Good morning, Gents-

Great comments. Mr. Warner, regarding the ESA you say: “Their material and education clearly state that it is widely accepted to provide indoor and outdoor samples in order for the lab to make a comparison of the levels and indicate elevated interior counts or not.”

That may be, but just because a brand new (formed only three years ago), small, local, obscure, training company with an handful of employees suddenly says “Do it this way” doesn’t wipe away decades and decades of procedures and methods that have been developed and validated by hundreds of international professionals. There are dozens of self-proclaimed commercial entities that are publishing “standards” that carry no weight whatever, and are not used by real experts; the IESO “standard” is a good example. On the other hand, there are real standards organizations such as ANSI, ASTM, ASHRAE, NFPA and others that put out real standards; additionally, there are standard texts that are “bibles” for air sampling that have been around for decades, I have included some of those references at the end of this post. IMHO, until one has read and understood at least these, one should not be taking samples.

If what ESA is teaching is blatently wrong (which you claim), what recourse do we have to rectify our erroneous teachings.

The ESA is at liberty to teach whatever they want. They can teach that one spore per cubic meter of air is extremely dangerous, and any building that contains a single mould spore should be evacuated and burned to the ground. (That may sound silly, but one of the bigger CMI courses employ a kook who used to teach that very thing).

ESA is claiming that Certified IHs are part of their team. Again the word "certified".

Certification in industrial hygiene is merely a club, not a statement of competency in industrial hygiene. For example, last year when I testified before the Colorado Department of Health regarding an upcoming regulation, the Board Explicitly stated: “If you restrict assessments to Certified Industrial Hygienists, the board WILL reject the regulation since ABIH certification is NOT a stamp of competence in industrial hygiene, or anything else for that matter.” Just last week, I taught the Biosafety section for ABIH certification. I was followed by a CIH, MPH, CSP, who came right out and told the attendees that if they think their certification would make them competent Industrial Hygienists, then they should leave the room, since, he stated, some of the most incompetant industrial hygienists he ever met were CIHs. Certification USED to mean something, now, it’s just a club. This is not a new argument, see my discussion in the AIHA Journal June, 1998, (
http://www.aiha.org/TheAcademy/html/june98.htm).


Hello Mr. Bennett:

Taken some one on in court is not what it is about.
Of course not, and I never stated as such. Indeed, I don’t generally sue people. However, incompetence frequently leads one to court, am I am hired by “the other side” to provide valid scientifically sound rebuttals. Maintaining the highest degree of competency for the benefit of one’s client is what it’s all about.

Question --- Did your test show mold -- Yes or No
Which test? I have performed several thousands over the last 18 years, in hundreds of houses, from Bakersfield to Boston, and Montana to Bucerias, Mexico. Regardless, ALL mould tests “show mold” as you would put it; it’s only a matter of detection limits. ALL houses, ALL HOUSES, contain moulds. ALL HOUSES contain Stachybotrys atra, ALL HOUSES contain the Aspergilli and Penicillia, ALL HOUSES contain the Cladosporia. So if your only data quality objective is to determine if the “test shows mould” then I want to be your lab, since I can charge you lots of $$$$ and only ever have to produce one report to cover all your samples. (Wanna buy a bridge?)

Question --- Can the test be done again and get the same results --Yes or No
Which test?

Question --- Is the level high enough to be a health issue
Which level, and what kind of health effect in what kind of person are you referring?

Question --- Would you live there
Where?

Should all the people selling "mold home test kits" like Home Depot etc be take out of the business??
They should be sued.


NOW WHAT??
I think I already answered that question. The practices and procedures for good sampling, based on sound sampling theory have been around for decades and decades. Just use those (I've listed a couple of standard references below); this may be new to the home inspection industry, but it isn’t anything new to microbiologists or Industrial Hygienists; who have been doing this since I was in diapers (and when I was born, there were only 48 States in America!).

If the public is to receive a service to keep them safe it has to be affordable and available.
And it is. I love it when someone calls me up and asks me over the phone to interpret their “mould test” and before I do it, I predict their results without ever having seen the lab result; and I do it for free (how affordable is that?). And them point out to them the fact that if someone could guess their lab results, sight unseen, why did they waste their money collecting a sample?

One Inspector in Florida is ready to do a school -- He has been doing Mold for a few years -- we are talking a lot of $$ and we are talking a lot of kids going to that school --- So help us out here.
I have been helping out; that is why I take the time to make these posts. If you would like to hire me, then please let me know. At $95 per hour, and $200 per hour for legal cases, I’m very reasonable.

BTW a home owner should have the same AFFORIDABLE information.
They do. To my knowledge, it costs nothing to read my posts here, or my web sites, or indeed, download thousands of legitimate academic papers and documents (see the references below).


----- Radon testing - lead testing -- CO2 -- testing --- Smoke testing -- Sound testing -- Temperature testing etc. is all off the shelf --
Is it? I am paid a lot of money to perform sound/noise monitoring. I performed work for the FBI on the Oklahoma City bombing case. As I remember, my tests were extremely complex, and required a very high level of understanding in the physics of sound and physiology. Radon testing is, for you, off the shelf, because you do not interpret the data; as I have discussed on this board in the past, virtually ALL of your “radon” readings are wrong, but you cannot get in trouble for it IF you have followed the US EPA protocols, since the EPA established those DQOs and interpretive tables, and a “certified” radon person, merely follows the cook-book instructions. In my case, as an ex Radiation Safety Officer, (who used to teach radiation toxicology to workers at the Rocky Flats Nuclear facility and having performed Radiation Endangerment Audits for Sandia National Labs), I am held to a slightly higher standard, and therefore, I NEVER follow the EPA protocols, since they are not valid (for reasons I have already described in earlier posts). As far as testing other items, such as CO2, of CO, or radon, or anything- everything I said about mould holds true for those as well- sampling theory doesn’t change just because the contaminant changes! (What a concept!)

I really want to tell them that I can not test for mold and no one else can either.

Tell them as you please, however, testing for mould can be done, and can be done correctly, and has been done for decades following valid, sound, tenable sampling theory using properly established DQOs to perform hypothesis testing. All of which seems to be ignored by the vast majority of those who are conducting "mould testing."

You see I too understand that testing without very controlled conditions, which we do not have, can be very far in the green at one point and then in the red a short time later.
I don’t see that at all. We DO have very controlled conditions, and I use them all the time to perform scientifically sound testing, producing very tenable results, and I have been doing so for years.

Give us a real simple reason to get out of the business.
I don’t want you out of the business, I just don’t want to see you in court getting sued for following myths and misconceptions and the ESA nonsense instead of doing things the right way. I want you to understand what you are and are not doing, so that you can provide a useful service to your clients instead of just running around willy-nilly collecting useless samples that are misinterpreted 99.9% of the time.


Remember our test can be reproduced -- even if not exactly but probably within normal testing tolerance to say that a building is a hazard or not.
No it can’t. And it you can, then you are REALLY screwing it up.

PLEASE your LOW LEVEL thoughts -- remember we see you as the expert and at this time do not want to challenge you --- but I am thinking
Based on my experience, most HIs are not low-level thinkers; they are highly technical, highly educated professionals who are keen to know the facts, and avoid the pitfalls of misconception. I have met a lot of you guys in the field, and I love ya, Man! And that is why I share this technical info on your chatboard, instead of waiting till you get sued and then sneak up and pounce.

Thanks for the great input!

What a great day to be alive! Cheers,
Caoimhín P. Connell
Forensic Industrial Hygienist
www.forensic-applications.com

(The opinions expressed here are exclusively my personal opinions and do not necessarily reflect my professional opinion, opinion of my employer, agency, peers, or professional affiliates. The above post is for information only and does not reflect professional advice and is not intended to supercede the professional advice of others.)

AMDG

Sampling References:

Occupational Exposure Sampling Strategy Manual, US DHEW, PHS, CDC, National Institutes of Occupational Safety and Health, 1977

Cox and Wathes, Bioaerosols Handbook, Lewis Publishers, 1995 (ISBN 0-87371-615-9)

Wells WF, Airborne Contagion and Air Hygiene, Harvard University Press, 1955

Cadle RD, The Measurement of Airborne Particles, Wiley Publishers, 1975 (ISBN 0-471-12910-0)

ISO Guide to the Expression of Uncertainty in Measurement, 1995 (There is an ancillary discussion put out by the US DoC, NIST called “American National Standard for Expressing Uncertainty--U.S. Guide to the Expression of Uncertainty in Measurement, ANSI/NCSL Z540-2-1997” that can be obtained from NIST, free of charge.)

NIOSH/NIOSH Manual of Analytical Methods, publication 94-113, 4th Ed. with Appendices

Reply With Quote
  #17  
Old 4/26/06, 12:40 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: Mold test

And thank you for your comments

I do apologize as to how I phrased some of my post

As you see we do have some questions and some opinnions

I thank you

More later

Report writing time

rlb
Reply With Quote
  #18  
Old 4/26/06, 12:46 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Mold test

Thanks for your responses.

You have refreshed much of what I was originally taught at a university Air Quality course during my education in Natural Resources. The instructor wrote the book because he felt there was not a good instructional book to be had at the time. I only remember his first name as Thadeous at Ball State University. Unfortunately I have been out of the higher learning scene and scientific arena for far too long. what you state is really refreshing my memory. I must dig up that text book. All too often we take what is taught as "certification" courses to be gospel, when in fact quite the opposite can be true. We must take what we learn and dig further to become truly qualified to provide our services. Courses often only scratch the surface of higher knowledge.

Your comments, aadvice, and remarks are truly welcome here.

The Scientific Method has indeed been around for centuries. All too often, we as "non-scientific" service providers forget or do not truly understand this concept. You have at least opened my eyes to the fact that I must educate my clients that much more regarding mold sampling and IAQ.

Thank you again.




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #19  
Old 4/26/06, 3:11 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 152
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Mold test

May I suggest that all of you that perform mold inspections verify with your insurance agent that performing such inspection will not cause the insurance company to cancel your liabiltiy insurance.

This is a rumor that was passed on to me 2nd hand. Just food for thought.

Another source for mold information is the IICRC. www.iicrc.org

We happen to be a member of this organization.
Reply With Quote
  #20  
Old 4/28/06, 6:29 PM
sbogren's Avatar
sbogren sbogren is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Nunn, CO
Posts: 33
Default Re: Mold test

Also,

ESA is the group providing training in conjunction with Prolab.

By the way; I have an air sampler for sale with air-o-cells and everything. Never been used, and taken out of the box once.

Any takers?
Reply With Quote
  #21  
Old 5/5/06, 11:37 AM
Robert F. Smith's Avatar
Robert F. Smith Robert F. Smith is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Durham, ME
Posts: 45
Default Re: Mold test

I have been reading this post with great interest. Not to belittle anyone or make light of a "touchy" subject, I offer the following:
First - mold testing is a viable service that can prove useful to anyone concerned about potential health issues. HI's do not profess to be Industrial Hygienist's, nor do we test in the same manner. Most homeowners cannot afford that type of testing, and the testing we provide is convenient and affordable.
Second - I agree that every home has mold. Its not a question of "if". Its a question of "how much" and "what type". If you see mold growing on sheathing in the attic, should you call a Industrial Hygienist to "scientifically" test it? With protocols and all the other scientific jargon I've seen posted here? I think not. My concern, and the concern of my client, is the type of mold growing, is a health risk present, and why is it growing there. Then how to get rid of it. To say a swab test is meaningless is absurd. First it verifies a suspicion of mold, and second it identifies the species of mold. From there, the type of mold that is identified may be capable of producing mycotoxins under the right circumstances. Don't you think a client would find that information valuable?
Third - if the client or a member of their family is already allergic to mold, regardless of the type, initial testing whether with a swab or air samples will tell us if mold is present and to what extent (if air samples). From there they can consult their allergist with the findings to determine if a health risk is present.

My feeling is that any testing service we provide as HI's is valuable information to a potential ore present home owner. Lawsuits? Bring 'em on!!



President
Maine State Nachi Chapter
Reply With Quote
  #22  
Old 5/5/06, 10:40 PM
Timothy J. Gardner Timothy J. Gardner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Moneta, VA
Posts: 272
Default Re: Mold test

I agree with Robert. CPC may well have overstepped his Academic Bounds.

Sorry Calamine, but 1.3million spores/cu m inside vs. 300 spores/cu m outside does mean there is a problem inside.

As my old mentor and nuclear scientist, Dr. Meir Degani, once said, "if it glows like a duck ..."

tg
Reply With Quote
  #23  
Old 5/5/06, 10:52 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: Mold test

A little USN nuclear history -- the air in our subs was safer than the air that our wives lived in when we were on patrol -- 1960-70's

rlb
Reply With Quote
  #24  
Old 5/6/06, 10:01 PM
Matt Berman, CMI Matt Berman, CMI is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Mt. Clemens, MI
Posts: 107
Wink Re: Mold test

I also agree with mr.Smith.I feel that my client should know if they may be buying a money pit.I will tell them if the foundation is bad,but they can have it tested by a structural engineer if they choose too.The same goes for mold if i see mold i will tell them and they can choose to have a sample tested for the type( or if its a health risk) at a lab or not.Thats why i am inspecting the home,to inform the client of defects.Matt
Reply With Quote
  #25  
Old 5/9/06, 11:51 PM
sbogren's Avatar
sbogren sbogren is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Nunn, CO
Posts: 33
Default Re: Mold test

From a layman.

I'm not so sure if I get it. In my opinion the greatest threat that mold poses to my clients is if the structure is compromised. In most of those cases, the cause can easily be traced to a leak of some kind; weather it is coming from a fixture or is a drainage problem.
problems what levels of mold constitutes a health issue? There are no safe or unsafe levels of mold to my knowledge that have been established. An air test that returns a high level of mold inside compared to levels outside will also most likely test low if other tests are run for the rest of the day. When the outside levels of mold are much higher does that mean that the outside air is dangerous?

As far as causing health
I believe a visual test is the best mold test I can offer my clients. Since all molds are treated in the same manner, testing is also a waste of their money. When the test comes back from the lab stating it's not a "toxic" mold does that mean it shouldn't be removed?

Thanks to some great media hype and lucrative scare tactics mold is to be feared by not only the ill-advised but also those with deep pockets.

I miss the days when mold was merely a nuisance.


Reply With Quote
  #26  
Old 6/7/06, 11:25 PM
Randall M. Cole Randall M. Cole is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Marietta, GA
Posts: 35
Default Re: Mold test

After using EMSL Labs, I am setup with Pro-Lab and attended the training class presented by ESA. I have a couple general pricing questions and would appreciate any and all input.

1- How much do y'all charge per each cotton-swab and tape-lift mold test? What is your Total Mold test charge (including time taken for sampling, mileage & gas, expertise, handling and shipping to the lab, etc)?

2- How much do you charge per IAQ Micro 5 sampling cassette? What is your Total IAQ test charge (including time taken for sampling, mileage & gas, expertise, handling and shipping to the lab, etc)?

Thank you in advance,

Randy Cole
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Interesting article about mold by litigation. gromicko IAC2 Indoor Air Forum 16 5/5/11 7:48 PM
Mold mcyr IAC2 Indoor Air Forum 5 9/13/10 10:31 AM
CMI imposter? jbraun Certified Master Inspector (CMI) Discussion 118 11/26/07 4:55 PM
Mold Remediation & Duck Cleaning Work-If Done Right dplummer Ancillary Inspection Services & Additional Topics 8 10/12/07 2:03 PM


All times are GMT -4. The time now is 10:57 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts