Default Whats the problem?

2 side by side units for a duplex today.

The upstairs one was checked first.
70 deg out of most vents with my temp gun.

The upstairs unit was struggling to keep up.

"Thats funny" so I turn down the a/c thinking just a little more load.

"Still not working right, and still 69 to 70 deg" "78 off of the return" I go out and grab the compressor suction line. "cold as ice".

Now what??? I check the tag, and it was sized just right.


I go back to the furnaces and "oh there is the problem!!!!"

Can you spot the problem?
Attached Thumbnails
whats-problem-p7280093.jpg  




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/28/11, 8:48 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Whats the problem?

Are you referring to the reduction in the high pressure line?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 7/28/11, 8:55 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Whats the problem?

Quote:
Originally Posted by jpope View Post
Are you referring to the reduction in the high pressure line?
You know the answer. Stop spoiling all the fun.

and yes it was about 130 deg to the touch..




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #4  
Old 7/28/11, 10:36 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Whats the problem?

That reduction is not going to make it as bad as you found it.

Look at the crimped/damaged spot a foot down the line from the reduction.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #5  
Old 7/28/11, 10:57 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Whats the problem?

Quote:
Originally Posted by sfogarty View Post
2 side by side units for a duplex today.
"Thats funny" so I turn down the a/c thinking just a little more load.
Hey big boy what are you saying here if you turn down the stat it will put more load on the unit or perhaps your thinking it makes the unit get colder by turning down the Stat
Now that is Really FUNNY we need to talk



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #6  
Old 7/28/11, 11:55 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: Whats the problem?

A reduced line will not get hotter, it gets cooler.

The suction line will not be cold if there is a liquid line restriction.

130 F is a dirty condenser coil (even if it looks clean)...

So what was the question?



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #7  
Old 7/29/11, 10:43 AM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Whats the problem?

Quote:
Originally Posted by cbottger View Post
Hey big boy what are you saying here if you turn down the stat it will put more load on the unit or perhaps your thinking it makes the unit get colder by turning down the Stat
Now that is Really FUNNY we need to talk
Wow Charley, thanks for ridiculing me on the board.
If you want clairity since i was not techinical enough for you, I thought that it may have been at the end of the cycle where only the fan was still running and turning the air down would have started the compressor again.
Sorry I can't be an expert like you.

You should be happy a dumb inspector like myself actually discovered the unit had this problem and it was not cooling properly..




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net

Last edited by sfogarty; 7/29/11 at 10:47 AM..
Reply With Quote
  #8  
Old 7/29/11, 10:45 AM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Whats the problem?

Quote:
Originally Posted by dandersen View Post
A reduced line will not get hotter, it gets cooler.

The suction line will not be cold if there is a liquid line restriction.

130 F is a dirty condenser coil (even if it looks clean)...

So what was the question?
I thought the reduction was causing the unit to run constantly, therfore not being able to cool enough.
The copmressors were not dirty looking BTW. How much do you think a line that reduced woul lower the tonnage? The unit was a 2 ton.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #9  
Old 7/29/11, 1:05 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Whats the problem?

Quote:
Originally Posted by sfogarty View Post
Wow Charley, thanks for ridiculing me on the board.
If you want clairity since i was not techinical enough for you, I thought that it may have been at the end of the cycle where only the fan was still running and turning the air down would have started the compressor again.
Sorry I can't be an expert like you.

You should be happy a dumb inspector like myself actually discovered the unit had this problem and it was not cooling properly..
Hey I am not ridiculing you just having a little fun with you thought Wayne had taught you better than that the way you made your statement was kinda funny made me laugh anyway. Lighten up you take every thing a little to serious.

That down size in the refrigerant line will reduce that unit approximately 1/2 ton.

I am happy you discovered the downsized line I have put pictures up of that very item at least twice on this board and some thought it was frivolous. Those kind of finds separate the real home inspectors from the desk jocks or wanta be inspectors



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #10  
Old 7/29/11, 1:28 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Whats the problem?

Little grass hopper can be mean Charlie lololol



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #11  
Old 7/29/11, 2:30 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: Whats the problem?


When sizing liquid refrigerant lines; it's liquid refrigerant and oil mix completely, velocity is not essential for oil circulation liquid line. The primary concern in liquid line sizing is to ensure a solid liquid had the refrigerant at the expansion valve. If the pressure of the liquid refrigerant falls below its saturation temperature, a portion of the liquid will flash into vapor and cool the liquid refrigerant to the new saturation temperature. This can occur in a liquid line if the pressure drops significantly due to friction or vertical left.
Flash gas in the liquid line has a detrimental effect on system performance for several reasons. It increases the pressure drop due to friction. It reduces the capacity of the expansion valve. It may erode the metering device components. It also causes erratic feeding of the liquid refrigerant to the evaporator which reduces its capacity.
So long as the refrigerant that reaches the metering device is properly sub cooled below its saturation temperature there is generally not a problem associated with liquid line sizing.
Liquid line pressure drop causes no direct penalty in power consumption and a decrease in system capacity due to friction losses in the liquid line is negligible. Because of this, the only real restriction on the amount of liquid pressure drop is the amount of sub cooling available.
The design of refrigerant piping is a series of compromises. The effect of sizing a liquid refrigerant line is a compromise between restricted flow and too much refrigerant in the system, both of which adversely affect its performance.
Unless you are prepared to compute the performance of the HVAC system by using the hundreds of charts available, simply calling out a refrigeration line that is smaller than the input line of the evaporator coil is just another "wild *** guess " that home inspectors should keep away from.
The reason that the unit is running constantly is because of the latent heat in the air we are experiencing this week! The unit is undersized because it was not designed for 100° outdoor air temperatures.
As I said, regardless of what the condensers look like, they can be dirty even though they look clean. The ultimate identifier for the home inspector is a hot liquid line.
The only time that the liquid line will become hot other than a dirty coil is if there is not enough refrigerant in the system. Refrigerant passes through the system too rapidly and does not have time to properly sub cool. In this case the suction refrigerant line will not be cool ( as you described).



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #12  
Old 7/29/11, 2:42 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Whats the problem?

As you know it will usually void a MFG warranty if one decreases the size of the liquid line from what the MFG intended by the size of the stub out. The problem is the old units that used a 1/4 inch liquid line are now being replaced with new units that require 3/8 and contractors are not updating the liquid line I see it quite frequently and IMO every HI should call it out



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #13  
Old 7/29/11, 5:44 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Whats the problem?

Quote:
Originally Posted by cbottger View Post
Hey I am not ridiculing you just having a little fun with you thought Wayne had taught you better than that the way you made your statement was kinda funny made me laugh anyway. Lighten up you take every thing a little to serious.

That down size in the refrigerant line will reduce that unit approximately 1/2 ton.

I am happy you discovered the downsized line I have put pictures up of that very item at least twice on this board and some thought it was frivolous. Those kind of finds separate the real home inspectors from the desk jocks or wanta be inspectors
I'm sorry Charlie you just got my panties in a bunch.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/29/11, 6:26 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Whats the problem?

Quote:
Originally Posted by sfogarty View Post
You should be happy a dumb inspector like myself actually discovered the unit had this problem and it was not cooling properly..
Determining that the unit was not operating properly indicates that you are not "dumb"...rather it shows that you did your job well.

It is not the deign of the Home Inspector to determine why a defect exists nor how it should be repaired--unless you wish to step in a certain pile.

If HVAC is not your buttered toast--recommend an expert.

Ain't nobody what knows everything (except maybe me) so don't feel bad about recommending experts.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #15  
Old 7/29/11, 6:45 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Whats the problem?

Quote:
Originally Posted by sfogarty View Post
I'm sorry Charlie you just got my panties in a bunch.

That is fine no problem do you wear pink ruffled panties or just plain panties



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Weird water heater problem kweiss Plumbing Inspections 3 4/5/09 6:34 PM
furnace problem ? Aaron lore General Inspection Discussion 11 2/5/09 1:04 PM
Internet browser problem bking Miscellaneous Discussion for Inspectors 33 1/26/09 1:45 AM
I have a problem cbottger Electrical Inspections 17 1/20/09 4:45 PM
Plumbing problem at home. mnahrgang Plumbing Inspections 25 7/10/07 5:32 PM


All times are GMT -4. The time now is 12:33 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts