Default Venting question

I've never seen a setup like this one -

The vent on the right is from hot water heater #1.
The middle vent is from the second floor gas fired boiler.
The left vent is from the first floor forced hot air furnace.
There is an additional hot water heater that joins the manifold just out of the picture.

If I'm not mistaken, smaller units should join the vent after/over the larger units. Does this look ok?
Attached Thumbnails
venting-question-dscf0011.jpg  



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #2  
Old 2/7/06, 4:39 PM
Brady Brady is offline
New User
 
Join Date: Feb 2006
Location: Lakeville, MN
Posts: 20
Please Note: Brady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Venting question

Not sure, but I think that if the vent stack is inclining, then it should be OK..
Reply With Quote
  #3  
Old 2/8/06, 8:44 AM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Venting question

Most manufacturers recommend a 10 - 12 inch vertical rise on the vent before elbowing the vent. Don't see that on the water heater. Write it up for the trades to check especially if you see evidence of spillage at the draft hood area.
Reply With Quote
  #4  
Old 2/9/06, 11:13 PM
Robert Wade Robert Wade is offline
New User
 
Join Date: Sep 2005
Posts: 7
Please Note: Robert Wade is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Venting question

Bill, AGA (American Gas Association) and GAMA (Gas Appliance Manufacturers Association) have publication called "Venting Tables Category 1 Central Furnaces" that might help you. It shows examples of multiple fan-assisted and natural vent combinations and the requirements for vent size and capacity.
Reply With Quote
  #5  
Old 2/10/06, 1:41 AM
hspinnler's Avatar
hspinnler hspinnler is offline
Active Poster
 
Join Date: Apr 2005
Location: Hoschton, GA
Posts: 149
Please Note: hspinnler is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Venting question

Quote:
Originally Posted by bsmith
If I'm not mistaken, smaller units should join the vent after/over the larger units. Does this look ok?
I believe you are correct. The smaller appliances should connected to the highest available points above the larger appliance vents.
Reply With Quote
  #6  
Old 2/13/06, 3:04 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Unhappy Re: Venting question

AAAAAHHHHHH!

What a lousy potentially dangerous install!

My local gas company training tells me this:

These should all be cat 1 natural draft appliances... NO mixing of negative pressure and positive pressure should there be any!

Notice the draft hood on the water heater? Take a look at the slope of the flue after the hood! Wrong! Wrong location since it is smaller in diameter then the rest of the flues (Fau's) The smallest flue should be closer to the chimney then the larger one. So much more here.. The hood also looks as if there could be evidence of excessive rusting telling me that draft / draw is improper..

The slope period!!
The size of all these flues in that contraption of a connection! No "Y" gradual sizing connections just one big "manifold" deal...
Sizing issues with respect to all appliances working at the same time and one working by itself!!

GAMA or local gas company requirements ,check the installs regarding Chimney (perhaps no liner to) size and BTU's/ appliances per sizing.. Seven times rule and so on.. Even the Mfg. Installation instructions are # 1 to look at first then AHJ since the appliance Mfg.'s use GAMA guidelines for design..

Last edited by pbolliger; 2/14/06 at 1:59 PM..
Reply With Quote
  #7  
Old 2/14/06, 8:14 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,008
Default Re: Venting question

Excellent post - Thanks Patrick.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Venting Materials question bmargiotti Inspecting HVAC Systems 4 11/15/07 6:08 AM
Venting Question dmacy Inspecting HVAC Systems 4 8/30/07 8:33 PM
Island sink venting question ehyde Plumbing Inspections 4 7/13/07 2:36 AM
Basement Bathroom Venting Question Sean M. Jeric Plumbing Inspections 4 3/21/07 12:56 AM


All times are GMT -4. The time now is 6:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts