Default Zone System Temp Differentials

One of the Inspect points that we use for heat pumps and air conditioning systems is to measure the differential temperature between the supply and return air in the system and typically if we see 14-20 degrees we consider the unit working OK if the other points are also OK.
We had a home yesterday with two levels and one system serving two zones in the home. The differential was only 8 degrees and the builder asked if we had run both zones at the same time. I said we had and his comment was that that was normal to see a lower differential with both zones operating.
Anyone had experience with this and is there a differential temp we could use in this situation? Should an effort be made to shut one zone off and take measurements then?
Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/17/10, 10:41 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Zone System Temp Differentials

I don't buy it, but I don't know everything...

8 degrees differential, says something isn't right. It could be the units are running just fine, but something else is up and needs to be addressed. (or in all fairness, it could be the builder is right.)

My recommendation to my client would be to have their own HVAC expert come in to evaluate the system independent of what the builder says, and go with their recommendation. It may cost a few dollars, but if something is wrong, now is the time to get it addressed.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #3  
Old 8/17/10, 6:30 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Zone System Temp Differentials

Calling David A... calling David A... Please report to the HVAC thread

Curious, was the system equipped with a barometric bypass damper? That will definitely affect the split when only one zone is running.

The system should be sized to adequately cool the whole house, but you can't go by Delta T alone. So how did the system do at cooling the house? How was the temp of the suction line at the condenser? I'm sure it wasn't cooling well, but don't base your assertion just on Delta-T.

If you don't think it was cooling adequately stick to the report comment. I frequently find systems in new construction that don't cool well because the A/C installer didn't take the time to properly charge it (new construction factory assembly line mentality). The guys who do the callbacks are usually more conscientious and spend the time with the gauges to get the charge right, at least in my experience.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX

Last edited by cevans; 8/17/10 at 6:49 PM..
Reply With Quote
  #4  
Old 8/17/10, 6:44 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Zone System Temp Differentials

Call it out, let the Builder put his "Story" in writing as well.

8 degrees is not enough, at least here...

Last edited by bkelly2; 8/17/10 at 6:55 PM..
Reply With Quote
  #5  
Old 8/17/10, 8:21 PM
Mike W. Cole Mike W. Cole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Hickory, NC
Posts: 65
Default Re: Zone System Temp Differentials

This system had motorized dampers that controlled the major duct for each level. We have noticed that our rule of thumb ie, 600-700 sqft per ton out of the ground and 800-1000 sqft per ton below grade on zone systems seems to run a little light on tonnage on the zone systems. I would suppose that the design would assume both thermostats would not be calling for heat/cool at the same time at least in most situations and they are able to use less tonnage versus a non-zone system. Other than to 'feel' the suction line we don't measure temps there. Maybe we should. Is there a temp to use for this? 'How well it is cooling the house' is hard for me to define given all the variables that are usually present. This was a vacant home that had the system turned way up when we arrived.
I did in fact recommend analysis by a HVAC person but it was one of those where I thought I could do a better job if I faced this situation at some other date with a more definitive measurement. Thanks you all of you who have responded to date!!
Reply With Quote
  #6  
Old 8/17/10, 9:31 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: Zone System Temp Differentials

Quote:
Anyone had experience with this and is there a differential temp we could use in this situation?
Yea, call it out.

Do you even know anything about a zoned system?

Are you EPA certified to mess with ozone depleting refrigerants?
You do know that this is not just a federal law but international?!

I just inspected a house owned by a ****ing home Inspector. He is trying to sue me.

This idiot is barking up the wrong tree.

If you don't now HVAC, line your *** up and get sued or shut up about what your not required to do.

If you want to make a wild *** guess, go for it and don't bother us about your sorry *** being sued for making the wrong call.

Sorry, I'm not in a ****ing good mood today! ...



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission

Last edited by dandersen; 8/17/10 at 9:34 PM..
Reply With Quote
  #7  
Old 8/17/10, 9:37 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Zone System Temp Differentials

Wow David , Was it Sean's hose lol



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #8  
Old 8/17/10, 9:53 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: Zone System Temp Differentials

No, but.....



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #9  
Old 8/17/10, 10:08 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Zone System Temp Differentials

I meant house lol
You know that little Deal Killer over here.



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #10  
Old 8/18/10, 7:49 AM
Mike W. Cole Mike W. Cole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Hickory, NC
Posts: 65
Default Re: Zone System Temp Differentials

David Anderson,
I know enough to not get sued unlike some other obnoxious home inspectors who are permeating the message center here at NACHI. And please feel free to take that the wrong way.
Reply With Quote
  #11  
Old 8/18/10, 8:24 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: Zone System Temp Differentials

Well when you figure it all out, teach us...



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #12  
Old 8/19/10, 1:41 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Zone System Temp Differentials

Quote:
Originally Posted by dandersen View Post
Yea, call it out.

Do you even know anything about a zoned system?

Are you EPA certified to mess with ozone depleting refrigerants?
You do know that this is not just a federal law but international?!

I just inspected a house owned by a ****ing home Inspector. He is trying to sue me.

This idiot is barking up the wrong tree.

If you don't now HVAC, line your *** up and get sued or shut up about what your not required to do.

If you want to make a wild *** guess, go for it and don't bother us about your sorry *** being sued for making the wrong call.

Sorry, I'm not in a ****ing good mood today! ...
Sorry to hear about the trouble with a past client David, it is not fun and can happen for any reason at all.
Reply With Quote
  #13  
Old 8/19/10, 8:11 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: Zone System Temp Differentials

Thanks, but I don't even think about this stuff as I start my day!! ....

He can pound sand, and I am prepared after every inspection to cover every thing I report on.

If I said it, you had better have proof because you can be assure that I in fact do!



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 8/19/10, 9:40 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Zone System Temp Differentials

[quote=dandersen;682383]Thanks, but I don't even think about this stuff as I start my day!! ....

He can pound sand, and I am prepared after every inspection to cover every thing I report on.

If I said it, you had better have proof because you can be assure that I in fact do![/quote]

Man after my own heart.

If I said it, I'll write, sign it, and prove it!


(If I ever get to Tennessee I gotta look up David.)



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #15  
Old 8/19/10, 10:13 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Zone System Temp Differentials

All i have is a 12 year old armstrong POS heat pump. I need zoned heating though. Second thought I will just use Wayne's sister she is nice and fat. Warm for the winter!




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Checking AC with temp differentials. mnahrgang Inspecting HVAC Systems 39 7/2/10 7:37 AM
Emergency Lighting (commercial) mcyr Electrical Inspections 24 6/10/06 10:06 AM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues for Inspectors 0 2/14/06 3:38 AM


All times are GMT -4. The time now is 12:36 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts