Default 1" clearance

Does this application still require a 1" clearance from combustibles?
Attached Thumbnails
1-clearance-img_2805-small-.jpg.JPG
Views:	84
Size:	33.0 KB
ID:	32126  
Reply With Quote
Find an InterNACHI certified Kentucky Home Inspector (and anywhere else in North America)
  #2  
Old 9/25/09, 12:30 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: 1" clearance

If that's sheetrock, then it isn't "combustible" and there is no issue. Isn't sheetrock used to provide a fire barrier between the garage and home?

However, if that is a garage, then there is void in the fire barrier. The gap should be protected by a flange to prevent flame entry into the structure above the ceiling.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 9/25/09, 1:32 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,733
Default Re: 1" clearance

B Vent manufacturers will disagree and tell that a 1" clearance is required.

Quote:
Can I install drywall or wall board right up against the gas vent?
Quote:
No. Drywall and wallboard are considered combustible materials and should not be installed against the vent including the use of this material to close off the hole around the vent. Type B Gas Vent requires a minimum of one-inch clearance to combustibles. This one-inch is a typical clearance for all brands of Type B Vent, but each section of vent pipe is marked with the clearance required by Underwriter Laboratories, so it should be checked


http://www.americanmetalproducts.com...rivent/faq.htm



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail

Last edited by bkelly2; 9/25/09 at 1:37 AM..
Reply With Quote
  #4  
Old 9/25/09, 12:09 PM
Al D. Bolt Al D. Bolt is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Twin Falls, ID
Posts: 87
Default Re: 1" clearance

I think the difference is due to the different purposes. One is with performance under the conditions during a fire (where it is considered noncombustible), and another is with performance during exposure to a constant high-heat source (where it is considered combustible).
Correct?
Reply With Quote
  #5  
Old 9/25/09, 1:15 PM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,591
Default Re: 1" clearance

Quote:
Originally Posted by jfunderburk View Post
If that's sheetrock, then it isn't "combustible" and there is no issue. Isn't sheetrock used to provide a fire barrier between the garage and home?

.
I believe it is "combustible" as it will burn.

It is "fire-resistant", not "fire-proof"

Decent article...

http://www.homeadditionplus.com/dryw...ed-Drywall.htm



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #6  
Old 9/25/09, 8:46 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,733
Default Re: 1" clearance

Once again, it has nothing to do with drywall manufacturer, it has to due with what the Manufacturer recommends for the installation of their product. And how the product was tested by whatever agency validates the safety performance of the rpoduct(UL).

The dryall manufacturer can say whatever they want about their product............. They do no make B Vent.

Pyrolysis is also taken into consideration..................................... .....



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #7  
Old 9/25/09, 8:56 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2009
Location: Chicago
Posts: 1,049
Default Re: 1" clearance

Anyone know of a single problem caused in not having clearance?
Reply With Quote
  #8  
Old 9/25/09, 9:00 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,733
Default Re: 1" clearance

Quote:
Originally Posted by belliott View Post
Anyone know of a single problem caused in not having clearance?
Many fires in the north from pipes too close to combustibles. Watch the news this heating season or check with your fire department if need be for verification.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #9  
Old 9/25/09, 9:02 PM
Jeffrey Moore Jeffrey Moore is online now
InterNACHI Member
 
Join Date: Feb 2008
Location: Mesa, AZ
Posts: 110
Default Re: 1" clearance

Brian,

Don't you have to have an absence of oxygen to be called pyrolysis?

No, I haven't seen or heard of a problem with a smaller that 1'' clearance but
still call it out.



Jeff Moore
www.quantumhomeinspections.com
Flir (ITC) Level 1 Thermographer
Mesa, AZ
Reply With Quote
  #10  
Old 9/25/09, 11:08 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2009
Location: Chicago
Posts: 1,049
Default Re: 1" clearance

Quote:
Originally Posted by lkage View Post
Many fires in the north from pipes too close to combustibles. Watch the news this heating season or check with your fire department if need be for verification.
Thanks, but did they blame the drywall clearance?.
Reply With Quote
  #11  
Old 9/25/09, 11:21 PM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 610
Default Re: 1" clearance

Here is a picture of drywall in an interior utility closet that didn't 'burn' under pretty much worst case scenario with a flue! I ran into this a few years ago. I think someone made a boo boo when they were re-roofing.

1-clearance-bad-flue.jpg



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
  #12  
Old 9/25/09, 11:32 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2009
Location: Chicago
Posts: 1,049
Default Re: 1" clearance

Think I need to get a propane torch and see what happens , though I seem to recall a discussion here in the past about materials becoming more flammable over time when exposed to heat .
Reply With Quote
  #13  
Old 9/26/09, 12:15 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: 1" clearance

Read all of this and pay particular attention to the last paragraph. Provided Larry's information is correct, drywall is considered non-combustible by 3 national model building codes, I don't care what the b-vent manufacturer's say about it.

http://www.nachi.org/forum/f22/b-ven...34/#post543528



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Find an InterNACHI certified Kentucky Home Inspector (and anywhere else in North America)
  #14  
Old 9/26/09, 6:14 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,733
Default Re: 1" clearance

Remember to pay attention to whether there is wood behind the drywall within these clearance distance situations...



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #15  
Old 9/26/09, 6:43 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2009
Location: Chicago
Posts: 1,049
Default Re: 1" clearance

Quote:
Originally Posted by jfunderburk View Post
Read all of this and pay particular attention to the last paragraph. Provided Larry's information is correct, drywall is considered non-combustible by 3 national model building codes, I don't care what the b-vent manufacturer's say about it.

http://www.nachi.org/forum/f22/b-ven...34/#post543528
The paper is the combustible it says.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Walking surface and wall clearance dbucknavich Exterior 9 5/27/08 7:07 AM
Clearance Testing tfarmer Ancillary Services & Additional Topics 15 2/26/08 6:41 PM
Range Clearance dsmith6 Interior 18 1/7/07 10:55 PM
Service panel clearance wwarner Electrical 13 8/12/06 1:07 PM
Siding to Ground Clearance tneumann Exterior 14 2/9/06 12:48 AM


All times are GMT -4. The time now is 12:38 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts