Default Water Detection Devise

I was inspecting an air handler in the attic of today’s home. The air handler had a secondary condensation pan with a water detection float device beneath the unit. My shirt sleeve snagged the float device and pulled it. The system did not shut off. My curiosity got the best of me and I raise the float device and the system still did not shut down.

My question is do these floats have to absorb water to shut down the system like a rain sensor on an irrigation system, or was the water float likely not wired properly or defective? Should I make a point to check the the water detection devices on air handlers in attics?

Thanks in advance.
Reply With Quote
  #2  
Old 6/1/07, 10:32 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water Detection Devise

What do you mean by "the system"???

Depending on the installer's preference, some of the floats are wired to break "Y" and some break "R". Either one will stop the condensation, which is the goal, but breaking only "Y" will permit the fan to continue running. This may be what you observed, and is no problem. Unless you are in a postion to operate the float and observe the condensing unit at the same time, it would be difficult to inspect this device.
Reply With Quote
  #3  
Old 6/1/07, 10:52 PM
Mathew Hawley Mathew Hawley is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 782
Default Re: Water Detection Devise

Thanks Marc,

That makes sense, if the condenser shut off and i was in the attic I guess the only way to tell would be to make sure the temp at the plenum did not increase after a min. or so.

Thanks again

Last edited by mhawley; 6/1/07 at 10:56 PM..
Reply With Quote
  #4  
Old 6/2/07, 10:55 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: Water Detection Devise

If you do not have a time delay on the condensor, the lights in the attic will dim when you release the float switch and the compressor starts. If they don't, you have to find another way to prove the shut-down.

My next favorite would be to feel the warming of the suction refrigerant line at the furance (if the condensor shuts down).
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Need Help On Chimney Liners Nick Scibetta Exterior Inspections 13 1/11/06 9:53 PM


All times are GMT -4. The time now is 12:30 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts