Default What would you say about this vent placement?

Besides needing a 90 on the air intake is there anything else wrong here ?

would-you-say-vent-placement-fast-picture.jpg
Reply With Quote
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/27/11, 12:49 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: What would you say about this vent placement?

For where you live, the furnace intake is too close to the exhaust. You may get a snowball in the intake and shut things down (when they are needed the most, very cold weather).

Needs a 90 and an extension.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #3  
Old 5/27/11, 12:52 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: What would you say about this vent placement?

Quote:
Originally Posted by dandersen View Post
For where you live, the furnace intake is too close to the exhaust. You may get a snowball in the intake and shut things down (when they are needed the most, very cold weather).

Needs a 90 and an extension.
What is min you have?
I am getting 6" so is that correct?

No issue with the bath exhaust? Just looks strange to me never see that many jammed together of one unit.
Reply With Quote
  #4  
Old 5/27/11, 12:55 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: What would you say about this vent placement?

Depends on orientation. Get below the rising exhaust and you should be fine.

I see nothing wrong with the bath vent unless it sucks in when "off". Negative building pressure from HVAC leaks to the exterior, dryer, mech vents etc.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #5  
Old 5/27/11, 12:58 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: What would you say about this vent placement?

Quote:
Originally Posted by dandersen View Post
Depends on orientation. Get below the rising exhaust and you should be fine.

I see nothing wrong with the bath vent unless it sucks in when "off". Negative building pressure from HVAC leaks to the exterior, dryer, mech vents etc.
Guess the double whammy of HWH and Furnace bothers me the most .OK thanks.

Forgot to mention lack of pest screen.
Reply With Quote
  #6  
Old 5/27/11, 3:52 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What would you say about this vent placement?

Quote:
Originally Posted by belliott View Post
Besides needing a 90 on the air intake is there anything else wrong here ?

Attachment 45045
Why would you need a 90 deg on the combustion air intake? I can see needing a downward extension on it to prevent crossflow/intake from the exhaust.......... or having a 90 + short horizontal extension on the exhausts to blow exhaust gases away from the intake.

Here's a home made video of a Lennox direct vent system. I inspected a house with this system on Tuesday.

http://www.youtube.com/watch?v=Sxeo5...eature=related


Also:

http://www.docs.hvacpartners.com/idc...t/OM58-129.pdf
Reply With Quote
  #7  
Old 5/27/11, 4:02 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: What would you say about this vent placement?

Have a PDF that makes it required, will check links.
Reply With Quote
  #8  
Old 5/27/11, 4:19 PM
John E. Mullarkey John E. Mullarkey is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: Sarasota, Fl
Posts: 349
Default Re: What would you say about this vent placement?

Nice to see you posting again Dave.
Reply With Quote
  #9  
Old 5/27/11, 6:18 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: What would you say about this vent placement?

Quote:
Originally Posted by Brian A. MacNeish View Post
Why would you need a 90 deg on the combustion air intake? I can see needing a downward extension on it to prevent crossflow/intake from the exhaust.......... or having a 90 + short horizontal extension on the exhausts to blow exhaust gases away from the intake.

Here's a home made video of a Lennox direct vent system. I inspected a house with this system on Tuesday.

http://www.youtube.com/watch?v=Sxeo5...eature=related


Also:

http://www.docs.hvacpartners.com/idc...t/OM58-129.pdf
I checked the PDF out and it lacks detail.
Here is part of mine from Nordyne (sorry no link)

4. Insure the combustion air inlet pipe (for a 2
pipe installation) has a 90 degree termination
elbow as shown in Figures 21 and 22.
Figure 21. Alternate Horizontal
Vent Installation
Note: A combustion air intake must be provided
with an elbow opening downward. The screen
provided with the furnace must be installed in the
elbow to prevent entry of debris or creatures.
When the vent pipe must exit an exterior wall
close to the grade or expected snow level, a riser
should be provided as shown in Figure 20.
Table 6 describes the maximum length of fl ue pipe
that can travel through an unconditioned space
or an exterior space. The total vent length must
not exceed the lengths noted on Table 5.
Vertical Venting
Figure 23 shows the proper installation and
clearances for vertical vent termination. The
roof penetration must be properly fl ashed and
waterproofed with a plumbing roof boot or equivalent
fl ashing. Termination spacing requirements
from the roof and from each other must be per
Figure 23.
would-you-say-vent-placement-2011-05-27_171405.jpg
Reply With Quote
  #10  
Old 5/27/11, 6:24 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: What would you say about this vent placement?

If I read your diagram correctly Bob, your vents should be seperated by min. 18 inches o.c.
Reply With Quote
  #11  
Old 5/27/11, 6:45 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: What would you say about this vent placement?

Quote:
Originally Posted by jjonas View Post
If I read your diagram correctly Bob, your vents should be seperated by min. 18 inches o.c.
Good (thank you) glad you saw that because I am confused here.
I have another that seems to state 6 inches in the same PDF.

[ATTACH]would-you-say-vent-placement-vent-clearance-part-2.jpg[/ATTACH]

Does anyone have something more definitive or different on minimum gap between intake and exhaust on cat 4 units?
Am I reading this wrong?

Also 18 inches makes more sense because it sucks fumes back in but remember they also use concentric vents (right).
Attached Thumbnails
would-you-say-vent-placement-vent-clearance-illustration-part-1.jpg  

Last edited by belliott; 5/27/11 at 6:48 PM..
Reply With Quote
  #12  
Old 6/2/11, 1:02 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: What would you say about this vent placement?

Quote:
Originally Posted by Brian A. MacNeish View Post
Why would you need a 90 deg on the combustion air intake?
One reason is you dont want (wind driven) rain to get inside the furnace intake.

There are usually provisions for draining moisture/condensate on the exhaust, but not on the intake



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #13  
Old 6/2/11, 1:18 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: What would you say about this vent placement?

Quote:
Originally Posted by roconnor View Post
One reason is you dont want (wind driven) rain to get inside the furnace intake.

There are usually provisions for draining moisture/condensate on the exhaust, but not on the intake
Very true and a good point.
Reply With Quote
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 6/2/11, 2:24 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: What would you say about this vent placement?

Quote:
Originally Posted by belliott View Post
I have another that seems to state 6 inches in the same PDF ... Does anyone have something more definitive or different on minimum gap between intake and exhaust ...
That table/diagram indicates clearances to elements other than the furnace intake. So its 6" clear to the combustion air intake of any other appliance at 10,000 BTU or less (and 12" for > 50,000 BTU)

Typical spacing between the intake and exhaust pipes for the same furnace (90%+) are usually between 3" (e.g. Goodman) and 9" (e.g Trane) ... your mileage might vary ...

The diagram you posted earlier showing the wall termination was the correct one to get the spacing between the intake and exhaust of that furnace ... BUT it looks like an older version of the Nordyne instructions that has a typo (or they changed it). It probably should read "8 to 36" spacing of the Nordyne furnace intake and exhaust per their current (90%+) furnace installation instructions.

Way beyond an inspection to get into the Mfr's install instructions, but you seemed confused by the mfr info (it can get sticky).

I would just look for some separation between the furnace intake/exhaust (could be very minimal depending on Mfr), and an elbow pointing down for the intake (more important in my mind).
Attached Thumbnails
would-you-say-vent-placement-nordyne-sc-sl-furnace-venting-termination-diagram.jpg  
Attached Files
File Type: pdf Nordyne SC-SL Furnace Venting Termination.pdf (43.5 KB, 63 views)



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 6/2/11 at 2:36 PM..
Reply With Quote
  #15  
Old 6/2/11, 2:40 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: What would you say about this vent placement?

I find it amazing that only inches is needed when the intake is like a vacuum.Must be me.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pellet stove help chellickson General Inspection Discussion 23 8/19/10 1:23 AM
B vent placement tyeager Inspecting HVAC Systems 1 3/1/10 1:32 AM
Air admittance valves everywhere apfaff Plumbing Inspections 13 4/16/07 9:17 AM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 5:22 PM