Inspected an 80 year old house yesterday with Dual Carrier HE furnaces (2006). The intake and exhaust go to the exterior directly below a window. Is there any problem with HE that would make this improper? The photo shows the bottom of the window, just above the pipes.
Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. Last edited by mnahrgang; 11/30/08 at 4:07 PM.. |
|
#2
|
||||
|
||||
|
Please Note:
relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
On way out ,I want to say a cat four exhaust needs to be 18 inches from.
Hope thats right. |
|
#3
|
||||
|
||||
|
IMO yes there is a problem. The install manuals should tell you distance requirements. I would refer to the manual first by finding it online. However, keep in mind these vents are pushing out carbon monixide. It is common to vent outside the walls however I recommend going to the roof. Nevertheless venting right under a window is plain stupid to me especially on a drafty older home.
Bill Boerner STL Home Inspection ServicesServing St. Louis/Surrounding (314) 805-2137 billy.boerner@gmail.com http://www.stlhomeinspector.com |
|
#4
|
||||
|
||||
|
Looks OK to me. Forced or induced vent requires a one foot clearance from windows. However, this might be overridden by the manufacturer's installation instructions.
|
|
#5
|
||||
|
||||
|
Quote:
BTW, it's a Carrier Infinity 96 Model#58MVB100-20 Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#6
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Is that an operable window? With the sill so low, and apparently large, could that be a fixed window?
|
|
#7
|
||||
|
||||
|
Here's another photo of the window. The vents are behind and to the right of the AC units. Directly beneath the double window to the right. BTW, didn't measure it, but they are probably about 18 inches from the bottom of the window.
Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#8
|
||||
|
||||
|
I would recommend they keep a CO detector in that room.
Gerry Pallotta Alota Home Inspection Services www.alotahomeinspect.ca Greater Toronto Area Home Inspector Mississauga Home Inspector |
|
#9
|
||||
|
||||
|
Mark let the experts tell you. Post this over on hvac-talk.com! Great MB.
Bill Boerner STL Home Inspection ServicesServing St. Louis/Surrounding (314) 805-2137 billy.boerner@gmail.com http://www.stlhomeinspector.com |
|
#10
|
||||
|
||||
|
I questioned a similar setup last Spring. I don't remember the brand, but while I continued with my inspection, my Client went to his computer, found the instructions online, and showed me that everything was okay. I love it when Clients work with me on this stuff -- LOL. With HE, though, check those manufacturer installation instructions. Get an HVAC company or two as Power Partners.
NACHI 2005 U.S. Member of the Year
|
|
#11
|
||||
|
||||
|
I did go online, but the installation instructions weren't available, only the owners manual. Apparently Carrier reserves the installation instructions for installers.
Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#12
|
||||
|
||||
|
Quote:
NACHI 2005 U.S. Member of the Year
|
|
#13
|
||||
|
||||
|
Quote:
He posted it up top. Bill Boerner STL Home Inspection ServicesServing St. Louis/Surrounding (314) 805-2137 billy.boerner@gmail.com http://www.stlhomeinspector.com |
|
#14
|
||||
|
||||
|
Let's put this to bed.
Below is the diagram I use when this issue comes up. It's from a Goodman 95% series install guide. Some important terms: Direct vent - all combustion air is supplied from out side the building envelope(i.e. 2 pipes to the exterior) Non Direct vent - Combustion air is taken from within the building envelope (1 pipe system to the exterior) Note for Canadians: In Canada, venting must conform to the requirements of the current CAN/CSA-B149 Installation Code. Use only CSA listed two or three inch diameter PVC or ABS pipe, solvent cement, and fittings throughout. Carefully follow the pipe manufacturers instructions for cutting, cleaning, and solvent cementing PVC and/or ABS. The vent can be run through an existing unused chimney provided the space between the vent pipe and the chimney is insulated and closed with a weather-tight, corrosion-resistant flashing. He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father |
|
#15
|
||||
|
||||
|
Quote:
Bill Boerner STL Home Inspection ServicesServing St. Louis/Surrounding (314) 805-2137 billy.boerner@gmail.com http://www.stlhomeinspector.com |
![]() |