#1
|
|||
|
|||
|
Can someone post their wording for what they say in their inspection reports when the temperatures are too low to test the AC system....The more the better.
|
| Need a home inspection in Kentucky? Check out InterNACHI's listing of Kentucky certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Due to low outdoor ambient temperatures, the AC unit was not tested in the cooling mode as this is outside the scope of this inspection. Operating cooling system equipment which has been "shut down" without proper preparation risks costly damage to the compressor or other components.
As the cooling equipment had clearly been shut down and because the weather temperature in the past 24 hours has been below 60 degrees fahrenheit I was not able to test-operate this equipment. Operating cooling system equipment which has been "shut down" without proper preparation risks costly damage to the compressor or other component Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#3
|
||||
|
||||
|
The A/C system(s) are not tested for proper operation when the outside air temperature is 65 degrees or less. Colder temps make it difficult to determine proper function and can potentially damage components of an air conditioner.
Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#4
|
||||
|
||||
|
Just put to damn cold only a idiot would run a AC at this ridiculous temp. And surely you didn't hire me because i was stupid. Just Kidding
I agree with above . Wayne Wilson East TN Home Inspections LLC Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-1490 http://site.myhomeinspection.net |
|
#5
|
||||
|
||||
|
It's too cold to run the air conditioner this time of year. Operating the equipment under these conditions could possibly damage the compressor.
If you must run the air conditioner in wintertime conditions, call David A. Andersen & Assoc. at 615-406-6808 and they will temporarily modify your equipment to run in the wintertime! Just kidding! Too busy for that type of thing ...
"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#6
|
|||
|
|||
|
Thanks for the replies...Are any of you making any recommendations in your phrasing? Inevitably I have clients who ask me what they should do to protect themselves since I can't test the AC system. Do you put in your report that you recommend a licensed HVAC company check the system or that they possibly obtain an extended warranty on the house?
|
|
#7
|
||||
|
||||
|
Greg, in most cases the HVAC contractors will not run the air-conditioners in the winter time either.
The ability to test requires installing a heater onto the compressor for a period of time to detach the refrigerant from the oil to prevent oil slugging when the compressor turns on. This oil slugging is what causes damage to reciprocal compressors. The next obstacle is to overcome the low outdoor ambient temperature. Head pressure controllers make the equipment think that it's hot outside. After all this is said and done, the analysis is limited to determine that the components actually functions but that capacity or refrigerant charge cannot be determined as there is an insufficient load on the equipment and differential pressures are obtained artificially. Extended warranties should be carefully examined as they do not cover "pre-existing conditions" that cannot be evaluated before the policy is put in place. Though this is a significant concern for all involved, the cost is generally prohibitive. If you buy a house in the winter time, it is difficult to impossible to know if the air conditioner will work in the spring. I was recruited as a home inspector by a real estate agent that was "sick and tired" of buying air-conditioners for her clients in the springtime when they purchased their homes in the wintertime. As I design and operate air conditioning and refrigeration equipment for operation in the state of Alaska, I was recruited because of a back injury that put me out of work. Seriously, I am not your competition in Nashville and if you would like to give me a call about this I would be more than happy to discuss this further. In actuality, I have many requests for inspections that I would be more than happy to forward to someone that knows their limitations on home inspection. For a minor consultant fee I will work you through some of these more complex issues over the telephone, as well as providing the referral. If you want to be the big dog in the Nashville community, you have got to use outside resources. I work with lawyers, architects and engineers of assorted flavors to address my clients issues. As the majority of my clients are associated with the music industry, they require more of my time than I can afford to give to someone that wants a basic Tennessee regulated home inspection. I have engineers and architects recruiting me. Therefore I find it necessary to recruit outside inspectors. I will not or cannot hire additional employees in this economic recession/depression. If I cannot perform to the client's expectations, I leave the money on the table. That is a loss to us all. "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#8
|
|||
|
|||
|
Get creative .................
We were unable to inspect the system due to the outside air temperature being below 60 degrees (operation in cool weather has the potential to damage the compressor). Nothing is known of the absence or presence of any deficiencies in the system, If this is a concern, you may ask the seller to: (a) warrant the unit for a 1 time start-up by a licensed and competent HVAC contractor in warmer weather; (b) escrow the cost of the AC unit until a licensed and competent HVAC contractor can service and check the unit in warmer weather; (c) have seller provide a comprehensive warranty covering the unit (including existing conditions); or (d) accept the unit as is. |
|
#9
|
||||
|
||||
|
11 years never a complaint .
I just put to cold to check AC . If I get questioned I state Outside temp should be abouve 65°F 24 hours to run the unit . I like KIss ,the more info I put down the more questions I get asked .. Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#10
|
|||
|
|||
|
Please Note:
clambert2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Where is the 65 °F cut off coming from? Please submit hard proof not just "I was told this , years ago"
Thanks. |
|
#11
|
||||
|
||||
|
Quote:
I would like to see that too. The temperature overnight in my service area can vary 10 degrees on the same night. I go by recent temps, present temp and other factors. Just checked one today with temp around 61. The performance was really poor too, so I found a valid problem for my client. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#12
|
||||
|
||||
|
Outside air temperature was below 60 degrees. Unable to test system at this time, Inquire with the home owner about the condition of the central air unit.
www.tristatehomeinspections.org www.tristateenergyinspections.com If you always do what you always did you will always get what you always got. |
|
#13
|
||||
|
||||
|
This picture is from Carson Dunlop home reference book page 243
Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
| Need a home inspection in Kentucky? Check out InterNACHI's listing of Kentucky certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Quote:
CARRIER -page 3 Do Not Operate Below 55 F Your outdoor unit is not designed to operate when outdoor temperatures are lower than 55_F without modification. If operation below this temperature is required, consult your Carrier dealer. ColdPoint -page2 CNC air conditioners are designed to provide comfort cooling at outside temperatures above 60 degrees. Operating the air conditioner below 60 degrees may cause unit failure and will void the Warranty. If you have need for cooling at lower outdoor temperatures a 'low ambient cooling' option is available. Contact your local contractor or call the factory. Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#15
|
||||
|
||||
|
Every Mfg. has some temp listed in their manuals.
When you run their equipment below their specs, you must add a low ambient kit. Hay, I thought that if it was posted here, it was the law of the land...? "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Allergy Testing in Coeur d’Alene, ID 83815 | rspriggs | Ancillary Inspection Services & Additional Topics | 3 | 10/12/09 2:39 AM |
| Water Testing in Coeur d’Alene, ID 83815 | rspriggs | Ancillary Inspection Services & Additional Topics | 0 | 1/9/09 3:17 AM |
| Moisture in slabs | mcyr | Structural Inspections | 7 | 8/20/07 7:33 PM |
| bbbb | mcyr | Structural Inspections | 1 | 8/19/07 10:26 PM |