Default Yesterday's inspection

yesterdays-inspection-cond-1.jpg

yesterdays-inspection-cond-2.jpg



Another homeowner "fixit"
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/25/11, 6:36 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Yesterday's inspection

What was that line connected to on both ends I'm guessing A-coil in the attic and no telling what the connection below was inquiring minds want to know



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #3  
Old 1/25/11, 6:54 PM
jhugenroth jhugenroth is offline
Active Poster
 
Join Date: May 2004
Location: Fresno, CA
Posts: 1,152
Please Note: jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Yesterday's inspection

Quote:
Originally Posted by cbottger View Post
What was that line connected to on both ends I'm guessing A-coil in the attic and no telling what the connection below was inquiring minds want to know
Newer houses around here have the furnace and A/C coil in the attic, and the upper drain line is for the overflow pan. The end of the drain should be visible, in case the main drain line gets blocked and the overflow pan gets the condensate.
Whoever did this, just tied the upper drain into the primary drain at the bottom.
Now if the main line gets blocked, there is no way to tell.
Reply With Quote
  #4  
Old 1/25/11, 7:30 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Yesterday's inspection

That was the purpose of my question is there a P-trap installed in the primary drain line and where is it located . The bottom line appears to be going into the concrete or the ground hard to tell from the pic. To What and where does the primary drain connect



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #5  
Old 1/25/11, 7:49 PM
jhugenroth jhugenroth is offline
Active Poster
 
Join Date: May 2004
Location: Fresno, CA
Posts: 1,152
Please Note: jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Yesterday's inspection

Quote:
Originally Posted by cbottger View Post
That was the purpose of my question is there a P-trap installed in the primary drain line and where is it located . The bottom line appears to be going into the concrete or the ground hard to tell from the pic. To What and where does the primary drain connect
P-trap is in the attic. But that wasn't the point of my post.

It was just to show homeowners are clueless when modifying things they know nothing about.
Reply With Quote
  #6  
Old 1/25/11, 11:09 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Yesterday's inspection

Quote:
Originally Posted by jhugenroth View Post
P-trap is in the attic. But that wasn't the point of my post.

It was just to show homeowners are clueless when modifying things they know nothing about.
I understand clueless I see it everyday just trying to understand what was not visible in the PIC



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 1/25/11, 11:37 PM
jhugenroth jhugenroth is offline
Active Poster
 
Join Date: May 2004
Location: Fresno, CA
Posts: 1,152
Please Note: jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Yesterday's inspection

Quote:
Originally Posted by cbottger View Post
I understand clueless I see it everyday just trying to understand what was not visible in the PIC
No problem. The main drain is the one on the right in the first pic, and the secondary was tied into it. So now, neither one is visible at the termination point. Nice, huh?
Reply With Quote
  #8  
Old 1/25/11, 11:54 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Yesterday's inspection

What has my curiosity up the most is where they both were connected into and you stated it was a heat pump so we only deal with condensate during the cooling season do you see where I am headed with this



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #9  
Old 1/26/11, 1:26 AM
jhugenroth jhugenroth is offline
Active Poster
 
Join Date: May 2004
Location: Fresno, CA
Posts: 1,152
Please Note: jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Yesterday's inspection

Ahh... you misunderstood my post. This is a split system, with condenser on the ground outside, and the gas furnace and A/C coil in the attic.

Heat pumps are rare around here, except for a few on rural properties

It is a high efficiency furnace (90%) so there would be condensate all year long.
Reply With Quote
  #10  
Old 1/26/11, 8:33 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Yesterday's inspection

Quote:
Originally Posted by jhugenroth View Post
Ahh... you misunderstood my post. This is a split system, with condenser on the ground outside, and the gas furnace and A/C coil in the attic.

Heat pumps are rare around here, except for a few on rural properties

It is a high efficiency furnace (90%) so there would be condensate all year long.
I have no idea where I came up heat pump I must have been dreaming you just destroyed my theory with condensate all year long Shucks



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #11  
Old 1/26/11, 12:10 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Yesterday's inspection

Quote:
Originally Posted by cbottger View Post
I have no idea where I came up heat pump I must have been dreaming you just destroyed my theory with condensate all year long Shucks
Ya know Charley, it's weird. I thought the same thing. Maybe it was from reading the other thread about heat pump condensate line in bathtub, just before this one.

http://www.nachi.org/forum/f20/heat-...bathtub-57453/
Reply With Quote
  #12  
Old 1/26/11, 12:12 PM
jhugenroth jhugenroth is offline
Active Poster
 
Join Date: May 2004
Location: Fresno, CA
Posts: 1,152
Please Note: jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Yesterday's inspection

Quote:
Originally Posted by cbottger View Post
I have no idea where I came up heat pump I must have been dreaming you just destroyed my theory with condensate all year long Shucks

Theories are made to be broken Charley.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Chicago provides never ending scenery (yesterdays) belliott Miscellaneous Discussion for Inspectors 10 3/27/09 5:15 PM
Yesterday's Inspection dduffy Miscellaneous Discussion for Inspectors 13 1/19/09 9:25 PM
Hot PIC of yesterday's training with Kenny Hart. gromicko Miscellaneous Discussion for Inspectors 0 2/16/07 4:45 PM