Is this acceptacle ? this was in the clients garage.
The two were side/side, the water was less than 18inches above the floor. David
|
|
#2
|
|||
|
|||
|
I am more worried about the TPRV not being piped, the electric going to the furnace, the appliance connector going thru the unit casing, the lack of a drip leg, a 90 right off of the furnace, and I guess you could throw in if it was only 16" instead of 18" off of the floor.
1st Inspection Services Bruce M. Graham III Gainesville, FL 32608 352 871 8989 Florida Licensed Home Inspector #HI10 Radon Measurment Technician # R2279 NACHI05091592 ICC 5268478 www.1stinspectionsfl.com www.bungalowstomansions.com |
|
#3
|
||||
|
||||
|
If that build-up is 16" off the floor, then it will probably be alright. The gap between the floor and the bottom of the burner is likely to be at least 2", so total will be 18".
Jeff |
|
#4
|
||||
|
||||
|
What Bruce said, and is that the dryer vent laying on the floor?
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|