2 side by side units for a duplex today.
The upstairs one was checked first. 70 deg out of most vents with my temp gun. The upstairs unit was struggling to keep up. "Thats funny" so I turn down the a/c thinking just a little more load. "Still not working right, and still 69 to 70 deg" "78 off of the return" I go out and grab the compressor suction line. "cold as ice". Now what??? I check the tag, and it was sized just right. I go back to the furnaces and "oh there is the problem!!!!" Can you spot the problem? Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
| Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Are you referring to the reduction in the high pressure line?
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
You know the answer. Stop spoiling all the fun.
and yes it was about 130 deg to the touch.. Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#4
|
||||
|
||||
|
That reduction is not going to make it as bad as you found it.
Look at the crimped/damaged spot a foot down the line from the reduction. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#5
|
||||
|
||||
|
Quote:
Now that is Really FUNNY we need to talk Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#6
|
||||
|
||||
|
A reduced line will not get hotter, it gets cooler.
The suction line will not be cold if there is a liquid line restriction. 130 F is a dirty condenser coil (even if it looks clean)... So what was the question? "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#7
|
||||
|
||||
|
Quote:
If you want clairity since i was not techinical enough for you, I thought that it may have been at the end of the cycle where only the fan was still running and turning the air down would have started the compressor again. Sorry I can't be an expert like you. You should be happy a dumb inspector like myself actually discovered the unit had this problem and it was not cooling properly.. Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net Last edited by sfogarty; 7/29/11 at 10:47 AM.. |
|
#8
|
||||
|
||||
|
Quote:
The copmressors were not dirty looking BTW. How much do you think a line that reduced woul lower the tonnage? The unit was a 2 ton. Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#9
|
||||
|
||||
|
Quote:
That down size in the refrigerant line will reduce that unit approximately 1/2 ton. I am happy you discovered the downsized line I have put pictures up of that very item at least twice on this board and some thought it was frivolous. Those kind of finds separate the real home inspectors from the desk jocks or wanta be inspectors Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#10
|
||||
|
||||
|
Little grass hopper can be mean Charlie lololol
Wayne Wilson East TN Home Inspections LLC Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-1490 http://site.myhomeinspection.net |
|
#11
|
||||
|
||||
|
When sizing liquid refrigerant lines; it's liquid refrigerant and oil mix completely, velocity is not essential for oil circulation liquid line. The primary concern in liquid line sizing is to ensure a solid liquid had the refrigerant at the expansion valve. If the pressure of the liquid refrigerant falls below its saturation temperature, a portion of the liquid will flash into vapor and cool the liquid refrigerant to the new saturation temperature. This can occur in a liquid line if the pressure drops significantly due to friction or vertical left. Flash gas in the liquid line has a detrimental effect on system performance for several reasons. It increases the pressure drop due to friction. It reduces the capacity of the expansion valve. It may erode the metering device components. It also causes erratic feeding of the liquid refrigerant to the evaporator which reduces its capacity. So long as the refrigerant that reaches the metering device is properly sub cooled below its saturation temperature there is generally not a problem associated with liquid line sizing. Liquid line pressure drop causes no direct penalty in power consumption and a decrease in system capacity due to friction losses in the liquid line is negligible. Because of this, the only real restriction on the amount of liquid pressure drop is the amount of sub cooling available. The design of refrigerant piping is a series of compromises. The effect of sizing a liquid refrigerant line is a compromise between restricted flow and too much refrigerant in the system, both of which adversely affect its performance. Unless you are prepared to compute the performance of the HVAC system by using the hundreds of charts available, simply calling out a refrigeration line that is smaller than the input line of the evaporator coil is just another "wild *** guess " that home inspectors should keep away from. The reason that the unit is running constantly is because of the latent heat in the air we are experiencing this week! The unit is undersized because it was not designed for 100° outdoor air temperatures. As I said, regardless of what the condensers look like, they can be dirty even though they look clean. The ultimate identifier for the home inspector is a hot liquid line. The only time that the liquid line will become hot other than a dirty coil is if there is not enough refrigerant in the system. Refrigerant passes through the system too rapidly and does not have time to properly sub cool. In this case the suction refrigerant line will not be cool ( as you described). "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#12
|
||||
|
||||
|
As you know it will usually void a MFG warranty if one decreases the size of the liquid line from what the MFG intended by the size of the stub out. The problem is the old units that used a 1/4 inch liquid line are now being replaced with new units that require 3/8 and contractors are not updating the liquid line I see it quite frequently and IMO every HI should call it out
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#13
|
||||
|
||||
|
Quote:
Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
| Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
|||
|
|||
|
Quote:
It is not the deign of the Home Inspector to determine why a defect exists nor how it should be repaired--unless you wish to step in a certain pile. If HVAC is not your buttered toast--recommend an expert. Ain't nobody what knows everything (except maybe me) so don't feel bad about recommending experts. "not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#15
|
||||
|
||||
|
That is fine no problem do you wear pink ruffled panties or just plain panties Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Weird water heater problem | kweiss | Plumbing Inspections | 3 | 4/5/09 6:34 PM |
| furnace problem ? | Aaron lore | General Inspection Discussion | 11 | 2/5/09 1:04 PM |
| Internet browser problem | bking | Miscellaneous Discussion for Inspectors | 33 | 1/26/09 1:45 AM |
| I have a problem | cbottger | Electrical Inspections | 17 | 1/20/09 4:45 PM |
| Plumbing problem at home. | mnahrgang | Plumbing Inspections | 25 | 7/10/07 5:32 PM |