Default VERY humid AC air

Did an mould inspection yesterday for people with a very strong musty smell in the house, on their clothes etc, interior doors that stick, a black growth they noticed on some of the register covers among other things. This place has had an extended period of high humidity.

During the inspection I discovered the AC air coming out of the register was about 13 degrees celcius, 80-85% RH. They had a Geothermal unit installed a few years ago. Indoor unit is in a dirt crawlspace with a poor vapour barrier. There was no return and ductwork was sealed pretty good so I don't think it's drawing in much air from the crawl. Duct work was not insulated and had a little condensation on the outside.

This thing is basically working like a swamp cooler adding cool moist air to the house, but our summers here are very humid... not a good combination.

Would there be condensation on the inside of the ductwork adding to the problem or is the Geo Thermal unit just not woring right? It's still under warranty so they are going to have it serviced.



McRae Home Inspections
Goderich, ON
519-955-3277
Reply With Quote
Need a home inspection in Washington? Check out InterNACHI's listing of Washington certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/21/11, 9:11 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: VERY humid AC air

Quote:
Originally Posted by smcrae View Post
Did an mould inspection yesterday for people with a very strong musty smell in the house, on their clothes etc, interior doors that stick, a black growth they noticed on some of the register covers among other things. This place has had an extended period of high humidity.

During the inspection I discovered the AC air coming out of the register was about 13 degrees celcius, 80-85% RH. They had a Geothermal unit installed a few years ago. Indoor unit is in a dirt crawlspace with a poor vapour barrier. There was no return and ductwork was sealed pretty good so I don't think it's drawing in much air from the crawl. Duct work was not insulated and had a little condensation on the outside.

This thing is basically working like a swamp cooler adding cool moist air to the house, but our summers here are very humid... not a good combination.

Would there be condensation on the inside of the ductwork adding to the problem or is the Geo Thermal unit just not woring right? It's still under warranty so they are going to have it serviced.
The supply air fan has to take a suction from somewhere so there has to be a return from somewhere maybe not from the right place but from somewhere. If it is drawing from the crawl that is totally wrong.

All duct work supply and return is required to be insulation in non-conditioned spaces



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #3  
Old 8/21/11, 9:17 AM
Steve McRae's Avatar
Steve McRae Steve McRae is offline
InterNACHI Member
 
Join Date: Feb 2010
Location: Goderich, ON
Posts: 207
Default Re: VERY humid AC air

Sorry, I meant there was no return in the crawlspace which was good. It did have a supply in the crawl, but it was closed. Returns were on the main level. Isulating the ductwork is on my list of recommendations.



McRae Home Inspections
Goderich, ON
519-955-3277
Reply With Quote
  #4  
Old 8/21/11, 9:31 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: VERY humid AC air

Sounds like the AC unit is too big and not running long enough to remove the moisture????????

I think so ... Roy ....

A.....simple fix add a dehumidifier but not very cost efficient .



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #5  
Old 8/21/11, 9:38 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: VERY humid AC air

Quote:
Originally Posted by smcrae View Post
Sorry, I meant there was no return in the crawlspace which was good. It did have a supply in the crawl, but it was closed. Returns were on the main level. Isulating the ductwork is on my list of recommendations.
No problem just trying to get the big picture. Humidity at 80%-85% is almost like raining inside the home the A/C system can only remove a limited amount of moisture depending on the run time of the unit and if mold is growing on the registers you have a serious problem, was the A/C system over sized for the home what was the cycle time between on and off. I would very seriously check the return air side of the system to ensure no external air was being introduced into the system



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #6  
Old 8/21/11, 10:25 AM
Steve McRae's Avatar
Steve McRae Steve McRae is offline
InterNACHI Member
 
Join Date: Feb 2010
Location: Goderich, ON
Posts: 207
Default Re: VERY humid AC air

Thanks guys. Sizing might be the issue. Will recommend further review on that. I mentioned adding a dehumidifier as a bandaid, but would be a costly battle with that air.



McRae Home Inspections
Goderich, ON
519-955-3277
Reply With Quote
  #7  
Old 8/21/11, 11:42 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: VERY humid AC air

Quote:
Originally Posted by smcrae View Post
Did an mould inspection yesterday for people with a very strong musty smell in the house, on their clothes etc, interior doors that stick, a black growth they noticed on some of the register covers among other things. This place has had an extended period of high humidity.

During the inspection I discovered the AC air coming out of the register was about 13 degrees celcius, 80-85% RH. They had a Geothermal unit installed a few years ago. Indoor unit is in a dirt crawlspace with a poor vapour barrier. There was no return and ductwork was sealed pretty good so I don't think it's drawing in much air from the crawl. Duct work was not insulated and had a little condensation on the outside.

This thing is basically working like a swamp cooler adding cool moist air to the house, but our summers here are very humid... not a good combination.

Would there be condensation on the inside of the ductwork adding to the problem or is the Geo Thermal unit just not woring right? It's still under warranty so they are going to have it serviced.

No, that is not correct.

I have no time to teach you the laws of thermodynamics and psyhcrometrics at this time, all I can say is that you are so far out in left field, your out of the park!

I recommend that you get someone (other than an HVAC Contractor) to work with you on this.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #8  
Old 8/21/11, 12:06 PM
Steve McRae's Avatar
Steve McRae Steve McRae is offline
InterNACHI Member
 
Join Date: Feb 2010
Location: Goderich, ON
Posts: 207
Default Re: VERY humid AC air

David, what specifically is not correct?



McRae Home Inspections
Goderich, ON
519-955-3277
Reply With Quote
  #9  
Old 8/21/11, 3:00 PM
rspermo rspermo is offline
Active Poster
 
Join Date: Feb 2009
Posts: 155
Please Note: rspermo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: VERY humid AC air

Steve,

Alot of "duct leakage" is actually leakage through the air handler cabinet. I have seen studies where as much as 505 of the total "duct leakage" is actually in the air handler. I would guess that the house returns are few and undersized so the system must get return air (to balance off the supply air flow) from somewhere! That somewhere would be through the air handler leaks in the crawlspace without a moisture barrier. The moist air in the crawlspace is in fact entering the home's air flow.
Reply With Quote
  #10  
Old 8/21/11, 4:43 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: VERY humid AC air

If there is high humidity in the crawlspace, there is more of a problem than just the air conditioning.



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
  #11  
Old 8/21/11, 7:12 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: VERY humid AC air

Quote:
Originally Posted by smcrae View Post
Did an mould inspection yesterday for people with a very strong musty smell in the house, on their clothes etc, interior doors that stick, a black growth they noticed on some of the register covers among other things. This place has had an extended period of high humidity.

During the inspection I discovered the AC air coming out of the register was about 13 degrees celcius, 80-85% RH. They had a Geothermal unit installed a few years ago. Indoor unit is in a dirt crawlspace with a poor vapour barrier. There was no return and ductwork was sealed pretty good so I don't think it's drawing in much air from the crawl. Duct work was not insulated and had a little condensation on the outside.

This thing is basically working like a swamp cooler adding cool moist air to the house, but our summers here are very humid... not a good combination.

Would there be condensation on the inside of the ductwork adding to the problem or is the Geo Thermal unit just not woring right? It's still under warranty so they are going to have it serviced.

#1 All registers condense in humid conditions.
Is indoor 24C / 50% rh OK for you?
If so, it will sweat when the a/c turns off.

#2 What is "Wrong" with 13C / 85%rh? You tell me.

I'll tell you this;
13C 85% changes when mixed with indoor air.

16C will become 70%
18C will become 60%
21C will become 50%
24C will become 40%

#3 There is no way in hell it is working like a swamp cooler (period).

#4 Condensation inside duct? No, it will not.
As the air moves downstream from the evap coil (which is even colder) it warms up. The evap coil is at "saturation". ANY Rise in air temp will lower the rh below dew point. Unless there is something in the house that is colder than the evap coil, it can not condense.

What happens on the outside of the register is not the same thing.
When you stop the air flow, the register comes in more contact with the indoor ambient air which has more moisture than that which comes out of the duct.

85% rh is not a moisture quantity measurement.
Figurer that out and all things will become clear.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission

Last edited by dandersen; 8/21/11 at 7:17 PM..
Reply With Quote
  #12  
Old 8/22/11, 3:35 AM
Steve McRae's Avatar
Steve McRae Steve McRae is offline
InterNACHI Member
 
Join Date: Feb 2010
Location: Goderich, ON
Posts: 207
Default Re: VERY humid AC air

Thanks Sheldon. You are reading too much into my comments. My wife keeps telling me our kids don't get my sarcasm, I guess it doesn't translate well online either.
Not worried about that now, going to be too busy helping rebuild our town after it was badly hit by a tornado.



McRae Home Inspections
Goderich, ON
519-955-3277
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Moisture Management mcyr Exterior Inspections 15 9/8/08 12:11 PM
Kickout flashing Problem? Bonnie Gillis Exterior Inspections 10 12/27/06 9:37 PM