Default What are your thoughts on this

Found this in a home today....call me crazy but is half of the cabinet missing. I pointed this out to the buyer and she said that this is the way her unit was in her old house as well?
Attached Thumbnails
your-thoughts-heater1.jpg  
Reply With Quote
Find an InterNACHI certified Nevada Home Inspector (and anywhere else in North America)
  #2  
Old 3/17/09, 8:21 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: What are your thoughts on this

Was it a mobile home?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 3/17/09, 8:23 PM
acassady's Avatar
acassady acassady is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: Waynesville, MO
Posts: 117
Default Re: What are your thoughts on this

it was a mobile home
Reply With Quote
  #4  
Old 3/17/09, 8:34 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: What are your thoughts on this

I've seen that lots of times. The units are usually contained in a closet that serves as a cabinet in a way. I'll refrain from comment until a HVAC expert jumps in. I've always wondered about it.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 3/17/09, 9:32 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: What are your thoughts on this

No thoughts at all a piece of junk A/C are not designed to operate in that manner absolutely no efficiency. The coil has to be contained within its own box and air flow channeled across the fins poor people poor ways.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #6  
Old 3/17/09, 10:06 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: What are your thoughts on this

Quote:
Originally Posted by cbottger View Post
No thoughts at all a piece of junk A/C are not designed to operate in that manner absolutely no efficiency. The coil has to be contained within its own box and air flow channeled across the fins poor people poor ways.
Charley, if it's "not designed to operate in that manner", then why are they installed that way? They most certainly are designed that way. Not saying it's the best, but it is by design. The manufactured home meets HUD specifications.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 3/18/09, 7:55 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: What are your thoughts on this

Quote:
Originally Posted by jfunderburk View Post
Charley, if it's "not designed to operate in that manner", then why are they installed that way? They most certainly are designed that way. Not saying it's the best, but it is by design. The manufactured home meets HUD specifications.
Joe I don't think you can find any MFG installation instructions that would allow that type of open A-coil design and warranty the equipment. I get to thinking about this and I also found one about 3 years ago on a Double wide MFG home I wrote it up as improperly installed. I was not hired to do a re-inspect so I don't know what the outcome of my report was but I wrote it up anyway. Just another example of a short cut to save the MFG of these Modular homes a $100.00 by not using a coil box. There are lots of things that gets past HUD that should never be.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #8  
Old 3/18/09, 8:11 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: What are your thoughts on this

Quote:
Originally Posted by cbottger View Post
Joe I don't think you can find any MFG installation instructions that would allow that type of open A-coil design and warranty the equipment. I get to thinking about this and I also found one about 3 years ago on a Double wide MFG home I wrote it up as improperly installed. I was not hired to do a re-inspect so I don't know what the outcome of my report was but I wrote it up anyway. Just another example of a short cut to save the MFG of these Modular homes a $100.00 by not using a coil box. There are lots of things that gets past HUD that should never be.
Charlie
I thought the same thing , I called the maker of the unit and They said that is how they are put in that type of home. The use the closet as a duct
LOL it is a cheap way of doing thing i agree .
Of course they are magnets for twisters so maybe it is a good thing that there is less sharp metal flying around .
Reply With Quote
  #9  
Old 3/18/09, 6:38 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What are your thoughts on this

Quote:
Originally Posted by jfunderburk View Post
Charley, if it's "not designed to operate in that manner", then why are they installed that way? They most certainly are designed that way. Not saying it's the best, but it is by design. The manufactured home meets HUD specifications.

The same reason some companies will install a return on the back of the furnace when the installation manual says NO. Or they use 2 inch pvc pipe to vent a 120,000 btuhr high efficiency furnace when the manual only lists 3 inch for that btu rating. They got away with in the past and will continue to do so until they are called out on it.
Reply With Quote
  #10  
Old 3/19/09, 4:57 AM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: What are your thoughts on this

I've inspected only a few mobile homes in my time, but have never seen this setup before. I can't believe this installation would meet any Equip.Manuf's. specs..
By the way, what is the insulated flexduct designed to do in this picture?
Reply With Quote
  #11  
Old 3/19/09, 10:17 PM
acassady's Avatar
acassady acassady is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: Waynesville, MO
Posts: 117
Default Re: What are your thoughts on this

I am thinking of writing this up as: Although this is a common practice in the MFG Homes in this area it is not installed as the manufacturer intended recommend having a HVAC Professional evaluate.
Reply With Quote
  #12  
Old 3/19/09, 10:38 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: What are your thoughts on this

Quote:
Originally Posted by acassady View Post
I am thinking of writing this up as: Although this is a common practice in the MFG Homes in this area it is not installed as the manufacturer intended recommend having a HVAC Professional evaluate.
Do you know what the manufacturer intends? Do you have an installation manual from them when it comes to installation in a mfg. home? If you haven't already called them or a local HVAC rep. for that equipment, you should.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #13  
Old 3/20/09, 7:57 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: What are your thoughts on this

Anthony

I don't think I would do that.

I would state - The existing installation is inconsistant with any established design for this type of HVAC system I am aware of. I recommend a Prof. HVAC Contractor inspect and advise on any changes necessary for safe and reliable operation.

IMHO
Reply With Quote
Find an InterNACHI certified Nevada Home Inspector (and anywhere else in North America)
  #14  
Old 3/20/09, 9:31 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: What are your thoughts on this

Quote:
Originally Posted by gveal View Post
Anthony

I don't think I would do that.

I would state - The existing installation is inconsistant with any established design for this type of HVAC system I am aware of. I recommend a Prof. HVAC Contractor inspect and advise on any changes necessary for safe and reliable operation.

IMHO

Dat's veally gute.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #15  
Old 3/21/09, 10:34 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: What are your thoughts on this

I spoke with a competent licensed HVAC contractor about this yesterday and we discussed it. He said that's they way they come from the factory and HUD approves it. He said it's not the best installation, but there's nothing "wrong" with it.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Thoughts: Combustion Air Vent pdoane Inspecting HVAC Systems 1 9/26/08 1:41 PM


All times are GMT -4. The time now is 12:36 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts