I have a new duct heater and I want to make sure I am using the correct wire and breaker on the heater and the breaker panel. For some reason I can't post a photo, but the sticker says
Warren Electric heater with Integral Limit Control Model WGO1002B 240volt 1PH 1Step 60 HZ 39.6amps TAG: HKR-10C Any hell would be greatly appreciated. Dan |
| Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
With that amount of amperage it would require # 8 copper wire with a 50 amp double pole breaker. Being you are asking this question I would highly recommend having a qualified contractor install for you
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#3
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Using the above....... In Canada, if the #8 NMD wire is rated for 40 amps (Can. Code), the breaker may be rated at 50 amps (40 x 1.25) Or is the #8 rated at higher than 40 amps? |
|
#4
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Help. What is the correct way to report a breaker that is too big. | gromicko | Electrical Inspections | 77 | 5/10/12 6:13 PM |
| Size of wire at 60 AMP breaker | bhartley | Electrical Inspections | 8 | 1/12/09 6:13 PM |
| Square D HOM Breaker & Max Wire Size | pbennett1 | Electrical Inspections | 20 | 3/3/08 9:22 PM |
| Service wire size to breaker panel | sfalvey | Electrical Inspections | 12 | 10/31/06 4:28 PM |
| 30 amp breaker wire size | kweiss | Electrical Inspections | 18 | 10/10/06 9:53 PM |