Default Water heater vent ducting...need advice

Metal ducting leads up to ...what looks like an older asbestos vent piping.
Should this be called out.....( that the asbestos vent pipe should removed ) and replaced with current duct materials?


David




An Ounce of prevention is better
than a pound of cure :}
Reply With Quote
Need a home inspection in Vermont? Check out InterNACHI's listing of Vermont certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/27/11, 5:27 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Water heater vent ducting...need advice

It's probably Transite and looks in good condition. I would mention it's presence only, but would definately report on the improper mounting/brackets attempting to hold it in place. Is that twine???
Reply With Quote
  #3  
Old 8/27/11, 5:29 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Water heater vent ducting...need advice

"The vent includes a Transite pipe, which is comprised of a solid, cement-like material that is known to contain asbestos fibers. Admittedly, these fibers could not easily escape from within the material, but the majority of heat vents, and certainly those that pass through attics, are required to be double-walled, or Type-B. And, as an imperceptible crack in a single-walled vent pipe could result in a fire, we recommend that the Transite pipe be replaced with a modern double-walled type."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 8/27/11, 5:36 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Water heater vent ducting...need advice

Quote:
Originally Posted by jfunderburk View Post
"The vent includes a Transite pipe, which is comprised of a solid, cement-like material that is known to contain asbestos fibers. Admittedly, these fibers could not easily escape from within the material, but the majority of heat vents, and certainly those that pass through attics, are required to be double-walled, or Type-B. And, as an imperceptible crack in a single-walled vent pipe could result in a fire, we recommend that the Transite pipe be replaced with a modern double-walled type."
Nice comment Joe, but I don't think I agree completely with it. I don't have time to look it up now, but I believe your requirement applies to metal vent material only. Even so, I would consider adding your comment to my report, depending upon more information of it's condition, as a suggestion vs a recommendation, for safety of course.
Reply With Quote
  #5  
Old 8/27/11, 5:38 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Water heater vent ducting...need advice

Quote:
Originally Posted by jfunderburk View Post
"The vent includes a Transite pipe, which is comprised of a solid, cement-like material that is known to contain asbestos fibers. Admittedly, these fibers could not easily escape from within the material, but the majority of heat vents, and certainly those that pass through attics, are required to be double-walled, or Type-B. And, as an imperceptible crack in a single-walled vent pipe could result in a fire, we recommend that the Transite pipe be replaced with a modern double-walled type."

The underlined is an important comment with transite pipe.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #6  
Old 8/27/11, 5:41 PM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: Water heater vent ducting...need advice

Quote:
Originally Posted by jjonas View Post
It's probably Transite and looks in good condition. I would mention it's presence only, but would definately report on the improper mounting/brackets attempting to hold it in place. Is that twine???

Thanks Jeff....



An Ounce of prevention is better
than a pound of cure :}
Reply With Quote
  #7  
Old 8/27/11, 5:43 PM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: Water heater vent ducting...need advice

Quote:
Originally Posted by jfunderburk View Post
"The vent includes a Transite pipe, which is comprised of a solid, cement-like material that is known to contain asbestos fibers. Admittedly, these fibers could not easily escape from within the material, but the majority of heat vents, and certainly those that pass through attics, are required to be double-walled, or Type-B. And, as an imperceptible crack in a single-walled vent pipe could result in a fire, we recommend that the Transite pipe be replaced with a modern double-walled type."

Thanks Joe...Im going to save this info.



An Ounce of prevention is better
than a pound of cure :}
Reply With Quote
  #8  
Old 8/27/11, 5:44 PM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: Water heater vent ducting...need advice

Quote:
Originally Posted by lkage View Post
The underlined is an important comment with transite pipe.
Thanks larry....



An Ounce of prevention is better
than a pound of cure :}
Reply With Quote
  #9  
Old 8/27/11, 11:17 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Water heater vent ducting...need advice

And EPA says:
Quote:
Asbestos-Cement Pipe

EPA considers asbestos-cement pipe to be a "facility component" (as defined in 40 CFR 61.141) of the facility which owns or utilizes the pipe. In addition, EPA considers asbestos- cement pipe to be Category II nonfriable asbestos containing material. This material becomes "regulated asbestos containing material" (RACM), as defined in 40 CFR 61.141, when it becomes "friable asbestos material" or when it "has a high probability of becoming or has become crumbled, pulverized or reduced to powder by the forces expected to act on the material during the course of demolition or renovation operations regulated by [40 CFR Part 61 Subpart M]." Consequently, the crushing of asbestos-cement pipe with mechanical equipment will cause this material to become RACM. The demolition and renovation provisions in 40 CFR 61.145 and the waste disposal provisions in 40 CFR 61.150 apply to asbestos-cement pipe where the pipe is considered RACM, and the amount of pipe being removed and crushed is at least 260 linear feet for a single renovation project or during a calendar year for individual nonscheduled operations.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #10  
Old 8/28/11, 1:29 AM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: Water heater vent ducting...need advice

Quote:
Originally Posted by mlarson View Post
And EPA says:[/left]

Thanks Michael....Im going to save all this info.



An Ounce of prevention is better
than a pound of cure :}
Reply With Quote
  #11  
Old 8/28/11, 9:17 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Water heater vent ducting...need advice

Quote:
Originally Posted by jjonas View Post
Nice comment Joe, but I don't think I agree completely with it. I don't have time to look it up now, but I believe your requirement applies to metal vent material only. Even so, I would consider adding your comment to my report, depending upon more information of it's condition, as a suggestion vs a recommendation, for safety of course.
Modern standards identify B-vents as "double-walled steel vents," but the Transite piping used in these applications were (at that time) classified as "Listed B-vents."

The biggest concern (for me) is the potential for cracks that cannot be seen, but will allow heat to escape. For this reason, I always recommend replacement as a "recommended safety upgrade."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 8/28/11, 9:25 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Water heater vent ducting...need advice

Thanks Jeff. I wasn't aware of the Transite classification being a "B-vent" (at the time).

Another concern, would be the exposure to elements above the roofline, but the OP didn't comment on that.
Reply With Quote
  #13  
Old 8/28/11, 9:43 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Water heater vent ducting...need advice

Something else to consider.

The ground doesn't shake so much in the midwest Jeff Pope.

Do you know of cracks appearing in transite if it has not been subjected to mechanical impact?

It was use around here sub slab heating duct but since it is considered non friable creating air born particles is difficult unless it is crushed.

I make the client aware of the issue but do not recommend replaceent if it does not appear subject to mechnical damage. YMMV



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
Need a home inspection in Vermont? Check out InterNACHI's listing of Vermont certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 8/28/11, 7:05 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Water heater vent ducting...need advice

Quote:
Originally Posted by mlarson View Post
The ground doesn't shake so much in the midwest Jeff Pope.
That's true, and based on the damage caused in that Virgina tremor last week, it seems the rest of the country is a "third-world country" with regard to seismic requirements

I couldn't believe the extent of the damage caused by that little shaker.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #15  
Old 8/28/11, 9:01 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Water heater vent ducting...need advice

Quote:
Originally Posted by jpope View Post
That's true, and based on the damage caused in that Virgina tremor last week, it seems the rest of the country is a "third-world country" with regard to seismic requirements
Many people are surprised that there are actually significant fault lines running throughout the US, including one that runs right below NYC not too far from me. But the ones in CA are much more active and severe. You would probably never know it unless you looked at a USGS/FEMA seismic risk map.

Quote:
Originally Posted by jpope View Post
I couldn't believe the extent of the damage caused by that little shaker.
I felt it on Long Island, NY ... it shook my house a bit ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Exterior tankless water heater vent clearance jfrederick Plumbing Inspections 12 1/31/11 11:46 PM
Staining around water heater vent piping? dnasser Inspecting HVAC Systems 5 11/3/09 3:36 PM
Tankless Water Heater Recall ldapkus Plumbing Inspections 1 2/22/07 8:34 PM
Hot Water Heater djohnson6 Plumbing Inspections 12 12/28/06 9:18 PM


All times are GMT -4. The time now is 12:30 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts