Default What would you say?

Inspected an 80 year old house yesterday with Dual Carrier HE furnaces (2006). The intake and exhaust go to the exterior directly below a window. Is there any problem with HE that would make this improper? The photo shows the bottom of the window, just above the pipes.
Attached Thumbnails
would-you-say-p1010412.jpg  



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.

Last edited by mnahrgang; 11/30/08 at 4:07 PM..
Reply With Quote
  #2  
Old 11/30/08, 4:24 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What would you say?

On way out ,I want to say a cat four exhaust needs to be 18 inches from.
Hope thats right.
Reply With Quote
  #3  
Old 11/30/08, 5:27 PM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,194
Send a message via Yahoo to bboerner
Default Re: What would you say?

IMO yes there is a problem. The install manuals should tell you distance requirements. I would refer to the manual first by finding it online. However, keep in mind these vents are pushing out carbon monixide. It is common to vent outside the walls however I recommend going to the roof. Nevertheless venting right under a window is plain stupid to me especially on a drafty older home.



Bill Boerner
STL Home Inspection Services
Serving St. Louis/Surrounding
(314) 805-2137
billy.boerner@gmail.com
http://www.stlhomeinspector.com


Reply With Quote
  #4  
Old 11/30/08, 5:41 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: What would you say?

Looks OK to me. Forced or induced vent requires a one foot clearance from windows. However, this might be overridden by the manufacturer's installation instructions.
Reply With Quote
  #5  
Old 11/30/08, 6:01 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: What would you say?

Quote:
Originally Posted by dvalley View Post
Looks OK to me. Forced or induced vent requires a one foot clearance from windows. However, this might be overridden by the manufacturer's installation instructions.
Thanks, unfortunately the only manual I can find on-line is the owners manual, and it doesn't address clearances. Apparently the only people to get the installation manuals are the installers. If anyone has a link or a resource I would sure appreciate it.

BTW, it's a Carrier Infinity 96 Model#58MVB100-20



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #6  
Old 11/30/08, 6:09 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What would you say?

Is that an operable window? With the sill so low, and apparently large, could that be a fixed window?
Reply With Quote
  #7  
Old 11/30/08, 6:15 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: What would you say?

Here's another photo of the window. The vents are behind and to the right of the AC units. Directly beneath the double window to the right. BTW, didn't measure it, but they are probably about 18 inches from the bottom of the window.
Attached Thumbnails
would-you-say-p1010403.jpg  



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #8  
Old 11/30/08, 6:18 PM
Gerry Pallotta's Avatar
Gerry Pallotta Gerry Pallotta is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Mississauga, ON
Posts: 1,122
Send a message via Yahoo to gpallotta
Default Re: What would you say?

I would recommend they keep a CO detector in that room.
Reply With Quote
  #9  
Old 11/30/08, 6:46 PM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,194
Send a message via Yahoo to bboerner
Default Re: What would you say?

Mark let the experts tell you. Post this over on hvac-talk.com! Great MB.



Bill Boerner
STL Home Inspection Services
Serving St. Louis/Surrounding
(314) 805-2137
billy.boerner@gmail.com
http://www.stlhomeinspector.com


Reply With Quote
  #10  
Old 12/1/08, 3:39 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: What would you say?

I questioned a similar setup last Spring. I don't remember the brand, but while I continued with my inspection, my Client went to his computer, found the instructions online, and showed me that everything was okay. I love it when Clients work with me on this stuff -- LOL. With HE, though, check those manufacturer installation instructions. Get an HVAC company or two as Power Partners.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #11  
Old 12/1/08, 9:13 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: What would you say?

I did go online, but the installation instructions weren't available, only the owners manual. Apparently Carrier reserves the installation instructions for installers.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #12  
Old 12/1/08, 11:26 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: What would you say?

Quote:
Originally Posted by mnahrgang View Post
Inspected an 80 year old house yesterday with Dual Carrier HE furnaces (2006). The intake and exhaust go to the exterior directly below a window. Is there any problem with HE that would make this improper? The photo shows the bottom of the window, just above the pipes.
Do you have a model name or a model number? I might have a Carrier resource if you have either one of those.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #13  
Old 12/1/08, 11:35 AM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,194
Send a message via Yahoo to bboerner
Default Re: What would you say?

Quote:
Originally Posted by rray View Post
Do you have a model name or a model number? I might have a Carrier resource if you have either one of those.
Carrier Infinity 96 Model#58MVB100-20

He posted it up top.



Bill Boerner
STL Home Inspection Services
Serving St. Louis/Surrounding
(314) 805-2137
billy.boerner@gmail.com
http://www.stlhomeinspector.com


Reply With Quote
  #14  
Old 12/1/08, 12:09 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: What would you say?

Let's put this to bed.

Below is the diagram I use when this issue comes up.
It's from a Goodman 95% series install guide.

Some important terms:

Direct vent - all combustion air is supplied from out side the building envelope(i.e. 2 pipes to the exterior)

Non Direct vent - Combustion air is taken from within the building envelope (1 pipe system to the exterior)

Note for Canadians:

In Canada, venting must conform to the requirements of the current
CAN/CSA-B149 Installation Code. Use only CSA listed two or three
inch diameter PVC or ABS pipe, solvent cement, and fittings throughout.
Carefully follow the pipe manufacturers’ instructions for cutting,
cleaning, and solvent cementing PVC and/or ABS.
The vent can be run through an existing unused chimney provided
the space between the vent pipe and the chimney is insulated and
closed with a weather-tight, corrosion-resistant flashing.
Attached Thumbnails
would-you-say-he-vent-termination.jpg  



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #15  
Old 12/1/08, 12:36 PM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,194
Send a message via Yahoo to bboerner
Default Re: What would you say?

Quote:
Originally Posted by mlarson View Post
Let's put this to bed.

Below is the diagram I use when this issue comes up.
It's from a Goodman 95% series install guide.

Some important terms:

Direct vent - all combustion air is supplied from out side the building envelope(i.e. 2 pipes to the exterior)

Non Direct vent - Combustion air is taken from within the building envelope (1 pipe system to the exterior)

Note for Canadians:

In Canada, venting must conform to the requirements of the current
CAN/CSA-B149 Installation Code. Use only CSA listed two or three
inch diameter PVC or ABS pipe, solvent cement, and fittings throughout.
Carefully follow the pipe manufacturers’ instructions for cutting,
cleaning, and solvent cementing PVC and/or ABS.
The vent can be run through an existing unused chimney provided
the space between the vent pipe and the chimney is insulated and
closed with a weather-tight, corrosion-resistant flashing.
There you go Mark. Diagram shows it all. However with the house being 80 yrs old you can be rest assured it's not air tight and I would HIGHLY recommend a CO detector be installed in that room.



Bill Boerner
STL Home Inspection Services
Serving St. Louis/Surrounding
(314) 805-2137
billy.boerner@gmail.com
http://www.stlhomeinspector.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On