure, therefore. Stack effect.
03 IRC allows attic combustion air. 1703.2



"Dale for MAB"

ps some of the opinions I have posted here may or may not be factually based.




AZ Cert # 39975
AZ Pest # 050898
Reply With Quote
  #9  
Old 8/15/08, 2:30 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,653
David A. Andersen .
Default Re: Is this venting necessary?

Attic air here too.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Infrared Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #10  
Old 8/15/08, 9:20 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 4,037
Larry D. Kage .
Default Re: Is this venting necessary?

Quote:
Originally Posted by wdecker
Combustion air cannot be drawn from the attic. The attic is ventilated to allow air outflow. The attic is under negative pressure, therefore. Stack effect.
It is allowed around here, too, Will.



"An Education, not just an Inspection"


Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525



Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #11  
Old 8/15/08, 10:05 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,281
Charley L. Bottger .
Default Re: Is this venting necessary?

Quote:
Originally Posted by wdecker
Combustion air cannot be drawn from the attic. The attic is ventilated to allow air outflow. The attic is under negative pressure, therefore. Stack effect.
What, Two million homes in Ok improperly vented for combustion air



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #12  
Old 8/15/08, 11:09 AM
Mark Sylvester's Avatar
Mark Sylvester Mark Sylvester is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Batavia, IL
Posts: 667
Mark Sylvester is often very helpful Mark Sylvester is often very helpful Mark Sylvester is often very helpful
Send a message via AIM to msylvester
Default Re: Is this venting necessary?

It's OK here in Illinois as well.



Mark Sylvester
P.I. Home Inspection Services
www.pihomeinspection.com
mark@pihomeinspection.com
Reply With Quote
  #13  
Old 8/15/08, 4:14 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,281
Charley L. Bottger .
Default Re: Is this venting necessary?

Quote:
Originally Posted by msylvester
It's OK here in Illinois as well.
Mark Chicago is not in Illinois right
</IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
Find an InterNACHI certified Minnesota Home Inspector (and anywhere else in North America)
  #14  
Old 8/15/08, 4:27 PM
Mark Sylvester's Avatar
Mark Sylvester Mark Sylvester is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Batavia, IL
Posts: 667
Mark Sylvester is often very helpful Mark Sylvester is often very helpful Mark Sylvester is often very helpful
Send a message via AIM to msylvester
Default Re: Is this venting necessary?

nowhere near Illinois.



Mark Sylvester
P.I. Home Inspection Services
www.pihomeinspection.com
mark@pihomeinspection.com
Reply With Quote
  #15  
Old 8/15/08, 7:23 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 5,250
William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information
Default Re: Is this venting necessary?

I stand corrected by my peers.

I was always taught that getting combustion air from the attic was wrong, mainly because of the stack effect and that the attic tends to craw air out.

Must have been wrong.

Sorry.



Will Decker
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Pellet stove help chellickson General Inspection Discussion 22 8/10/08 5:41 PM
Water Heater Venting dedwards Plumbing 1 8/19/06 1:46 PM
mixed fuel venting? sfalvey HVAC 7 4/17/06 10:23 AM
For anyone who needs info on venting! pbolliger HVAC 8 2/18/06 9:58 PM


All times are GMT -4. The time now is 5:09 AM.


1 2 3 4 5 6 7 8 9