Default Z flex pipe clearance?

HELP. I need to know the clearance for a Z flex vent on a Clare high boy direct vent oil furnace. OHB5 1998 s/n 182446 85.000 btu. When I inspected the furnace the unit had not been on for over half and hour and the outside temp of the vent pipe was 130.
I told my client it was to close to combustables and he called in the furnace installer and he said it was ok and that it passed inspection. Now my client wants me to pay for the Furnace Company Inspection. ( a few hundred bucks) He is also considering suing me for undue stress.
The vent was within 2 in. of the wood floor and floor joist and the plastic intake air vent was leaning against it. There was also a live wire laying on top of it. All the A/C lines were within one inch. Tks Tim
Reply With Quote
Find an InterNACHI certified Louisiana Home Inspector (and anywhere else in North America)
  #2  
Old 3/31/09, 10:13 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Z flex pipe clearance?

Tim,

I'm having a hard time visualizing your conditions. Hopefully you have pictures, if not, I recommend you go back to get some before having to go to court. Hopefully Court won't occur, but today, you just never know.
I rarely see "Oil systems" in my region, but clearances should still be the same as for NG or LPG, especially if the vent material is rated for Oil,NG,LPG usage.
I'll be interested to see what you and others find.
Reply With Quote
  #3  
Old 3/31/09, 11:07 PM
pabrioux pabrioux is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Peterborough, ON
Posts: 132
Default Re: Z flex pipe clearance?

Tim, you might find the info here: or at least a number to call.

http://www.novaflex.com/productcart/...y=468&idpage=4

Good luck.
Reply With Quote
  #4  
Old 3/31/09, 11:30 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Z flex pipe clearance?

Cat. III Z-flex requires 1" clearance minimum.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 4/1/09, 12:10 AM
Timothy M. Cole Timothy M. Cole is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: picton, on
Posts: 22
Default Re: Z flex pipe clearance?

z-flex-pipe-clearance-hykes-pt-346-024.jpg

z-flex-pipe-clearance-hykes-pt-346-025.jpg

z-flex-pipe-clearance-hykes-pt-346-026.jpg

z-flex-pipe-clearance-hykes-pt-346-027.jpg

z-flex-pipe-clearance-hykes-pt-346-028.jpg
Here are my pictures. Hope they come through.
Reply With Quote
  #6  
Old 4/1/09, 6:35 AM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Z flex pipe clearance?

Tim

Looks to me like your pictures are indicating a clearance problem.

I'd call a local inspection official, and discuss what you saw, seeking his/her advice. You can't bring them in at this point to inspect, but at least you're on record as to investigating your position/advice you gave to your previous client. If something does come up, you might have witness' you can call.

By the way, I don't think I would pay the HVAC Contr. inspection fee. As for your previous clients "undue stress"....give me a break.
Reply With Quote
  #7  
Old 4/2/09, 9:45 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Z flex pipe clearance?

Let me get this right. The client called back the guy that installed it wrong in the first place, who claims it is right, and that is passed some sort of "inspection". Now he wants you to pay for that?

I think I would say, that's a difference of opinion, and when there are additional problems in the future (like a fire) be sure to call that installer back to fix it.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #8  
Old 4/2/09, 4:26 PM
Matt Berman Matt Berman is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Mt. Clemens, MI
Posts: 107
Default Re: Z flex pipe clearance?

Tim, what does the manufacturers instructions read, they should be near or at the furnace.
Reply With Quote
  #9  
Old 4/2/09, 4:29 PM
Terry Clayton Terry Clayton is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Arnold, MO
Posts: 244
Default Re: Z flex pipe clearance?

Tim I am not up on Z-Flex but I was wondering if there is some sort of duct connecting devise under the foil tape, it looks like 2 ends butted together to me. I am just asking for my eyes sake, thank you
Reply With Quote
  #10  
Old 4/2/09, 4:53 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Z flex pipe clearance?

Can Tim tell us what is going on in this pick?

I'm not seeing something right because I see:
straw at the bottom,
more than one size of Z flex taped together with shiny tape
and a PVC line into a Z FLEX T.

Are my eyes failing me?

It just is doesn't look right.

HELP!

[/IMG][/IMG]



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #11  
Old 4/2/09, 7:09 PM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is online now
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 951
Default Re: Z flex pipe clearance?

Was the guy who installed it the same guy who inspected it?



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #12  
Old 4/3/09, 1:02 PM
Timothy M. Cole Timothy M. Cole is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: picton, on
Posts: 22
Default Re: Z flex pipe clearance?

Thank you for your interest. The bottom of the picture is the pipe going out the side of the building. There was a live romex wire laying on the top of the flu during inspection. The a/c lines are approx. one inch away as well. It looks as if the flu has been cut and taped togther,,,using 2 old pieces instead of one complete new one--to save money is my guess. I am sure that is not allowed. How would they connect it inside and also it should be a proper sleeve connection. I think the straw is an old plant or flower arrangement. ????? Also the pvc is touching the flu at one point near the furnace. any comments would be welcome
Reply With Quote
  #13  
Old 4/4/09, 3:53 PM
gkay gkay is offline
New User
 
Join Date: Jan 2009
Location: Olkanagan Valley British Columbiia Canada eh
Posts: 50
Please Note: gkay is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Z flex pipe clearance?

Its hard to see the whole picture in your pictures. Direct vent appliances have unique venting. This link may explain what we can't see.

http://yaunco.com/ycreport/july99noframe/clare.html
Optional DC2000 Direct Venting:
· Stainless steel terminal uses integrated exhaust and outside combustion air format (patent pending).
· Vent or intake blockage safety shutdown design (patent pending).
· Vent lengths up to 30'.
· Zero clearance vent system incorporates stainless steel core and flexible aluminum outer shell separated by 5/8" high temperature fibreglass insulation.
· Rated for wind conditions in excess of 60mph.
· Combustion air piping (field provided) approved for schedule 40; PVC DWV, ABS DWV and ASTMD2729.
Reply With Quote
Find an InterNACHI certified Louisiana Home Inspector (and anywhere else in North America)
  #14  
Old 4/9/09, 10:19 AM
Charles Jones Charles Jones is offline
New User
 
Join Date: Jul 2007
Location: new jersey
Posts: 24
Please Note: Charles Jones is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Z flex pipe clearance?

http://www.novaflex.com/information_centre/zflex/01Z-Vent%20Residential/Z-Vent_Residential_Installation_Guide.pdf this explains in an enclosed space 8" and in and open space 1"
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you put polybutylene in the Summary? jfunderburk Plumbing Inspections 36 10/27/10 11:21 AM
Pellet stove help chellickson General Inspection Discussion 23 8/19/10 2:23 AM
Help - Polybutylene Pipes Rick G Plumbing Inspections 39 2/12/09 9:16 AM
Identify ABS defective pipe mcyr Plumbing Inspections 6 1/29/09 7:39 PM
gas pipe clearance to flue? ahinz Inspecting HVAC Systems 3 5/7/08 7:11 PM


All times are GMT -4. The time now is 11:27 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts