Default Something Missing on this Pipe?

This radon mitigation system was installed at a property I tested today. Shouldn't the top of the pipe have a U-shaped or gooseneck anto it?

Thanks

Jonathan
Attached Thumbnails
something-missing-pipe-img_5781.jpg   something-missing-pipe-img_5783.jpg  




Jonathan N. Leahy
President
A Rock Solid Home Inspection, LLC.
www.arocksolidhome.com
303-718-7779
Residential Home Inspections, Radon Testing, Mold Inspections
Reply With Quote
Find an InterNACHI certified Washington Home Inspector (and anywhere else in North America)
  #2  
Old 10/3/09, 10:51 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Something Missing on this Pipe?

Yes and it should also be above the roofline.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #3  
Old 10/3/09, 11:21 PM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 951
Default Re: Something Missing on this Pipe?

Does it have to go above the roof line if there are no windows or openings nearby?



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #4  
Old 10/3/09, 11:48 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Something Missing on this Pipe?

Quote:
Originally Posted by dokeefe View Post
Does it have to go above the roof line if there are no windows or openings nearby?
I'm not 100% sure because I don't do mitigation, but I believe so. Yes.

However, I did a radon test on a home that had a similar setup (garage side of the home). Radon levels were below 2.0 so apparently there was no negative effect.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #5  
Old 10/4/09, 7:20 AM
Gary Oleski Gary Oleski is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Bridgeport, CT
Posts: 726
Default Re: Something Missing on this Pipe?

Quote:
Originally Posted by mnahrgang View Post
Yes and it should also be above the roofline.
What Mark said.



Gary Oleski Home Inspections
Home Inspections Connecticut
Connecticut . 06610
NACHI04012833
CT#HOI.341
C M I
Reply With Quote
  #6  
Old 10/4/09, 9:01 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Something Missing on this Pipe?

Yep.

Radon reduction systems must be clearly labeled. This will avoid accidental changes to the system which could disrupt its function.

The exhaust pipe(s) of soil suction systems must vent above the surface of the roof and 10 feet or more above the ground, and at least 10 feet away from windows, doors, or other openings that could allow the radon to reenter the house, if the exhaust pipe(s) do not vent at least 2 feet above these openings.
Reply With Quote
  #7  
Old 10/4/09, 10:02 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Something Missing on this Pipe?

It must also have a "U-Tube"' manometer installed on it also (not so you can look at U-Tube videos either...)



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #8  
Old 10/4/09, 10:57 AM
Jonathan N. Leahy Jonathan N. Leahy is offline
InterNACHI Member
 
Join Date: Sep 2007
Location: Westminster, CO
Posts: 87
Default Re: Something Missing on this Pipe?

This pipe did discharge at least 10 feet above grade. The house tested below 1.0. The house next door also had a mitigation system as well. The manometer and vent pipe on the interior of the property was clearly marked.

Thanks

Jonathan




Jonathan N. Leahy
President
A Rock Solid Home Inspection, LLC.
www.arocksolidhome.com
303-718-7779
Residential Home Inspections, Radon Testing, Mold Inspections
Reply With Quote
  #9  
Old 10/4/09, 2:58 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Something Missing on this Pipe?

Quote:
Originally Posted by jleahy View Post
This pipe did discharge at least 10 feet above grade. The house tested below 1.0. The house next door also had a mitigation system as well. The manometer and vent pipe on the interior of the property was clearly marked.

Thanks

Jonathan
In that case I would note it, tell the buyers about the "issue" but not make a big deal of it.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you put polybutylene in the Summary? jfunderburk Plumbing Inspections 36 10/27/10 11:21 AM
Pellet stove help chellickson General Inspection Discussion 23 8/19/10 2:23 AM
Is this allowed? relliott Plumbing Inspections 4 7/15/09 7:40 PM
Help - Polybutylene Pipes Rick G Plumbing Inspections 39 2/12/09 9:16 AM
Identify ABS defective pipe mcyr Plumbing Inspections 6 1/29/09 7:39 PM


All times are GMT -4. The time now is 1:36 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts