observation: water pressure testing conducted at the lowest hose outlet on the exterior of the house. No verification that the hose valve is located downstream of the water pressure regulator. No expansion tank installed on the hot water heater.

Water pressure testing results:90# psig.

What say you?

There are no other indicators anywhere in the house that water pressure is excessive.

Must the pressure reducing valve be adjusted?



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Need a home inspection in Wyoming? Check out InterNACHI's listing of Wyoming certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/10/10, 10:15 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: 90 PSI water pressure?

"Must" is an inappropriate word in an inspection report.

I would record my observation that the pressure is above the optimum and I would recommend that it be adjusted to be between 60 and 80.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #3  
Old 7/10/10, 10:30 AM
gfitzgerald's Avatar
gfitzgerald gfitzgerald is offline
Active Poster
 
Join Date: Jun 2009
Location: Sherman Oaks Ca.
Posts: 335
Please Note: gfitzgerald is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 90 PSI water pressure?

In my area most arrogation supply is installed before the interior regulator which sometimes includes the hose bibs.
Reply With Quote
  #4  
Old 7/10/10, 10:44 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: 90 PSI water pressure?

Quote:
Originally Posted by jbushart View Post
"Must" is an inappropriate word in an inspection report.

I would record my observation that the pressure is above the optimum and I would recommend that it be adjusted to be between 60 and 80.
would you expect a plumber to come out on a service call to adjust 10 psi when there is no other associated conditions?

I find that water pressure gauges are very inaccurate. I go through at least six or seven of them a year due to freezing, shock damage, inaccuracy etc...

Outside of those cells are often not part of the regulated water supply. This was not covered in the inspection report.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #5  
Old 7/10/10, 11:00 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: 90 PSI water pressure?

Whether or not my recommendation in an inspection report is "practical" has no bearing on whether or not it will appear in my report, since it is simply a record of observations and recommendations from which my client may (or may not) choose to have accomplished. They may decide to wait until there is some other problem in the future...and then implement one of my recommendations in conjunction with it. I don't know.

In an energy audit report, where I am writing/prioritizing a scope of work, I will take such matters into consideration. For a home inspection report....it's a waste of time, IMO. More often than not, they are going to use the sum of the issues to negotiate a reduction in price....get their reduction in price....and then file the report away for years.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #6  
Old 7/10/10, 1:44 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: 90 PSI water pressure?

Quote:
Originally Posted by dandersen View Post
observation: water pressure testing conducted at the lowest hose outlet on the exterior of the house. No verification that the hose valve is located downstream of the water pressure regulator. No expansion tank installed on the hot water heater.

Water pressure testing results:90# psig.

What say you?

There are no other indicators anywhere in the house that water pressure is excessive.

Must the pressure reducing valve be adjusted?
what did the other hose bibs read??

90 is too high and should be regulated down.....
Reply With Quote
  #7  
Old 7/10/10, 1:48 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: 90 PSI water pressure?

First, I would verify (with my accurate, non-freezing pressure gauge) that the INSIDE pressure is high. Then my report would simply state;

"The water pressure inside the residence is exceeds 80 psi and the regulator should be adjusted so that the static pressure is between 60 and 75 psi. However, it may be that the regulator has failed, or is failing and the pressure cannot be reduced, in which case the regulator should be replaced by a qualified plumber."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 7/10/10, 1:55 PM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: 90 PSI water pressure?

82 or for that matter 80.5 is too high.

Either of which are an indication that the regulator (if there is one) is not doing it's job.

If we are there during the day... what do you suppose the pressure is "creeping" to at night?

Just about every regulator I've installed was nearly 60 psi, right out of the box. If I see see a measurement near 80 psi, I'll make a note to check again in the near future.

Next time you see a borderline measurement, leave a gauge with the "High Sweep" if you have one... on overnite, you may see it creep up quite a bit.

I've done just that several times when it was borderline, only to find the daytime pressure about the same during the daytime and as high as 120 (red sweep hand) for overnite pressure.

Always something...



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #9  
Old 7/10/10, 1:58 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: 90 PSI water pressure?

Brian, I didn't do this testing. I inspected the house three years ago. The now listing real estate agent (selling real estate agent then) is asking for opinions.

I gave my opinion.

I am looking for other opinions or possible requirements (not building code) that sets maximum water pressure requirements.

I'm interested in the arguments that the homeowner is required to pay for a plumber to adjust water pressure one psi above 80 psi standards.

It is noteworthy to report that the pressure is elevated, but what is the justification for requiring adjustment?

How does it fit here?
Quote:
1.2. A Material Defect is a condition of a residential real property, or any portion of it, that would have a significant, adverse impact on the value of the real property, or that involves an unreasonable risk to people on the property.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #10  
Old 7/10/10, 2:13 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: 90 PSI water pressure?

Quote:
Originally Posted by dandersen View Post
Brian, I didn't do this testing. I inspected the house three years ago. The now listing real estate agent (selling real estate agent then) is asking for opinions.

I gave my opinion.

I am looking for other opinions or possible requirements (not building code) that sets maximum water pressure requirements.

I'm interested in the arguments that the homeowner is required to pay for a plumber to adjust water pressure one psi above 80 psi standards.

It is noteworthy to report that the pressure is elevated, but what is the justification for requiring adjustment?

How does it fit here?
one PSIG above standard,, probably not because none of us carry Calibrated, mirror back, accurate, pressure gauges...

But 90 PSIG is too much... it is hard on the crappy internal piping assembled in Sri Lanka, on Dishwashers, Icemakers, Clothes Washers,,, etc....

The regulator installed may have failed....

Homeowners are not required here to even look at my report let alone act on any of my recommendations.
Reply With Quote
  #11  
Old 7/10/10, 2:34 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: 90 PSI water pressure?

Quote:
Originally Posted by dandersen View Post
I'm interested in the arguments that the homeowner is required to pay for a plumber to adjust water pressure one psi above 80 psi standards.
This is a false assertion. There is no argument that would require a homeowner to take any action on this issue.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 7/10/10, 4:44 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: 90 PSI water pressure?

Quote:
But 90 PSIG is too much... it is hard on the crappy internal piping assembled in Sri Lanka, on Dishwashers, Icemakers, Clothes Washers,,, etc....
what I'm asking is how much is too much?

is there documentation on any appliance that specifically addresses pressure regulation limits?

thank you Jeffrey, that is what I'm trying to ascertain. I keep getting conjecture!



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #13  
Old 7/10/10, 5:14 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: 90 PSI water pressure?

http://webcache.googleusercontent.co...&ct=clnk&gl=us

Quote:
Although most household appliances are designed to work with water pressure between 15 and 120 pounds per square inch (psi), the IRWD standard for water pressure is between 50-100 psi
Reply With Quote
Need a home inspection in Wyoming? Check out InterNACHI's listing of Wyoming certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/10/10, 5:37 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: 90 PSI water pressure?

Quote:
Originally Posted by dandersen View Post
what I'm asking is how much is too much?

is there documentation on any appliance that specifically addresses pressure regulation limits?

thank you Jeffrey, that is what I'm trying to ascertain. I keep getting conjecture!
most of your posts are conjecture... why should we be any different....

Just make up stuff to tell your Realtor friend and I am sure they will keep using you...
Reply With Quote
  #15  
Old 7/10/10, 5:45 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: 90 PSI water pressure?

I don't make stuff up is I go along !

So,#1 my posts are not conjecture, #2 your recommendation proves that you do!



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water Pressure Problem dcossar Plumbing Inspections 19 11/21/09 8:47 PM
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues for Inspectors 294 2/10/08 1:20 AM


All times are GMT -4. The time now is 12:13 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts