For where you live, the furnace intake is too close to the exhaust. You may get a snowball in the intake and shut things down (when they are needed the most, very cold weather).
Needs a 90 and an extension. "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#3
|
||||
|
||||
|
Quote:
I am getting 6" so is that correct? No issue with the bath exhaust? Just looks strange to me never see that many jammed together of one unit. |
|
#4
|
||||
|
||||
|
Depends on orientation. Get below the rising exhaust and you should be fine.
I see nothing wrong with the bath vent unless it sucks in when "off". Negative building pressure from HVAC leaks to the exterior, dryer, mech vents etc. "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#5
|
||||
|
||||
|
Quote:
Forgot to mention lack of pest screen. |
|
#6
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Here's a home made video of a Lennox direct vent system. I inspected a house with this system on Tuesday. http://www.youtube.com/watch?v=Sxeo5...eature=related Also: http://www.docs.hvacpartners.com/idc...t/OM58-129.pdf |
|
#7
|
||||
|
||||
|
Have a PDF that makes it required, will check links.
|
|
#8
|
|||
|
|||
|
Nice to see you posting again Dave.
|
|
#9
|
||||
|
||||
|
Quote:
Here is part of mine from Nordyne (sorry no link) 4. Insure the combustion air inlet pipe (for a 2 pipe installation) has a 90 degree termination elbow as shown in Figures 21 and 22. Figure 21. Alternate Horizontal Vent Installation Note: A combustion air intake must be provided with an elbow opening downward. The screen provided with the furnace must be installed in the elbow to prevent entry of debris or creatures. When the vent pipe must exit an exterior wall close to the grade or expected snow level, a riser should be provided as shown in Figure 20. Table 6 describes the maximum length of fl ue pipe that can travel through an unconditioned space or an exterior space. The total vent length must not exceed the lengths noted on Table 5. Vertical Venting Figure 23 shows the proper installation and clearances for vertical vent termination. The roof penetration must be properly fl ashed and waterproofed with a plumbing roof boot or equivalent fl ashing. Termination spacing requirements from the roof and from each other must be per Figure 23.
|
|
#10
|
||||
|
||||
|
If I read your diagram correctly Bob, your vents should be seperated by min. 18 inches o.c.
Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#11
|
||||
|
||||
|
Quote:
I have another that seems to state 6 inches in the same PDF. [ATTACH] [/ATTACH]Does anyone have something more definitive or different on minimum gap between intake and exhaust on cat 4 units? Am I reading this wrong? Also 18 inches makes more sense because it sucks fumes back in but remember they also use concentric vents (right). www.chicagopropertyinspection.com www.elliotthomeinspection.com www.chicagolandhomeinspection.com www.homeandcondoinspector.com www.homeandcondoinspection.com http://www.homeinspectorpro.com/ (Report Software) Bob Elliott http://www.chicagolandhomeinspector.com/ Last edited by belliott; 5/27/11 at 6:48 PM.. |
|
#12
|
||||
|
||||
|
Quote:
There are usually provisions for draining moisture/condensate on the exhaust, but not on the intake Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#13
|
||||
|
||||
|
Very true and a good point.
|
| Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Quote:
Typical spacing between the intake and exhaust pipes for the same furnace (90%+) are usually between 3" (e.g. Goodman) and 9" (e.g Trane) ... your mileage might vary ... The diagram you posted earlier showing the wall termination was the correct one to get the spacing between the intake and exhaust of that furnace ... BUT it looks like an older version of the Nordyne instructions that has a typo (or they changed it). It probably should read "8 to 36" spacing of the Nordyne furnace intake and exhaust per their current (90%+) furnace installation instructions. Way beyond an inspection to get into the Mfr's install instructions, but you seemed confused by the mfr info (it can get sticky). I would just look for some separation between the furnace intake/exhaust (could be very minimal depending on Mfr), and an elbow pointing down for the intake (more important in my mind). Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 6/2/11 at 2:36 PM.. |
|
#15
|
||||
|
||||
|
I find it amazing that only inches is needed when the intake is like a vacuum.Must be me.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Pellet stove help | chellickson | General Inspection Discussion | 23 | 8/19/10 1:23 AM |
| B vent placement | tyeager | Inspecting HVAC Systems | 1 | 3/1/10 1:32 AM |
| Air admittance valves everywhere | apfaff | Plumbing Inspections | 13 | 4/16/07 9:17 AM |
| Gas and oil hot water tank and Boiler Share Vents | hvanderbeek | Miscellaneous Discussion for Inspectors | 8 | 1/25/07 5:22 PM |