1998 Rheem furnace installed in garage. What is the white stuff and/or how is it formed? A form of efflorescence perhaps? Additionally, there was some on the B-vent joints in the attic. Any help/insight is appreciated.
|
| Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
|||
|
|||
|
Anyone???
|
|
#3
|
|||
|
|||
|
On the vent pipe it appears at the seams of the elbows and appears to be concentrated in one area. Is it possible that there was an external factor? eg Could the stuff have fallen, landed, or dripped in while other work was being done. The pattern in the furnace looks the same as what you would find on the floor if you cut out a piece of wallboard to install another outlet.....dust picked up by the exhaust vent and allowed to exit at the seam of the elbow. The elbow shows signs of corrosion. The seams show signs of corrosion, pinholes through which the dust/material coould exit????
I am not a HVAC guy, this is just a SWAG. |
|
#4
|
||||
|
||||
|
On the flue, I'm guessing this is what corrosion looks like on galvanized metal. I assume you referred it to a specialist because it's too close to the wood.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#5
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Corrosion....... most likely caused by wind driven rain leakage past the rain cap. In the case of extremely low flue gas temps, moisture could be from condensation in the flue.
|
|
#6
|
|||
|
|||
|
Please Note:
rsummers is a non-member guest and is in no way affiliated with InterNACHI or its members.
Flue gases need to be at a high enough temperature to prevent the condensation that is taking place in this flue vent.What you see are the mineral deposits left after the water evaporates. The moisture will cause premature failure of the flue vent & possible damage the vent motor & cause the reference tube on the inducer housing to plug up with minerals. If the unit is not operating in the top 2/3 of the temperature rise chart found in unit you can try lower blower speeds & check gas supply pressure.
|
|
#7
|
||||
|
||||
|
Condensation from condensing type furnace. HVAC video training class for home inpsectors on NACHI.TV it is a outstanding class.
Mid America Property Inspections, Inc. Shawnee, KS 66217 www.mapii.com NACHI # 05110992 KHIRB # 0110-0008 KS-Radon Cert.# KS-MS-0035 KS-Termite Cert. # 18933 M0-Termite Cert. # N 5033 |
|
#8
|
||||
|
||||
|
Quote:
"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com SmithHomeInspection@yahoo.com NY State Lic. # 16000008304 631-434-5200 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| White Substance On Ducts and Metal??? | krigler | Inspecting HVAC Systems | 14 | 2/2/10 6:48 PM |
| White substance in the attic | dlee2 | Interior Inspections | 7 | 12/8/09 12:56 PM |
| What is this White substance on Crawlspace lumber | rcole | General Inspection Discussion | 4 | 7/4/09 7:40 PM |
| White powdery substance | sjohns | Inspecting HVAC Systems | 13 | 1/30/09 11:13 PM |