Old 10/6/07, 10:06 PM
lfoster's Avatar
lfoster lfoster is offline
Question 2 water heaters, combined TPR and pan drain line
Todays inspection had 2 water heaters. The TPR drain for each meet at a 'T' in area between them, then travel 2' to the rear, 90 degree angle down, 90 degree angle toward the exterior.
Can these lines be joined together? If one were to blow, the discharge would first travel to the other unit, then to the 't'.
The drain pan is engineered the same way.
Don't these units each need a drain for the TPR, and the pan?
Thanks,
Linda
Old 10/6/07, 10:29 PM
grusk grusk is offline
Please Note: grusk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2 water heaters, combined TPR and pan drain line
The discharge piping serving a TPR valve should:
  1. Be constructed of an approved material such as CPVC, copper, polyethylene, galvanized steel, polybutylene, polypropylene, or stainless steel.
  2. Not be smaller than the diameter of the outlet of the valve it serves (usually no smaller than 3/4").
  3. Shall not reduce in size from the valve to the air gap (point of discharge).
  4. Be as short and as straight as possible so as to avoid undue stress on the valve.
  5. Be installed so as to drain by flow of gravity.
  6. Not be trapped since standing water may become contaminated and backflow into the potable water.
  7. Discharge to the floor, to an indirect waste receptor, or to the outdoors.
  8. Not be directly connected to the drainage system to prevent backflow of potentially contaminating the potable water.
  9. Discharge through a visible air gap (atmosphere) in the same room as the water heater.
  10. Be first piped to an indirect waste receptor through an air gap located in a heated area when discharging to the outdoors in areas subject to freezing, since freezing water could block the pipe.
  11. Not terminate more than 6 inches (152 mm) above the floor or waste receptor.
  12. Discharge in a manner that could not cause scalding.
  13. Discharge in a manner that could not cause structural or property damage.
  14. Discharge to a termination point that is readily observable by occupants because discharge indicates that something is wrong.
  15. Be piped independent of other equipment drains, water heater pans, or relief valve discharge piping to the point of discharge.
  16. Not have valves anywhere.
  17. Not have tee fittings.
  18. Not have a threaded connection at the end of the pipe so as to avoid capping.
See 15 and 17
Gary
Old 10/6/07, 10:38 PM
lfoster's Avatar
Thanks Gary,
Is there a reference code #?
Old 10/6/07, 10:47 PM
No it's fron the NACHI Water Heater TPR Valve Discharge Piping mini-course.
Gary
Old 10/11/07, 11:29 PM
I know that recent IRC requirement do not allow the TPR drain pipe to have a T. Does anyone know how long this has been a requirement?
Old 10/12/07, 4:40 AM
Emmanuel J. Scanlan Emmanuel J. Scanlan is offline
Originally Posted by lfoster
Thanks Gary,
2003 IRC:
P2803.6.1 Requirements of discharge pipe.
The outlet of a pressure relief valve, temperature relief valve or combination thereof, shall not be directly connected to the drainage system. The discharge from the relief valve shall be piped full size separately to the floor, to the outside of the building or to an indirect waste receptor located inside the building. In areas subject to freezing, the relief valve shall discharge through an air gap into an indirect waste receptor located within a heated space, or by other approved means. The discharge shall be installed in a manner that does not cause personal injury or property damage and that is readily observable by the building occupants. The discharge from a relief valve shall not be trapped. The diameter of the discharge piping shall not be less than the diameter of the relief valve outlet. The discharge pipe shall be installed so as to drain by gravity flow and shall terminate atmospherically not more than 6 inches (152 mm) above the floor. The outlet end of the discharge pipe shall not have a valve installed.
Knowledge is power, but sharing knowledge brings peace!
http://www.psinspection.com
TREC License# 7593
Professional Real Estate Inspections for the counties of Collin, Rockwall, Hunt, Dallas, Tarrant, Kaufman and all surrounding areas. If you want the the best you will find it with PS Inspection & Property Services LLC!
Old 10/14/07, 1:22 AM
William J. Decker's Avatar
TPR piping should never be PVC. Metal pipe (preferably copper, it doesn't corrode) and drained to within 6" of the floor or to the exterior.
Just because Home Depot sells it, that doesn't mean its correct.
Will Decker, CMI
ILL License # 450.0002240
Decker Home Services, LLC
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702
wjd@DeckerHomeServices.com
www.DeckerHomeServices.com
Old 10/14/07, 8:03 AM
Barry Adair's Avatar
CPVC is allowed by many AHJ around here, even though 3/4" CPVC is undersized for this application. The interior diameter of CPVC is 0.71". The code and TPR valve manufacturer require it to be 0.75" the ID is .04" smaller, so go figure how they came to reason this is OK.
Until the code changes I continue to write them up.
Regardless what Linda has depicted is wrong.
ADAIR INSPECTION
972-487-5634
TREC # 4563
EDI: EIFS-MA TX # 39
2008 US Member of the Year
Old 12/18/07, 1:07 AM
dblanchard dblanchard is offline
Where does one get a copy of the national plumbing code book? I checked Lock Supply this afternoon and they had a 2006 copy of the International Plumbing Code for $63. They said there is a national code book but they can't get it.Thanks
Old 12/18/07, 1:27 AM
Brian E. Kelly's Avatar
http://www.constructionbook.com/unif...CMP=KNC-Google
Old 12/18/07, 1:36 AM
Barry, are you an electrician?
Where did an ID of 0.71" come from???
http://www.engineeringtoolbox.com/pv...ons-d_795.html
I won't even comment on Will's "copper doesn't corrode" fairy tale.
Old 12/18/07, 11:23 AM
Tracy Schoop Tracy Schoop is offline
Please Note: Tracy Schoop is a non-member guest and is in no way affiliated with InterNACHI or its members.
The NACHI guidelines have several wrong and or inconsistent remarks. Why try to reinvent he wheel. Just say what the manufacturers say and the codes say. Very simple. IMO, this needs to be removed as it could get inspectors into trouble.