Default 45 degree slope of 3" waste pipe?

Sorry, No picture.

Twice this last week I saw horizontal 3" waste pipe dropped a foot or two over three to five feet span (with the use of 45 degree splices.) I have seen nothing in my library that says "don't do it this way ..." Although, because my material makes no exception to the to 1/4 - 1/8" rule I noted in these reports that elevation changes accomplished in this way will eventually cause problems and should be changed to 90 degree transitions. Am I correct?
Reply With Quote
  #2  
Old 11/21/06, 12:43 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,067
Default Re: 45 degree slope of 3" waste pipe?

Dennis, if you ever had to clean the line 45's would allow a snake through without dismantling.
Reply With Quote
  #3  
Old 11/21/06, 12:50 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: 45 degree slope of 3" waste pipe?

90's are more likely to cause problems in drain line than 45's. . .

Neither is improper.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 11/21/06, 1:13 AM
dthomas2 dthomas2 is offline
Active Poster
 
Join Date: Jun 2006
Location: Spokane, Wa
Posts: 262
Please Note: dthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 45 degree slope of 3" waste pipe?

ouch!
Reply With Quote
  #5  
Old 11/21/06, 1:13 AM
Darrell B. Hadler's Avatar
Darrell B. Hadler Darrell B. Hadler is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Medicine Hat, AB
Posts: 367
Default Re: 45 degree slope of 3" waste pipe?

Don't see how this could cause a problem. I would far sooner see a couple of 45's used in the manner you stated, than a 90. Better flow with lest restriction, and as mentioned in previous posts...much easier to snake/auger.



Darrell Hadler CMI
Five Star Home Inspections
Medicine Hat, AB. Canada
NACHI# 04111082 Cell phone# (403)502-3593
Inspected once . . . inspected right!
Reply With Quote
  #6  
Old 11/21/06, 1:25 AM
jschulte jschulte is offline
Active Poster
 
Join Date: Jul 2006
Location: Moberly, MO
Posts: 445
Please Note: jschulte is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 45 degree slope of 3" waste pipe?

I think the problem generally comes from the fact that if you have too much slope, solids will build because the liquids drain too fast. However, if it's over a short span, I do not think it will be a problem, especially if it drains into a vertical line. I would consider a three to five foot span a short distance.

Just my opinion, though, I haven't spent much time in a drain line to see it happen.
Reply With Quote
  #7  
Old 11/21/06, 2:14 AM
dthomas2 dthomas2 is offline
Active Poster
 
Join Date: Jun 2006
Location: Spokane, Wa
Posts: 262
Please Note: dthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 45 degree slope of 3" waste pipe?

Thanks guys.

Right now I am googling to see if I can find a definitive statement. The problem is that the charts and write-ups I use as reference do not sight exception to the 90 degree rule. Since I fear overlooking a problem with a seemingly correct situation I would like to see a research related report - so I am trying to find one.
Reply With Quote
  #8  
Old 11/21/06, 9:50 AM
ckratzer ckratzer is offline
Active Poster
 
Join Date: Mar 2005
Posts: 256
Please Note: ckratzer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 45 degree slope of 3" waste pipe?

Quote:
Originally Posted by dduffy
Dennis, if you ever had to clean the line 45's would allow a snake through without dismantling.
I'd be guessing Dale has done the research .
Hands -on experiance. Thats what I'm talking about .
Reply With Quote
  #9  
Old 11/21/06, 6:56 PM
lcapaul's Avatar
lcapaul lcapaul is offline
Active Poster
 
Join Date: Jun 2005
Location: Rathdrum, ID
Posts: 1,581
Please Note: lcapaul is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 45 degree slope of 3" waste pipe?

Quote:
Originally Posted by dthomas2
Thanks guys.

Right now I am googling to see if I can find a definitive statement. The problem is that the charts and write-ups I use as reference do not sight exception to the 90 degree rule. Since I fear overlooking a problem with a seemingly correct situation I would like to see a research related report - so I am trying to find one.
Dennis,

Do you have the Code Check 4th Edition? On page 14 under drainage/changes of direction it states:

Vert to horiz or horiz to horiz through wye branches or 45 degree wy branches of fittings of equal sweep IRC 3005.1 UPC 706.3,4

Hope that helps.

Last edited by lcapaul; 11/21/06 at 7:12 PM..
Reply With Quote
  #10  
Old 11/21/06, 7:07 PM
lcapaul's Avatar
lcapaul lcapaul is offline
Active Poster
 
Join Date: Jun 2005
Location: Rathdrum, ID
Posts: 1,581
Please Note: lcapaul is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 45 degree slope of 3" waste pipe?

Quote:
Originally Posted by lcapaul
Dennis,

Do you have the Dode Check 4th Edition? On page 14 under drainage/changes of direction it states:

Vert to horiz or horiz to horiz through wye branches or 45 degree wy branches of fittings of equal sweep IRC 3005.1 UPC 706.3,4

Hope that helps.
Dennis,
I knew I'd read it some where, in Howard Massey's Plumbers Handbook on page 25: Verticle offset in Drainage Pipes,,,,,"You can consider as straight any verticle stack with an offset of 45 degrees or less. Size it as a straight vertical stack....."

Just make sure the fittlings don't reduce the diameter of the pipe or have any ridges that may cause an obstruction.
Reply With Quote
  #11  
Old 11/21/06, 7:39 PM
scosta's Avatar
scosta scosta is offline
Active Poster
 
Join Date: Oct 2005
Location: North Royalton, Oh
Posts: 186
Please Note: scosta is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 45 degree slope of 3" waste pipe?

This is what I have.
Attached Thumbnails
45-degree-slope-3-waste-pipe-1615.jpg  
Reply With Quote
  #12  
Old 11/21/06, 8:12 PM
lcapaul's Avatar
lcapaul lcapaul is offline
Active Poster
 
Join Date: Jun 2005
Location: Rathdrum, ID
Posts: 1,581
Please Note: lcapaul is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 45 degree slope of 3" waste pipe?

UPC 706.4

706.4 Vertical drainage lines connecting with
horizontal drainage lines shall enter through fortyfive
(45) degree (0.79 rad) wye branches, combination
wye and one-eighth (1/8 bend branches, or other
approved fittings of equivalent sweep. Sixty (60)
degree (1.05 rad) branches or offsets may be used
only when installed in a true vertical position.
SANITARY DRAINAGE
113
Reply With Quote
  #13  
Old 11/22/06, 12:23 AM
dthomas2 dthomas2 is offline
Active Poster
 
Join Date: Jun 2006
Location: Spokane, Wa
Posts: 262
Please Note: dthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 45 degree slope of 3" waste pipe?

Quote:
Originally Posted by lcapaul
UPC 706.4

706.4 Vertical drainage lines connecting with
horizontal drainage lines shall enter through fortyfive
(45) degree (0.79 rad) wye branches, combination
wye and one-eighth (1/8 bend branches, or other
approved fittings of equivalent sweep. Sixty (60)
degree (1.05 rad) branches or offsets may be used
only when installed in a true vertical position.
SANITARY DRAINAGE
113
Lewis,

Thanks for the effort. Does the UPC distinguish between a Solid waste drain and a sink/basin drain? Is the "706.4" referring to a solid waste drain?
Reply With Quote
  #14  
Old 11/22/06, 12:27 AM
dthomas2 dthomas2 is offline
Active Poster
 
Join Date: Jun 2006
Location: Spokane, Wa
Posts: 262
Please Note: dthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 45 degree slope of 3" waste pipe?

Quote:
Originally Posted by scosta
This is what I have.
Steve,

I have this picture too and is why I have a problem with contray statements. I did not find an exception with my google search but for some reason I could not get to the UPC - except to purchase. I may go the Library of Congress.
Thanks for the help.
Reply With Quote
  #15  
Old 11/22/06, 1:43 AM
lcapaul's Avatar
lcapaul lcapaul is offline
Active Poster
 
Join Date: Jun 2005
Location: Rathdrum, ID
Posts: 1,581
Please Note: lcapaul is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 45 degree slope of 3" waste pipe?

Dennis,
Here's a link to chapter 7 of the UPC

http://www.iapmo.org/common/ROP2004/...eprint/ch7.pdf

(If you want to see other chapters just change ch7 to whatever number you want.

Where are our plumbing guru's? I'm not sure about the verticle drop in the horizontal drain lines using 45's, but I think your statement "I noted in these reports that elevation changes accomplished in this way will eventually cause problems and should be changed to 90 degree transitions." was pretty good, although I would have used "May" instead of "will" cause problems and wouldn't have mentioned changing the fitting to 90 degree, I'd leave that up to a plumber
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you put polybutylene in the Summary? jfunderburk Plumbing Inspections 36 10/27/10 11:21 AM
Help - Polybutylene Pipes Rick G Plumbing Inspections 39 2/12/09 9:16 AM
Identify ABS defective pipe mcyr Plumbing Inspections 6 1/29/09 7:39 PM
orangeburg waste pipe bking Plumbing Inspections 5 10/24/07 6:46 PM
main waste pipe bking Plumbing Inspections 1 5/17/06 10:14 PM


All times are GMT -4. The time now is 10:29 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts