Default When would a vent be required in a bathroom?

A home was built in the 1930's. There is visual updates in a 1st floor half bath including newer glass block window (no vent), newer sink, toilet, floor tile, etc. There is no ventilation except the HVAC duct at the floor and the door. I don't know when the work was done, but it obviously is not original.

After looking at many other "improvements" throughout the home, I suspect the work may have been done by the owner and possibly without permits but there is no way to know for sure without calling the local building inspection department (outside SOP). Any ideas?



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/5/11, 11:35 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: When would a vent be required in a bathroom?

I don't involve myself with permit issues.

I point out unprofessional work however.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 8/5/11, 11:45 AM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: When would a vent be required in a bathroom?

I don't either, and I have used the non-professional work in the past. Maybe something like, "Visual evidence of recent updates. No ventilation installed. This could be an indication of non-professional work. Recommend consulting with a licensed HVAC contractor to confirm the work performed meets professional standards". I would tend to flag this as a maintenance item and not a Defect. OR

[Exhaust - NONE - Defect]There is no means of ventilation present either through a window or mechanically ventilated fan. Repairs recommended by a licensed HVAC technician.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In

Last edited by gliebig; 8/5/11 at 11:47 AM.. Reason: Added defect
Reply With Quote
  #4  
Old 8/5/11, 11:56 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: When would a vent be required in a bathroom?

You can undercut doors to provide adequate return air.

http://www.baihp.org/casestud/return_air/index.htm



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #5  
Old 8/5/11, 12:03 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: When would a vent be required in a bathroom?

Not concerned with return air. Concerned that there was no window opening or mechanical means of ventilation installed in the bathroom.

Every bathroom requires an openable window that provides at least 1.5 square ft of air flow area when open – 2006 IRC [303.3] OR mechanical type ventilation: 50 CFM intermittent or 20 CFM continuous operation – 2006 IRC [303.3X]



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #6  
Old 8/5/11, 12:08 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: When would a vent be required in a bathroom?

Quote:
Originally Posted by gliebig View Post
Not concerned with return air. Concerned that there was no window opening or mechanical means of ventilation installed in the bathroom.

Every bathroom requires an openable window that provides at least 1.5 square ft of air flow area when open – 2006 IRC [303.3] OR mechanical type ventilation: 50 CFM intermittent or 20 CFM continuous operation – 2006 IRC [303.3X]
I missed your point. Sorry. I thought you were talking about a heating vent.

No ventilation always get written up by me.

Quote:
Recommend addition of a exhaust vent to remove moisture and objectionable odors from bathroom.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #7  
Old 8/5/11, 12:32 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: When would a vent be required in a bathroom?

Don't forget that what you are talking about is minimum. 50 cfm is safe for operation during occupancy and as Michael said, the door should be cut to provide proper ventilation.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #8  
Old 8/5/11, 12:37 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: When would a vent be required in a bathroom?

Quote:
Originally Posted by kwood View Post
Don't forget that what you are talking about is minimum. 50 cfm is safe for operation during occupancy and as Michael said, the door should be cut to provide proper ventilation.
The undercut door is for the HVAC not room ventilation.

I misread Greg's intent.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #9  
Old 8/5/11, 1:03 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: When would a vent be required in a bathroom?

What goes out must come in.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #10  
Old 8/5/11, 1:04 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: When would a vent be required in a bathroom?

Quote:
Originally Posted by kwood View Post
What goes out must come in.
Please read Kevin.

You're confused.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #11  
Old 8/5/11, 1:25 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: When would a vent be required in a bathroom?

Don't forget that what you are talking about is minimum. 50 cfm is safe for operation during occupancy and the door should be under cut to provide proper ventilation unless the area around the door is not well sealed.

Is that better Michael



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #12  
Old 8/5/11, 1:35 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: When would a vent be required in a bathroom?

Quote:
Originally Posted by gliebig View Post
Any ideas?
With or without windows (since very few will shower on a cold February night with an open window in the same room), all bathrooms need a means to send the moisture that is generated within them to the outdoors. It doesn't matter what a code book says or when they were built. The lack of a vent is a material defect and should be addressed in an inspection report.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #13  
Old 8/5/11, 1:35 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: When would a vent be required in a bathroom?

Quote:
Originally Posted by kwood View Post
Don't forget that what you are talking about is minimum. 50 cfm is safe for operation during occupancy and the door should be under cut to provide proper ventilation unless the area around the door is not well sealed.

Is that better Michael
NO

He is asking about the lack of ventilation for the bathroom, not the heat source.

I misread his intent at first too but I explained that already. Read son.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 8/5/11, 1:51 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: When would a vent be required in a bathroom?

Re: When would a vent be required in a bathroom?

As soon as I leave the room...

That should clear it up.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #15  
Old 8/5/11, 2:09 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: When would a vent be required in a bathroom?

No one is talking about supply heat. We are talking about moisture removal through ventilation.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
The Importance of Bathroom and Kitchen Fans mkyriacou Interior Inspections 35 6/4/10 5:27 PM
Bathroom vent piping to "Near Exterior"? swaskewicz Inspecting HVAC Systems 26 6/4/10 4:35 PM
Bathroom vent to Stack vent sfalvey Plumbing Inspections 7 8/15/07 9:59 PM
Soot around the bathroom vent lclark Exterior Inspections 7 3/6/06 8:13 AM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues for Inspectors 0 2/14/06 3:38 AM


All times are GMT -4. The time now is 12:34 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts