Default Why amp meters

I performed a inspection yesterday so far in the boonies that my cell phone had no service????

This inspection was what I call a typical farm or redneck type of home. The electrical made the hair on the back of my neck stand up and I won't go into all of the Gorey details as I listed over 2k in repairs.

I would like to express the importance of a good amp meter as there were two items that would never have been detected if the meter had not been used.

The bottom element on the electric hot water heater was not working drawing no amps with the tank full of cold water.

The electrical heat strips for the furnace had a bank of 3 elements and the center bank was cycling on a safety control on and off with the stat turned as high as it would go. This would not have been detected with out the amp meter.

Bottom line give your clients a run for their money. This was all detected with just the removal of normal excess panels.
Reply With Quote
  #2  
Old 1/10/07, 1:42 AM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,323
Default Re: Why amp meters

Charley

This is what it is all about

I know that many will be upset that you used a clamp on amp meter but this is what your client was paying for


Go for it

rlb
Reply With Quote
  #3  
Old 1/10/07, 9:28 AM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Why amp meters

Quote:
Originally Posted by rbennett
Charley

This is what it is all about

I know that many will be upset that you used a clamp on amp meter but this is what your client was paying for


Go for it

rlb
Let them be upset an amp meter is a normal process for me. There is no way to determine if a electric furnace or a hot water heater is performing as intended with out an amp meter and if (THEY) are not using one I call this a short change for the customer.
Reply With Quote
  #4  
Old 1/10/07, 9:35 AM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Why amp meters

I wonder how many have you done and found nothing .
Now if you balance out all the time you spent finding nothing wrong with the electric element .
It would be interesting to see how many elements you could have bought with this time spent.
I do not take my clamp on with me as I feel this is an electricians job the same as I do not check how many inches of water the gas pressure is.
Not My job.
My openion others may disagree.

Roy Cooke
Reply With Quote
  #5  
Old 1/10/07, 9:47 AM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Why amp meters

Quote:
Originally Posted by rcooke
I wonder how many have you done and found nothing .
Now if you balance out all the time you spent finding nothing wrong with the electric element .
It would be interesting to see how many elements you could have bought with this time spent.
I do not take my clamp on with me as I feel this is an electricians job the same as I do not check how many inches of water the gas pressure is.
Not My job.
My openion others may disagree.

Roy Cooke
Roy; That is my job to find nothing the key word is FIND.

I am not into buying elements VS time
Reply With Quote
  #6  
Old 1/10/07, 10:16 AM
Mark A. Timpani's Avatar
Mark A. Timpani Mark A. Timpani is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 1,613
Default Re: Why amp meters

Could you please teach us on this proccess?....




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #7  
Old 1/10/07, 10:35 AM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Why amp meters

Quote:
Originally Posted by mtimpani
Could you please teach us on this proccess?....
Be more than happy to but have got to go on an inspect will be this evening.
Reply With Quote
  #8  
Old 1/10/07, 11:13 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,701
Default Re: Why amp meters

Roy,

If you look at it from another perspective, the Amp Meter will save time (and your *****).

You have to open the electrical panels anyway, you can stick the AMP Probe on a circuit and test the equipment from there.
For example, if you have electric heat, electric heat banks come on in sequence and are rated 3k, 5k, 7k, ect... the amp reading will show how many come on, if they come on.

If you have an electric heater around here in TN and dont find about 40 AMPS drawn with the heat running you have a problem.
This is a hell of a lot better than using a dry buld thermometer at the air side of the equipment! And much quicker.

BTU's = V * A * 3.415
1 BTU = 0.293 watts
1 kW = 3412 Btu/hr
Reply With Quote
  #9  
Old 1/10/07, 8:10 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Why amp meters

Quote:
Originally Posted by dandersen



You have to open the electrical panels anyway, you can stick the AMP Probe on a circuit and test the equipment from there.
For example, if you have electric heat, electric heat banks come on in sequence and are rated 3k, 5k, 7k, ect... the amp reading will show how many come on, if they come on.

If you have an electric heater around here in TN and dont find about 40 AMPS drawn with the heat running you have a problem.
This is a hell of a lot better than using a dry buld thermometer at the air side of the equipment! And much quicker.
David is absolutely right you can check the furnace amp draw at the main panel and get a good feel if the unit is drawing close to the proper amps.

I guess the old TECH just comes out in me I have to remove the control panel cover for the furnace because I have found to many wires that had burnt off or were about to burn off of elements and or sequencers so I have me a quick peek just normally two screws holding this panel.

I highly recommend you do not stick your wet Willy fingers into this area as you may end up looking like a piece of toast. The curiosity side of me wants to know how many elements are installed. I don't care what their KW is just the amount of elements. Your elements will be distinguished by perfect rows of wires attached to ceramic insulators on the front side with the elements not visible on the back side. (Nichrome wire that looks like a small cork screw) There will be two wires for each element most likely black on one side that travels Thur the sequencer and red on the other side that connects to the element Thur a Klixon heat sensitive switch. I place my amp meter on each element individually with the thermostat turned to its highest setting to ensure that the second stage of heating is being called for. You have sequencers that energize the elements in sequence so as not to place a heavy amp draw all at one time
The furnace I inspected this week had 3 elements and two sequencers the first sequencer controlled by the first stage heat from the thermostat had two stages bring on the first two elements one after the other. The second sequencer was a single sequencer controlled by the second stage heat from the thermostat. Boy that was a mouth full. The most common element to burn out is the first and or second element as these are used the most.

If I had checked the amp draw at the main electrical panel on this unit I would have missed the burnt out element as each of the two remaining elements were drawing 22 amps each at the elements. At the main panel I would have been indicating possibly 44 to 45 amps giving me false security that the furnace was performing as intended.

Guys with a little practice you can check the amp draw on a furnace in less than 5 minutes and it will make you shine like a diamond in a goats Butt. I can not tell you how many elements I have found in the last years as a HI that were bad but a bunch and I do not do that many electric furnaces

Electric Hot Water Heaters and AMP meters do I check every one absolutely not I have to have a reason to check the elements. 1.Not very hot water at the faucet. 2. Old heaters. 3. A pile of old elements lying near the water heater thats what rednecks do they never throw nothing away. The reason I checked the amp draw on this last find was the seller left a red flag he disclosed on the disclosure statement that the water heater was operating fine but, he the seller had removed the cover plates over the elements as if he had been checking the elements and failed to replace the covers. RED FLAG He probally used a redneck voltage tester and had 220 volts at the element and thought it was operating, That tells you nothing other than you are getting power to the element through the stat not if the element is operating. AMP METER thats what works.
Reply With Quote
  #10  
Old 1/10/07, 9:32 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: Why amp meters

Regarding the water heater full of cold water. Typically only one element in a water heater operates at a time. The top one runs as the primary element. When demand for hot water is met, the lower element takes over to finish heating the cold water at the bottom of the tank. Running a continuity test on the element with no load on it might show it to still be good. Make sure the power source is locked out.
Reply With Quote
  #11  
Old 1/10/07, 9:48 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,701
Default Re: Why amp meters

Quote:
Running a continuity test on the element with no load on it might show it to still be good.
yes, it may show it to be good even when it's bad!

Unless you know the actual resistance of the element, a burn element or water is leaking into the element may show impedance at any range which could be construed as a good element. Beware.
Reply With Quote
  #12  
Old 1/10/07, 9:50 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Why amp meters

Quote:
Originally Posted by dandersen
Roy,

If you look at it from another perspective, the Amp Meter will save time (and your *****).

You have to open the electrical panels anyway, you can stick the AMP Probe on a circuit and test the equipment from there.
For example, if you have electric heat, electric heat banks come on in sequence and are rated 3k, 5k, 7k, ect... the amp reading will show how many come on, if they come on.

If you have an electric heater around here in TN and dont find about 40 AMPS drawn with the heat running you have a problem.
This is a hell of a lot better than using a dry buld thermometer at the air side of the equipment! And much quicker.

BTU's = V * A * 3.415
1 BTU = 0.293 watts
1 kW = 3412 Btu/hr
And how many burned out elements have you found when doing a home inspection and how many electric furnaces have you done .
If you are not an electrical license you are not allowed to do that in Canada.
Thanks Roy Cooke
Reply With Quote
  #13  
Old 1/10/07, 9:56 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Why amp meters

Quote:
Originally Posted by rromoser
Regarding the water heater full of cold water. Typically only one element in a water heater operates at a time. The top one runs as the primary element. When demand for hot water is met, the lower element takes over to finish heating the cold water at the bottom of the tank. Running a continuity test on the element with no load on it might show it to still be good. Make sure the power source is locked out.
Randal you are correct but this tank had special circumstances and I knew the tank was full of cold water because I turned the water on to the home and activated the breakers to the water heater with permission from the owner and the listing Real Estate agent and my amp meter told me every thing I need to know the bottom element was not working regardless of the cause I was not troubleshooting If it has no amp draw it will not heat water.
Reply With Quote
  #14  
Old 1/10/07, 10:07 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Why amp meters

Quote:
Originally Posted by rcooke
And how many burned out elements have you found when doing a home inspection and how many electric furnaces have you done .
If you are not an electrical license you are not allowed to do that in Canada.
Thanks Roy Cooke
Roy I can not speak for David but my self I have found enough burnt out elements to justify my checking with an amp meter. I can also ask you the same question how many elements have you missed by not checking. What does that statement read at the bottom of your Posts

Come on Roy smile were are not all in Canada
</IMG></IMG>
Reply With Quote
  #15  
Old 1/11/07, 12:34 AM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,516
Default Re: Why amp meters

I do not disagree with any of the reasons you gave for troubleshooting the equipment but I shudder to think of some of the new untrained inspectors putting their "skinners" inside the electrical section and getting their YO-YO knocked into their watchpocket. I would venture to say the majority do not have a clue as to the proper way to use or read an amp meter or probe. If it isn't working, using normal operating controls, write it up for the professional. I had to fix my own furnace this morning but I know how but I would never dream of doing anything like that on an inspection. Ive been asked on occasion to override the thermostat with a jumper but refused. The dink that asked me to was the kind of SoB that would later come back and hit me for a new piece of equipment.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Moisture meters relliott Structural 35 8/3/07 6:57 AM
Noise from Meters?? mlong Electrical 9 2/3/07 9:08 PM
Carbon Monoxide and Moisture Meters jlapointe Canadian Inspectors 3 12/21/06 12:51 PM
Moisture Meters, What do you use? Lbisurfcaster Hardware, Software & Publications 7 2/22/06 6:59 PM
Watt Hour Meters jtedesco1 Electrical 0 2/5/06 12:08 PM


All times are GMT -4. The time now is 8:51 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts