Default Water Heater Exhaust Location with Furnace and Masonry Chimney

I ran across this one recently and wanted to confirm this is an improper installation. The water heater (2006) is naturally vented natural gas rated at 40,000 BTU/hr. The furnace (1967) is naturally vented natural gas furnace rated at 105,000 BTU/Hr.

The age of the furnace is a different subject. The water heater vent is approximately 12" BELOW the furnace in a common 8 x 8 flue. I called it as a safety problem since the smaller BTU appliance should be located ABOVE the larger BTU appliance. Your Thoughts?
Attached Thumbnails
water-heater-exhaust-location-furnace-and-masonry-chimney-p1270782-1.jpg   water-heater-exhaust-location-furnace-and-masonry-chimney-p1270703.jpg  



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/13/11, 12:52 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Water Heater Exhaust Location with Furnace and Masonry Chimney

Quote:
Originally Posted by gliebig View Post
I ran across this one recently and wanted to confirm this is an improper installation. The water heater (2006) is naturally vented natural gas rated at 40,000 BTU/hr. The furnace (1967) is naturally vented natural gas furnace rated at 105,000 BTU/Hr.

The age of the furnace is a different subject. The water heater vent is approximately 12" BELOW the furnace in a common 8 x 8 flue. I called it as a safety problem since the smaller BTU appliance should be located ABOVE the larger BTU appliance. Your Thoughts?
It should enter above. Correct.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #3  
Old 5/13/11, 6:09 PM
Gary Farnsworth Gary Farnsworth is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 3,715
Default Re: Water Heater Exhaust Location with Furnace and Masonry Chimney

Any time I see a hot water heater and/or a furnace venting into a chimney flue, especially when the flue runs through the center of a home, I recommend installation of a metal chimney liner/flue to the top of the chimney to keep gases from migrating through the mortar of the flue joints.



CMI, CPI, KS #0110-0094 Termite #16601
KS Radon #KS-MS-0027
BBB A+ Accredited Business
Serving the Greater Kansas City Metro Area
Eastern Kansas/Western Missouri
http://www.metrospeckc.com
"If opportunity doesn't knock, build a door"--Milton Berle
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Coming soon. Free, online, fireplace and chimney inspection course. gromicko General Inspection Discussion 15 12/14/09 4:19 PM
What's Inside A Chimney mcyr Inspecting HVAC Systems 14 9/17/08 6:11 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues for Inspectors 294 2/10/08 1:20 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM


All times are GMT -4. The time now is 12:30 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts