Default What is wrong with this picture

Condensate drain connecting into the bathroom drainage system located on the other side of the wall
Attached Thumbnails
wrong-picture-1400-michael-ln-pc-2-21-11-082.jpg   wrong-picture-1400-michael-ln-pc-2-21-11-087.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Need a home inspection in Texas? Check out InterNACHI's listing of Texas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/22/11, 5:21 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: What is wrong with this picture

That would be pretty smelly if there was a sewage backup.



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #3  
Old 2/22/11, 6:29 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: What is wrong with this picture

Quote:
Originally Posted by bwiley View Post
That would be pretty smelly if there was a sewage backup.
Not sure where it tied into exactly as it was between the two floors of a two story.

Where you been hiding Blaine been a long time



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 2/22/11, 6:36 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: What is wrong with this picture

Have they ever heard of support straps Charlie?
Was the leak at top front of the casing from the condensate line Charlie?

Also what is the vent in back for?
Sorry but I do not see a cutoff switch (at least no junction box for one)however I imagine there is one around there somewhere.
Reply With Quote
  #5  
Old 2/22/11, 7:04 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: What is wrong with this picture

Been workin, Charley, Which is a good thing!!

It's trapped, runs downward, so my guess would be that the condensate drain line is not allowed to terminate into the sewer lines. Municipalities don't like unmetered water running through their lines. It isn't allowed here for sure.

Or should it only terminate outside???



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #6  
Old 2/22/11, 7:48 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: What is wrong with this picture

Quote:
Originally Posted by belliott View Post
Have they ever heard of support straps Charlie?
Was the leak at top front of the casing from the condensate line Charlie?

Also what is the vent in back for?
Sorry but I do not see a cutoff switch (at least no junction box for one)however I imagine there is one around there somewhere.
Conduit clamped to the wall studs.
No the leak was condensate dripping from the uninsulated freon suction line where it enters the A-coil box.
The vent in back is a vertical dryer vent as the utility room was located below this area on the first level..
Sorry cut off switches are not required in this State.

So now Bob I answered all of your questions what about my question that you avoided about the condensate line is it correct what would you say about it in the windy city or am I going to have to get Linas after you.

Oh BTW there were many more issues in the pic that I put in my report that you did not mention don't be a slacker here get em all.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 2/22/11, 7:56 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: What is wrong with this picture

Quote:
Originally Posted by bwiley View Post
Been workin, Charley, Which is a good thing!!

It's trapped, runs downward, so my guess would be that the condensate drain line is not allowed to terminate into the sewer lines. Municipalities don't like unmetered water running through their lines. It isn't allowed here for sure.

Or should it only terminate outside???
The only time its allowed to terminate as in the pic is if it is a wet trap and the trap shown is only wet during the cooling season the furnace is not high efficiency no water.

Heard things were a little rough your way but its good your working. Good inspectors will always be working the not so good will just be complaining about the lack of work



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #8  
Old 2/22/11, 8:08 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: What is wrong with this picture

Hi Charlie
Busy on my own report ,but I did not see an air gap which I think was mentioned above so did not bother.
With time I would look up the flue turn to close.
No drain pan and I am sure could find others.
Reply With Quote
  #9  
Old 2/22/11, 8:12 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: What is wrong with this picture

Quote:
Originally Posted by cbottger View Post
The only time its allowed to terminate as in the pic is if it is a wet trap and the trap shown is only wet during the cooling season the furnace is not high efficiency no water.
Oh yeah, y'all have a heating season. We didn't till the last two winters. I haven't seen a gas furnace with an AC coil on top in so long I can't remember. Couple that with a bad case of CRAFT and you see where I'm coming from.

Heat pumps and A/C's please...



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #10  
Old 2/22/11, 9:04 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: What is wrong with this picture

Quote:
Originally Posted by cbottger View Post
The only time its allowed to terminate as in the pic is if it is a wet trap and the trap shown is only wet during the cooling season the furnace is not high efficiency no water.

Heard things were a little rough your way but its good your working. Good inspectors will always be working the not so good will just be complaining about the lack of work

Nice Charley...

Got any Water Softener brine drain pic's too???
Reply With Quote
  #11  
Old 2/22/11, 9:05 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: What is wrong with this picture

Quote:
Originally Posted by bwiley View Post
Oh yeah, y'all have a heating season. We didn't till the last two winters. I haven't seen a gas furnace with an AC coil on top in so long I can't remember. Couple that with a bad case of CRAFT and you see where I'm coming from.

Heat pumps and A/C's please...
I was in Orlando the middle of January and I sure could of used a gas furnace at the hotel was dam cold for Fla.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #12  
Old 2/22/11, 9:12 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: What is wrong with this picture

Quote:
Originally Posted by bkelly2 View Post
Nice Charley...

Got any Water Softener brine drain pic's too???
Not on the upper level, softener drain was within the garage closet with the water heater and the down stairs furnace. I suggested they re-route the drain from the upper level to the floor drain in the garage closet where the other condensate discharged. Should have been there in the first place
Attached Thumbnails
wrong-picture-1400-michael-ln-pc-2-21-11-041.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Picture with text software? bforeman Inspection Hardware, Software & Publications 5 2/16/09 12:24 PM
www.FireDoorInspector.org gromicko Commercial Inspections 108 1/12/09 2:39 PM


All times are GMT -4. The time now is 12:35 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts